Thanks for your valuable advice. I forgot to mention that my main panel is Challenger. Anything different Nema 3R I should watch out for?Im glad you realize it's wired wrong.
Spend your $ on a new NEMA 3R panel and scrap the one you have.
I saw the Challenger cb in this sub panel and assumed it was a Challenger also but spared you from that discussion. (Google Challenger Electrical Panels)Thanks for your valuable advice. I forgot to mention that my main panel is Challenger. Anything different Nema 3R I should watch out for?
, etc. At least get that inspected by a sparky and consider changing that out before any trouble starts.Thank you so much very helpful information. Subpanel is attached to the same wall outside not too far behind main panel (150 amp) inside the garage. I included a picture.I saw the Challenger cb in this sub panel and assumed it was a Challenger also but spared you from that discussion. (Google Challenger Electrical Panels)
NEMA 3R is an enclosure rating typically used for outdoor locations. Probably all manufacturers offer this enclosure rating. The enclosure rating typically found inside a home would be NEMA 1.
I suggest you look into more cb space for the exterior panel....16, 20, 24 circuits. Not much difference in cost when considering # cb spaces. Depends on future needs. No body ever complained about too many.
A 120/240VAC, single phase 100A panel in NEMA 3R enclosure is common. You may find it cheaper to buy one with a main cb instead of main lugs. Look into Siemens, Square D, Cutler Hammer brands.
If this panel is in/attached to the same building as the main panel, then a main cb is not needed (sparing you all the code minutia.)
Your next concern is checking out the main panel......Challenger panels had a special feature.....cb's and the buss lug connections weakened over time causing poor connections leading to heat, arcing,, etc. At least get that inspected by a sparky and consider changing that out before any trouble starts.

However subpanel is serving the shed and pool equipment plus ac compressor. I want to use square d but not sure with compatibility with Challenger? Here's what I have been looking at SQ d. It's 125 amp my mp is 150 is that a concern?Got it thank you so much. I will probably reach out as I am doing it never know what am I going to run into. Hopefully it will be a smooth implementation.You need to run a 4-wire feed from main panel to sub panel. Panel mfr's doesnt matter for either.
SQ D is fine for either or both.
Subpanel ampacity rating has no impact on main panel. It's the load that matters.
The cb in the main panel protects the cable feeding sub panel. That cb cant be greater than the lower of cable ampacity or subpanel (assumong main lug panel).
If the wire size is #8, it is only good for 40 amps. #6 is required for 50 (when it's Romex). Honestly, the size doesn't matter, it's the wrong cable type no matter the size of the wire. They may have only needed 40, and maybe the 40/30 quad breaker was the only thing available. Personally, I have never seen a quad breaker in the wild, only pictures. I've never needed one, but there have been times I could have used one.
What breaker size do you recommend upgrading to since I am going to be changing the wires anyways?If the wire size is #8, it is only good for 40 amps. #6 is required for 50 (when it's Romex). Honestly, the size doesn't matter, it's the wrong cable type no matter the size of the wire. They may have only needed 40, and maybe the 40/30 quad breaker was the only thing available. Personally, I have never seen a quad breaker in the wild, only pictures. I've never needed one, but there have been times I could have used one.
It depends on the route to get from panel to panel, but based on the what I see in the pictures, I would run a 6/3 with ground Romex and use a 50 amp breaker. The AHJ's I deal with don't care if a 60 gets thrown in because it's good for 55 amps and there is no such breaker size.What breaker size do you recommend upgrading to since I am going to be changing the wires anyways?
Another question maybe not related to the subpanel but where's the link between the neutral and ground bars in the mp? Also I don't see a bonding jumper (green screw). Am I missing something or because this panel is so old it has a different mechanism?It depends on the route to get from panel to panel, but based on the what I see in the pictures, I would run a 6/3 with ground Romex and use a 50 amp breaker. The AHJ's I deal with don't care if a 60 gets thrown in because it's good for 55 amps and there is no such breaker size.
I can't see it, but there may be a strap that connects to the can and neutral bar. There may be a screw that isn't green. Do a continuity test between the neutral bar and some exposed metal of the panel. I usually use a screw hole.Another question maybe not related to the subpanel but where's the link between the neutral and ground bars in the mp? Also I don't see a bonding jumper (green screw). Am I missing something or because this panel is so old it has a different mechanism?
From the one picture outside it looks like your main and your load center share the same wall inside and outside. I would run a conduit out the back of the main and down the wall to the new load center. Remember future use capabilities and run a bigger conduit.It depends on the route to get from panel to panel, but based on the what I see in the pictures, I would run a 6/3 with ground Romex and use a 50 amp breaker. The AHJ's I deal with don't care if a 60 gets thrown in because it's good for 55 amps and there is no such breaker size.
EDIT. I forgot the inside panel is a Challenger. Run the 6/3 but keep the 40 amp breaker. When the inside panel gets replaced (it will happen) put in the larger breaker. You may be able to source an Eaton quad, but I don't think it's worth it.
Easier said than done when getting out of the main panel and through the brick. The hole through the wall has to be larger than the knockout to allow the adapter/connector to fit through. It will also have to cross the service entrance conduit or meter socket so the conduit will have to go up and over it, it's probably too close for a saddle. Then the fence has to dealt with. Easiest is going to be to cut out some drywall and run it through the studs then through a hole through the wall that doesn't have to be perfect. Patch the drywall and be done with it.From the one picture outside it looks like your main and your load center share the same wall inside and outside. I would run a conduit out the back of the main and down the wall to the new load center. Remember future use capabilities and run a bigger conduit.
True that conduit through brick isn't hard, but lining up with an existing knockout can be tough for anyone. After the battle to get the proper knockout hole opened up bass ackwards from the direction it was designed to get punched, all it will take is the pilot hole just a little crooked or not quite centered in the hole, or it winding up on a mortar joint or two and having to go through two or three partial bricks and the whole project just took a turn for the worse. I've been there and done all of those. The OP didn't even know what kind of panel he has, which in my mind makes his install experience a 0. I doubt he has a bender and by the time he buys that, an LB, rain tight fittings, 20' pieces of black, red, and white #6 and a #10 ground, and enough EMT to do the job as well as make a ton of rookie mistakes. Then there is the issue of how to drill the hole. If he doesn't have an SDS, he's going to have to buy or rent and get a big enough bit for the connector to fit. He could probably rip all the drywall off the garage wall, run the cable, and have everything patched up in less time than the exterior conduit and be money ahead.Didn't mean to quote you, sorry.
Op gets the info still. Conduit through brick is not hard for some installers.
The panel looks to be a Westinghouse era Challenger, they kept the Challenger panels for both lines, & discontinued the breakers & had BR breakers listed for them, & the OP's breakers are the BR design, they continued to use those Zinsco main breakers until Eaton took over.It depends on the route to get from panel to panel, but based on the what I see in the pictures, I would run a 6/3 with ground Romex and use a 50 amp breaker. The AHJ's I deal with don't care if a 60 gets thrown in because it's good for 55 amps and there is no such breaker size.
EDIT. I forgot the inside panel is a Challenger. Run the 6/3 but keep the 40 amp breaker. When the inside panel gets replaced (it will happen) put in the larger breaker. You may be able to source an Eaton quad, but I don't think it's worth it.
You are absolutely right I don't have that much experience neither the tools. I am looking for a simple way yet safe to get this done. Definitely not willing to mess with bricks and concrete, LB etc.True that conduit through brick isn't hard, but lining up with an existing knockout can be tough for anyone. After the battle to get the proper knockout hole opened up bass ackwards from the direction it was designed to get punched, all it will take is the pilot hole just a little crooked or not quite centered in the hole, or it winding up on a mortar joint or two and having to go through two or three partial bricks and the whole project just took a turn for the worse. I've been there and done all of those. The OP didn't even know what kind of panel he has, which in my mind makes his install experience a 0. I doubt he has a bender and by the time he buys that, an LB, rain tight fittings, 20' pieces of black, red, and white #6 and a #10 ground, and enough EMT to do the job as well as make a ton of rookie mistakes. Then there is the issue of how to drill the hole. If he doesn't have an SDS, he's going to have to buy or rent and get a big enough bit for the connector to fit. He could probably rip all the drywall off the garage wall, run the cable, and have everything patched up in less time than the exterior conduit and be money ahead.





