Need some 220v electrical connection advise
remagenman
Hello folks, figured I'd ask some bonafide electrical gurus on my planned set up for the garage.
I have 3 machines at 220v that I want to use (one at a time) and connect to the same receptacle when I want to use. An electric ceramic kiln rated at 15A, a vintage wood planer rated at 25.6A and a Lincoln 225ac 50A stick welder with a NEMA 6-50 plug.
-Kiln has a 10-50P plug
-Planer has a 10-20P plug
-Stick welder has a 6-50P Plug.
So in a nutshell, can I just connect a 50A breaker and outlet connection for 6-50P and rewire the other plugs for 6-50P to connect to the same outlet location?
Thanks ahead of time.
sberry
Brethren, Michigan
Each one needs different over current according to the plug that comes on it. I agree, good place for a simple panel fed with 6. That kiln may have the wrong plug on it.
It this attactched or detatched garage, etc.
pattenp
Virginia - USA
If putting in a new circuit that the kiln will use the cord should be switched to a 14 series. The 10 series are ungrounded where the neutral is bonded at the unit. Also I'd consider changing the plug on the planner to a 6-30 on a 30A circuit if it's really listed as 25.6A. I'm not sure why there is a 10-20 on the planner. Or do you have some of those numbers backwards?
Geez the first 2 have the wrong plugs on them.
I agree with PATTENP
Does the kiln have 120v controls? If so it should have a NEMA 14-15p. If not then 6-15p.
The planer should have a nema 6-30p.
And the welder is correct.
These all need separate circuits.
Dont put them all on the same circuit.
R
remagenman
Thanks to all for the replies and thats why I ask these things.
The planers data plate says VOLTS 115/230, AMP 25.6/12.8 (now I think I misquoted the earlier Planer 220v amps) PH1 with 10-20P plug.
The kilns data plate says 120/240/3W Phase 1 but wired with the 10-50P plug and all information point at it being 240v.
Planer plug: https://imgur.com/BqC5ICI
Kiln plug: https://imgur.com/YhNTH8n
The planer is an older Parks style planer with thick gauge wiring and used to belong to a shop teacher. I took of the motor plate but the wiring doesnt make sense to me to be able to tell if it is 110 or 220 volts wired. I was planning on doing a "plug it into a 110v outlet first and see if it bogs or runs" test. Not very scientific but I think field expedient.
The pics didnt load
Planner if wired for 240v should be 6-15p then....
Kiln should be 6-15p as well unless it has 120v comtrols which then should be 14-15p...
Only thing that could and can have a 6-50p is the welder
R
remagenman
The pics didnt load
Thanks, pics link directly to imgur, tried to edit but pics dont show.
So would you suggest Kiln and Planer re-wired to 6-15p plug and ran from a dedicated 20amp breaker outlet and Welder ran from a dedicated 50amp breaker outlet?
I'll be using these one at a time when needed.
matt_i
I would build overcurrent protection into each machine other than the welder. A 6 inch square NEMA-1 square box you get at the home depot, some old school time-delay fuses and a 2 pole fuse holder. Breaker protects the hard-wiring, fuses protect the machine.
The one missing link is the cords, and if those are molded 6-50 cordsets (like you'd buy to hookup an electric range) they should have the appropriate wire gauge already to handle the current.
sberry
Brethren, Michigan
You can do that but simple breaker can work.
I don't recall about kilns,, are they dual voltage and 15A seems small. Most I have seen are 50A, I am sure there are smaller ones.
R
remagenman
Yeah, it's a small kiln. Think my setup would work?