Need your help with garage heater questions please

996scott

Member
Joined
Oct 8, 2006
Messages
8
I'm in the process of building a new home with a 4 car garage. I would like to heat it with a Mr. heater or Hot Dawg. I will have a gas line run into the garage, but I am very confused about the venting. I hope someone can help me. I guess I will need a vent kit so the exaust from the unit can vent to the outside, but do I ALSO need another kit to bring fresh air to the unit? Also, is there a maximum distance the unit can be from venting to the outside? If I put it in the middle of the garage it may have to travel 25 ft. Thanks for the help. Scott
 
To avoid these ads, REGISTER NOW!

beetroot72

Well-known member
Joined
Dec 4, 2006
Messages
150
Location
McHenry, Illinois
Vent it vertically if you can. B-pipe is very expensive! You want to stay as short as possible. Most models do not require "fresh air". Unless you want it or require it for some reason, you will have to buy a specific model. Venting is pretty easy. Find a local Furnace supply company, go to their "will call" and tell them what you want to do. You'll need to know the roof pitch (how many inches of rise per foot) to determine what kind of flashing needed. Mr heater and Hot dawg have a 3" vent, which you can stick with if you vent vertically. Otherwise (look in the manual) you'll need 4 or 5 inch to vent horizontally. Word to the wise..If you live in illinois do not buy the Hot Dawg.
 

Attachments

  • DSC03103.JPG
    DSC03103.JPG
    39.5 KB · Views: 58
  • DSC03101.JPG
    DSC03101.JPG
    47.5 KB · Views: 55
  • DSC03117.jpg
    DSC03117.jpg
    67.5 KB · Views: 50

beetroot72

Well-known member
Joined
Dec 4, 2006
Messages
150
Location
McHenry, Illinois
Very long Story....Modine blames Illinois' "Dirty Power" We have found in the Illinois area that we are have a power problem with your power supply company. What happens is there is an interruption of power "dirty power" and it's enough to close a set of contacts to turn the power exhauster on. Please contact Ron at Heinlein Supply 773-774-8616, and ask him to send you out a new wiring harness for the HD units. This harness will take care of the issue. If you need more help let me know.

Modine Manufacturing Company
Commercial HVAC&R Division

Jamie Tuinstra
Technical Service/Quality specialist

1500 DeKoven Avenue
Racine, Wisconsin 53403-2552
Tel. 800-828-4328
Fax 262-636-1665

Installed HD45 12/15/06 -
Model# - 45AH0134
Ser# - 38011033606-0551

• Monday 12-18-06 Informed of Revised Wire Harness to fix Exhaust motor.
• Contacted Ron @ HeinLein Supply 773.774.8616 - Revised Harness out of stock
• Brian @ Modine Will have one Aired Wednesday for Thursday Delivery.
12-20-06 Received New Harness - Have same problem when on call for heat - seems to only be during purge.
• 01-01-07 - Noticed burners turning off/on during heat cycle. Seems to be from cycling exhaust motor.

• 01-2-07 - Talked with Brian and other rep. Recommended new "Manual" Honeywell T-Stat and to jump the T-stat leads.
• 01-03-07 - Jumped terminals - seemed worse. - Installed new T-stat - same problems.
• 01-04-07 - Talked w/ Brian and Rep from ??? Sending New Valve, Board, & Harness
• 01-08-07 - received Valve and Board (No Harness)
• 01-09-07 - Left VM for Brian, informing on lack of new harness
• 01-10-07 - New board and Valve installed
• 01-13-07 - Acted up again - Jumped t-stat at board - checked 120v wiring/ground connections - pulled off tee cap in vent.
• 01-15-07 - Talked with Jon and Brian - Sending New Unit.
• 01-18-07 - Received UPS Return Labels
• 01-19-07 - Received New Unit - Beat up packaging, Dented Panel, Fins, Springs fell off.
• 01-20-07 - Installed new unit - Pressure switch fault on initial cycle. Refitted hose…fixed.
• 01-20-07 - Rollout/limit fault occurred a few times…????
• 01-22-07 - Returned original unit via ups Tracking# 1z5809779042290496
• 01-23-07 - Verified Delivery @ 7:48 am Signed by Hoechel.
• 02-25-07 - Still having problems, decided to call Bryan
• 02-26-07 - Talked w/Bryan, John - Tried Heat anticipator - nope
• 02-27-07 - Talked w/Bryan - Suggested taking off t-cap.
• 03-04-07 - Pulled off t-cap during malfunction to "open vent" still problems without even making it to ignition.
• 03-05-07 - Talked w/Bryan - Sent install pictures - Says it looks good to him.
• 03-10-07 - Bypass main switch - No better • Ran Electrical from alternative outlet on different breaker - No better
• 03-15-07 - Sent Video file of unit malfunctioning via USPS

And I'm still with a crappy unit. They said they would send someone out from Virginia but they pulled out of that. Now they're in the process of possibly taking it back and giving me my money back. I will then buy the Mr Heater.
 