That's one of them for sure. Do you happen to know if that's a breaker or bus issue?



Voilà I don't see any major burn or significant discoloration looks normal to m.Shut off the main and pop out cb's looking for burns, pitting and poor retention of the cbs. Take pics of both mating surfaces where issues appear.
If any insulation looks discolored/brown next to a terminal, it could be loose.
I'm thinking the discoloration you see is coming from the buss side of the bolted connection and not the main cb.
![]()


I had a sparky looking at the panel/subpanel he said that the existing feed wires are 4awg and I can replace the quad breaker with double pole 60 amps to feed the subpanel and double pole 30 for the topstove. He also mentioned adding an extra single 4awg wire for the neutral. Does that sound code compliant?It depends on the route to get from panel to panel, but based on the what I see in the pictures, I would run a 6/3 with ground Romex and use a 50 amp breaker. The AHJ's I deal with don't care if a 60 gets thrown in because it's good for 55 amps and there is no such breaker size.
EDIT. I forgot the inside panel is a Challenger. Run the 6/3 but keep the 40 amp breaker. When the inside panel gets replaced (it will happen) put in the larger breaker. You may be able to source an Eaton quad, but I don't think it's worth it.
I don't remember ever seeing a 4/2 or 4/3 romex, but I've lived a sheltered life. It looks to me like the old #6 that had the TW insulation on it, and it could very well be. He's right that you can put a #4 on a 60, but he's wrong about adding an individual wire in addition to the romex for a neutral and if he told you that, get that and everything else he told you out of your head. Everything needs to be contained in the cable assembly or conduit. Even if you could, in order to get there, you would have to run it through the same pathway as you would a new cable. Since it's not far, just run a new cable and get it over with correctly. My vote is for a 6/3 romex.I had a sparky looking at the panel/subpanel he said that the existing feed wires are 4awg and I can replace the quad breaker with double pole 60 amps to feed the subpanel and double pole 30 for the topstove. He also mentioned adding an extra single 4awg wire for the neutral. Does that sound code compliant?
Thanks a lot for confirming. That was my understanding per code all wires need to be contained.I don't remember ever seeing a 4/2 or 4/3 romex, but I've lived a sheltered life. It looks to me like the old #6 that had the TW insulation on it, and it could very well be. He's right that you can put a #4 on a 60, but he's wrong about adding an individual wire in addition to the romex for a neutral and if he told you that, get that and everything else he told you out of your head. Everything needs to be contained in the cable assembly or conduit. Even if you could, in order to get there, you would have to run it through the same pathway as you would a new cable. Since it's not far, just run a new cable and get it over with correctly. My vote is for a 6/3 romex.