We don't even know if the 100A sub in garage 1 will accept a 100A breaker
We don't even know if the 100A sub in garage 1 will accept a 100A breaker
I have a 200amp service going from the power pole to my house. From the house to the 24' x 24' garage i have 100amp service. I just had a 24' x 30' garage built 75' away from the first garage and i want 100amp service in it...
Well maybe I should feed off of the 200 amp house to run the 100 amp to the second garage. That way I wont have to replace anything in the first 100 amp garage. Would that be easier?
Well maybe I should feed off of the 200 amp house to run the 100 amp to the second garage. That way I wont have to replace anything in the first 100 amp garage. Would that be easier?
Is the meter at the pole or the residence? Where I am it is common to have the meter at the pole and use a triple tap meter base to feed up to three structures. It is done all over our county. Cuts out the whole issue of subpanels run from the house main panel. Then each structure is fed off one leg of the triple tap meter base.
Nope, #4 Cu is good up to 85A as a branch feeder and #2 Al is good to 90A.
Why do you continue to site just 60A for 2-2-2-4 MHF. #2 aluminum such as MHF can be over current protected up to 90 amps.
ez-duzit, your going to scare Jack to the point of not wiring his second garage. I have been an Electrician for 30 years and sub feeding from garage 1 to 2 will work fine. He isn't working in both garages at the same time and if the compressor in garage one starts up while he is in garage 2, the 100A isn't going to trip. Lets not overcomplicate this to death.
Tim.

It makes no difference if he plans on having only one 75-watt bulb on. Each 100-amp panel supply must safely carry its rated amps.
310.15 (B)(7)(2) allows for #4 Cu and #2 Al for the 100 amp installation described in the OP. There are a number of deviations allowed from Table 310.15(B)16. The 85 and 90 amps you cited are the general ratings of these conductors if no notes or correction factors apply.
Dont woryy. Code enforcement officer C96 wil be along shortly to read ez-duzit his miranda rights and cuff him!![]()

If it can't be fixed with that hammer, it's an electrical problem.
Lots of ways one can compromise the addition of 2 sub-panels to a main panel. 1 of them is to make one sub-panel a sub-panel of a sub-panel. If you all contend that code allows you to get away with such an installation, very well. But no one can rationalize it just to save 15' of wire. And thus creating a power management problem. And unnecessarily limiting future expansion.