Is it normal to have the ground and neutral connected on this receptacle?
My parents just bought a dryer and I was looking at the receptacle on the wall.

Sent from my DROID RAZR using Tapatalk
 

Attachments

  • uploadfromtaptalk1385059447905.jpg
    uploadfromtaptalk1385059447905.jpg
    41.7 KB · Views: 45
To avoid these ads, REGISTER NOW!

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
It used to be dryers/dryer outlets were 3-wire.

Since you have a neutral and ground on the receptacle end, you'll want to upgrade that to a 4-wire outlet which will split the two.

The dryer if it's been installed already will need a new 4-wire cordset, and you may need to remove a jumper where the cord is wired to the dryer so that the neutral and ground are disconnected. Usually though, you'll just use a different lug when you connect the cord to the new dryer.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
If you leave the 3 prong outlet as is the ground needs to be removed. That's an ungrounded outlet. You don't want a bare wire being used as a neutral. Just disconnect the ground from the outlet and tape it up and push it to the bottom out of the way.
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,795
If you leave the 3 prong outlet as is the ground needs to be removed. That's an ungrounded outlet. You don't want a bare wire being used as a neutral. Just disconnect the ground from the outlet and tape it up and push it to the bottom out of the way.



The metal of that receptacle needs to be bonded, so the OP would not push it out of the way.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I thought about that after I said move it out of the way because it's an ungrounded outlet and has a plastic cover. But, yes technically the metal should be grounded. But, I have seen many of the old ungrounded receptacles like that where the metal back plate is not bonded.

The back plate is stamped with the word "Ground".

The metal of that receptacle needs to be bonded, so the OP would not push it out of the way.
 