New compressor outlet
jumpstart
Central MA
I'm looking to install a compressor outlet in my detached garage.
Does the compressor outlet need to be GFCI protected? All the 15amp and 20 amp are, but not sure if required on a 220v/30amp.
pattenp
Virginia - USA
240V outlets are not required to be GFCI protected. As a side note, compressors with motors larger than 3HP need to be hardwired, no plug and outlet.
J
jumpstart
Central MA
pattenp
Virginia - USA
You need a 10 cable to a 30 recept. If it was hard wired may require less.
If it's a single receptacle on an individual circuit its amp rating is not to be less than the circuit. Nothing says the receptacle can't have a higher amp rating than the circuit. NEC 210.21(B)(1)
J
jumpstart
Central MA
Maybe I should back up a bit. My original question of GFCI or not is cleared up.
This is an old Wayne compressor that I don't know the history on. It has a long cord with a plug on the end rated for 250v/20amp. I thought it was 30amp. I'll get my eyes checked soon.
Now that I've looked at the motor plate, I'm not sure if the 20amp plug is what I really need, or if it should be changed to a higher amp rating. Here's the plate -
View media item 91073
Again it will be wired for 220v.
sberry
Brethren, Michigan
I guess what I might have meant to say is a 30 recept and a 30 breaker it needs 10 wire. If it was hard wired the wire might be smaller than the breaker.
mike93lx
Richmond, VA
Why the 4 wire receptacle? Seems like just 2 hots and a ground is sufficient. Unless an dryer will end up there.
the receptacle linked is 125/250V, requiring 4 wires. I think the point of posting it is that there are receptacles rated at higher than 3HP, not as a suggestion to the OP.
alfredeneuman
Fullerton, CA
Yes, it's why I posted it, not as a suggestion for the OP.
A blanket rule by some at GJ that "any compressor over 3HP must be hardwired" is bad advice in my opinion.
Even higher HP receptacles are available with pin & sleeve designs, but cost mega $$, and would economically counterproductive.
pattenp
Virginia - USA
I can't say it's bad advise, it's more of suggested economical advice. Pin & Sleeve has been noted many times before as an option. We just need to set our HP higher than 3.5 for suggesting hardwiring. :)