Need help with wiring

To avoid these ads, REGISTER NOW!
OP
J

Jacks Garage

Member
Joined
Nov 23, 2014
Messages
5
Location
Danville Illinois
I will be running 5.5 HP air compressor, and small table saw, drill press, miter saw, etc. Just average homeowners tools, nothing big. Heater is a small propane portable unit. I will have about 6 or 8 four foot strip lights. Thanks for the help.
 

ez-duzit

Well-known member
Joined
Jun 24, 2013
Messages
5,104
Location
Marina del Rey
From the OP's original post.

I have a 200amp service going from the power pole to my house. From the house to the 24' x 24' garage i have 100amp service. I just had a 24' x 30' garage built 75' away from the first garage and i want 100amp service in it...

I take this to mean that each garage is to be capable of 100-amp service. My recommendations are based on this.

If a bunch of you are arguing that he can get away with a cheaper installation, where he has to turn everything off in one garage so he can run equipment in another garage, well, that is another story.

In my own garage, if my 7-1/2 hp air compressor comes on while I'm tig welding, my 100-amp panel is mostly maxed out, what with lights, etc. And I encourage the OP to not cheap out on the wiring. What will he save, 15' of wire?
 
OP
J

Jacks Garage

Member
Joined
Nov 23, 2014
Messages
5
Location
Danville Illinois
Well maybe I should feed off of the 200 amp house to run the 100 amp to the second garage. That way I wont have to replace anything in the first 100 amp garage. Would that be easier?
 

Coyote556

Well-known member
Joined
May 6, 2013
Messages
108
Location
The Show-Me State
Is the meter at the pole or the residence? Where I am it is common to have the meter at the pole and use a triple tap meter base to feed up to three structures. It is done all over our county. Cuts out the whole issue of subpanels run from the house main panel. Then each structure is fed off one leg of the triple tap meter base.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Well maybe I should feed off of the 200 amp house to run the 100 amp to the second garage. That way I wont have to replace anything in the first 100 amp garage. Would that be easier?

If now you're thinking the panel in the first garage would need to be changed, then yes it may be better to come off the main. Only you know how the feeder will need to be run from the main to get to the second garage.
 
OP
J

Jacks Garage

Member
Joined
Nov 23, 2014
Messages
5
Location
Danville Illinois
Is the meter at the pole or the residence? Where I am it is common to have the meter at the pole and use a triple tap meter base to feed up to three structures. It is done all over our county. Cuts out the whole issue of subpanels run from the house main panel. Then each structure is fed off one leg of the triple tap meter base.

The meter is at the house. Reason I wanted to run off the 1st garage is because there is a lot of landscaping and sidewalk that I will have to dig around and under.
 

JohnX14

Well-known member
Joined
Jun 2, 2014
Messages
608
Location
Boston 'burbs
Nope, #4 Cu is good up to 85A as a branch feeder and #2 Al is good to 90A.



Why do you continue to site just 60A for 2-2-2-4 MHF. #2 aluminum such as MHF can be over current protected up to 90 amps.

310.15 (B)(7)(2) allows for #4 Cu and #2 Al for the 100 amp installation described in the OP. There are a number of deviations allowed from Table 310.15(B)16. The 85 and 90 amps you cited are the general ratings of these conductors if no notes or correction factors apply.
 
To avoid these ads, REGISTER NOW!

canbug

Well-known member
Joined
May 6, 2008
Messages
337
Location
Just North of Cow Town
ez-duzit, your going to scare Jack to the point of not wiring his second garage. I have been an Electrician for 30 years and sub feeding from garage 1 to 2 will work fine. He isn't working in both garages at the same time and if the compressor in garage one starts up while he is in garage 2, the 100A isn't going to trip. Lets not overcomplicate this to death.

Tim.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,074
Location
Modesto, CA
ez-duzit, your going to scare Jack to the point of not wiring his second garage. I have been an Electrician for 30 years and sub feeding from garage 1 to 2 will work fine. He isn't working in both garages at the same time and if the compressor in garage one starts up while he is in garage 2, the 100A isn't going to trip. Lets not overcomplicate this to death.

Tim.

Dont woryy. Code enforcement officer C96 wil be along shortly to read ez-duzit his miranda rights and cuff him! :lol_hitti
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
It makes no difference if he plans on having only one 75-watt bulb on. Each 100-amp panel supply must safely carry its rated amps.

It does, the 100A breaker will trip if overloaded which I suspect will not be very likely.

310.15 (B)(7)(2) allows for #4 Cu and #2 Al for the 100 amp installation described in the OP. There are a number of deviations allowed from Table 310.15(B)16. The 85 and 90 amps you cited are the general ratings of these conductors if no notes or correction factors apply.

You need to read the criteria that goes along with that table, then you will know that your giving really bad advice, BTW that table has been removed from the 2014 NEC.
 
Last edited:

C96

Well-known member
Joined
Nov 30, 2013
Messages
1,251
Dont woryy. Code enforcement officer C96 wil be along shortly to read ez-duzit his miranda rights and cuff him! :lol_hitti

Yes, my bad, should have stepped in sooner.

ez-duzit needs a time out…:evil:

miranda.jpg

ez-d_zps2677c81e.jpg
 

C96

Well-known member
Joined
Nov 30, 2013
Messages
1,251
Oh, forgot to mention, nice bologna slab your sportin there ez-duzit :lol_hitti
 

ez-duzit

Well-known member
Joined
Jun 24, 2013
Messages
5,104
Location
Marina del Rey
If it can't be fixed with that hammer, it's an electrical problem. :)

Lots of ways one can compromise the addition of 2 sub-panels to a main panel. 1 of them is to make one sub-panel a sub-panel of a sub-panel. If you all contend that code allows you to get away with such an installation, very well. But no one can rationalize it just to save 15' of wire. And thus creating a power management problem. And unnecessarily limiting future expansion.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,074
Location
Modesto, CA
If it can't be fixed with that hammer, it's an electrical problem. :)

Lots of ways one can compromise the addition of 2 sub-panels to a main panel. 1 of them is to make one sub-panel a sub-panel of a sub-panel. If you all contend that code allows you to get away with such an installation, very well. But no one can rationalize it just to save 15' of wire. And thus creating a power management problem. And unnecessarily limiting future expansion.

I take it that youve never been in a plant where sub panels are fed from subpanels all over the place because the MDP is too far to run homeruns for each subpanel!
 