The book arrived... very helpful. Read through it all.
A while ago my older brother suggested that I run two 120v "legs" from the house - this means I would install:
60A dual breaker in the house, 2 hot wires -> to barn
One neutral wire from buss bar in house -> to barn
Ground wire -> to barn (is the separate ground wire necessary?)
@ barn
separate ground rod (actually two to avoid testing for resistance, spaced 6' apart)
All encased in a PVC conduit 18" from the top of the conduit.
================ Some questions ===============
Wire from house to barn:
I'm a bit confused about when I need to ground the bussbar in the barn? Based on what I read - it should NOT be grounded?
When would I want to use direct-burial cable, and when would I decide to run it in conduit?
I have a distance of max 150 feet from the house breaker out to the barn. To support 100A in the future, and allowing for up to a 2% drop, it looks like I would need to run 1/0 wire, in a 2" PVC conduit.
At the barn:
It says in a few places lighting must be provided at every entrance - I have a light installed above the side door, but not the big garage door. Is the garage door considered an entrance? Would spillover light from the light over the side door be sufficient.