new install, wiring & control questions

87jeepwrangler

Well-known member
Joined
May 23, 2013
Messages
195
I’ve been working on installing a weil-mcclain gold oil burner for my house and garage. I got the heater and burner as a freebie from a friend who changed over to a natural gas setup. It is only a few years old.

Another buddy is a HVAC guy/plumber, and he’s been advising me on the install from the beginning. He is going to look over all my work and help me fire it up next week, but I want to get some opinions on the best way to wire up my system before I get his opinion on that part. After all my reading, it seems like there is more than one way to do this. I also want to leave my options open for some future expansion to the system I have in mind.

I have a Taco ZVC406 zone controller, a beckett aquasmart aquastat, 1 circulator pump, a beckett burner, and Honeywell zone valves. At this time, I will only be using 1 circulator pump and 2 of the zones, however, I will be adding the following at later dates:

1 garage zone with a hanging heater equipped with a small 1/25 hp fan.
1 heated floor zone (which is my understanding that it will essentially require it’s own circulator of sorts)
Although I may never actually add it, theoretically 1 indirect fired water heater (IF I ever add this, I would more than likely use zone 6 on the Taco controller as a priority zone).

Here’s what I have so far:
Hot leg from service switch to Taco zone controller, and from service switch to aquastat, all landed.
Thermostat wire from thermostats, to taco controller, all landed.
Thermostat wire from taco controller, to each zone valve, all landed.

Whats the best way to power the circulator pump? From the Taco controller? From the aquastat?
Although I’m not hooking it up yet, where would I want to power the garage heater fan from? and the in-floor circulator?
other thoughts on wiring?
Thanks.

heater.jpg

Beckett-aquasmart.jpg

TacoZVC406.jpg
 
Last edited:
To avoid these ads, REGISTER NOW!

JackDiddly

Well-known member
Joined
Oct 6, 2014
Messages
185
Location
SE WI
That Beckett aqua-stat has contacts for a circ. pump. I would run your pump from the aqua-stat contacts and just bring your end switch from zone board to aqua-stat at least until you start adding more pumps for future alterations to the system. Having the zone board will be a huge time saver in the event of additions.
 
To avoid these ads, REGISTER NOW!

anthony666

Well-known member
Joined
Dec 29, 2007
Messages
987
Location
kirkfield ontario
i like to wire everything through the taco box, keeps it all organized .. even though your outs are all low voltage for zone valves, you can wire line voltage through end switches over on the lower left side of the box .. or you can take one of the 24 volt outs and use that to trigger a second taco box
 