I'm looking to install a compressor outlet in my detached garage.

Does the compressor outlet need to be GFCI protected? All the 15amp and 20 amp are, but not sure if required on a 220v/30amp.
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
240V outlets are not required to be GFCI protected. As a side note, compressors with motors larger than 3HP need to be hardwired, no plug and outlet.
 
OP
J

jumpstart

Well-known member
Joined
Jan 11, 2009
Messages
401
Location
Central MA

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
You need a 10 cable to a 30 recept. If it was hard wired may require less.

If it's a single receptacle on an individual circuit its amp rating is not to be less than the circuit. Nothing says the receptacle can't have a higher amp rating than the circuit. NEC 210.21(B)(1)
 
OP
J

jumpstart

Well-known member
Joined
Jan 11, 2009
Messages
401
Location
Central MA
Maybe I should back up a bit. My original question of GFCI or not is cleared up.

This is an old Wayne compressor that I don't know the history on. It has a long cord with a plug on the end rated for 250v/20amp. I thought it was 30amp. I'll get my eyes checked soon.

Now that I've looked at the motor plate, I'm not sure if the 20amp plug is what I really need, or if it should be changed to a higher amp rating. Here's the plate -
View media item 91073
Again it will be wired for 220v.
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
If it's a single receptacle on an individual circuit its amp rating is not to be less than the circuit. Nothing says the receptacle can't have a higher amp rating than the circuit. NEC 210.21(B)(1)

I guess what I might have meant to say is a 30 recept and a 30 breaker it needs 10 wire. If it was hard wired the wire might be smaller than the breaker.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,574
Location
Richmond, VA
Why the 4 wire receptacle? Seems like just 2 hots and a ground is sufficient. Unless an dryer will end up there.

the receptacle linked is 125/250V, requiring 4 wires. I think the point of posting it is that there are receptacles rated at higher than 3HP, not as a suggestion to the OP.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
Yes, it's why I posted it, not as a suggestion for the OP.
A blanket rule by some at GJ that "any compressor over 3HP must be hardwired" is bad advice in my opinion.
Even higher HP receptacles are available with pin & sleeve designs, but cost mega $$, and would economically counterproductive.
 
Last edited:

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Yes, it's why I posted it, not as a suggestion for the OP.
A blanket rule by some at GJ that "any compressor over 3HP must be hardwired" is bad advice in my opinion.
Even higher HP receptacles are available with pin & sleeve designs, but cost mega $$, and would economically counterproductive.

I can't say it's bad advise, it's more of suggested economical advice. Pin & Sleeve has been noted many times before as an option. We just need to set our HP higher than 3.5 for suggesting hardwiring. :)
 