To avoid these ads, REGISTER NOW!

Kinger

Well-known member
Joined
Oct 6, 2006
Messages
81
Location
Southern WI
beetroot72 said:
Very long Story....Modine blames Illinois' "Dirty Power" We have found in the Illinois area that we are have a power problem with your power supply company. What happens is there is an interruption of power "dirty power" and it's enough to close a set of contacts to turn the power exhauster on. Please contact Ron at Heinlein Supply 773-774-8616, and ask him to send you out a new wiring harness for the HD units. This harness will take care of the issue. If you need more help let me know.

Modine Manufacturing Company
Commercial HVAC&R Division

Jamie Tuinstra
Technical Service/Quality specialist

1500 DeKoven Avenue
Racine, Wisconsin 53403-2552
Tel. 800-828-4328
Fax 262-636-1665

Installed HD45 12/15/06 -
Model# - 45AH0134
Ser# - 38011033606-0551

• Monday 12-18-06 Informed of Revised Wire Harness to fix Exhaust motor.
• Contacted Ron @ HeinLein Supply 773.774.8616 - Revised Harness out of stock
• Brian @ Modine Will have one Aired Wednesday for Thursday Delivery.
12-20-06 Received New Harness - Have same problem when on call for heat - seems to only be during purge.
• 01-01-07 - Noticed burners turning off/on during heat cycle. Seems to be from cycling exhaust motor.

• 01-2-07 - Talked with Brian and other rep. Recommended new "Manual" Honeywell T-Stat and to jump the T-stat leads.
• 01-03-07 - Jumped terminals - seemed worse. - Installed new T-stat - same problems.
• 01-04-07 - Talked w/ Brian and Rep from ??? Sending New Valve, Board, & Harness
• 01-08-07 - received Valve and Board (No Harness)
• 01-09-07 - Left VM for Brian, informing on lack of new harness
• 01-10-07 - New board and Valve installed
• 01-13-07 - Acted up again - Jumped t-stat at board - checked 120v wiring/ground connections - pulled off tee cap in vent.
• 01-15-07 - Talked with Jon and Brian - Sending New Unit.
• 01-18-07 - Received UPS Return Labels
• 01-19-07 - Received New Unit - Beat up packaging, Dented Panel, Fins, Springs fell off.
• 01-20-07 - Installed new unit - Pressure switch fault on initial cycle. Refitted hose…fixed.
• 01-20-07 - Rollout/limit fault occurred a few times…????
• 01-22-07 - Returned original unit via ups Tracking# 1z5809779042290496
• 01-23-07 - Verified Delivery @ 7:48 am Signed by Hoechel.
• 02-25-07 - Still having problems, decided to call Bryan
• 02-26-07 - Talked w/Bryan, John - Tried Heat anticipator - nope
• 02-27-07 - Talked w/Bryan - Suggested taking off t-cap.
• 03-04-07 - Pulled off t-cap during malfunction to "open vent" still problems without even making it to ignition.
• 03-05-07 - Talked w/Bryan - Sent install pictures - Says it looks good to him.
• 03-10-07 - Bypass main switch - No better • Ran Electrical from alternative outlet on different breaker - No better
• 03-15-07 - Sent Video file of unit malfunctioning via USPS

And I'm still with a crappy unit. They said they would send someone out from Virginia but they pulled out of that. Now they're in the process of possibly taking it back and giving me my money back. I will then buy the Mr Heater.

Thanks for the explanation. Sorry to hear that you are having so much trouble. Glad I moved to WI about 12 years ago.:lol_hitti
 
OP
9

996scott

Member
Joined
Oct 8, 2006
Messages
8
Beetroot72, thanks for the response. I talked to my contractor today and we dicided that what we probably will do is run a vertical vent adjacent to the direct vent fireplace we are doing. We can run both the vent tubes ( 3 inch for the heater and 8 inch for the fireplace) together and out the chimney. Anyone see any problems with this? So if we do a vertical vent I only need to use a 3inch and not a 5? Thanks again.
 

beetroot72

Well-known member
Joined
Dec 4, 2006
Messages
150
Location
McHenry, Illinois
996scott said:
Beetroot72, thanks for the response. I talked to my contractor today and we dicided that what we probably will do is run a vertical vent adjacent to the direct vent fireplace we are doing. We can run both the vent tubes ( 3 inch for the heater and 8 inch for the fireplace) together and out the chimney. Anyone see any problems with this? So if we do a vertical vent I only need to use a 3inch and not a 5? Thanks again.

I have PDF's of both the Modine and the Mr. Heater They have all the specifics you need...

http://www.mrheater.com/upload/newsletter/60016_mhu_hsu_45_75.pdf


http://www.gas-space-heater.com/pdf/modine-install.pdf
 