Hey I'm looking for some help picking the right size wire for my shop.
My property has a 50 amp service currently
My shop is 200 ft away from my house.
I have dug a trench but im getting different wire sizes from the apps somwantbsome real life help from someone doing he same thing
I would like to have a 50 amp breaker in the shop.
I will be running 2 2500 watt water bowl heaters all winter and need to have a few plugs and yard light. Please let me know your thoughts on it and your experience is also helpful Thanks
 
To avoid these ads, REGISTER NOW!

corvette43056

Well-known member
Joined
Mar 24, 2019
Messages
49
Location
ohio
Ok so you have 100 or 200 amp to house just using 50 amp breaker

Sent from my SM-N960U using Tapatalk
 

corvette43056

Well-known member
Joined
Mar 24, 2019
Messages
49
Location
ohio
U can use this probably over kill but direct bury
6406404b69977fcd2bc7e8cc6d3b8082.jpg


Sent from my SM-N960U using Tapatalk
 
OP
S

Shopbuilder

New member
Joined
Nov 26, 2019
Messages
3
Location
Alberta
I only have a 50 amp service to my farm right know. I have run a larger wire to accomadate a 100 amp service but don't have the permit to upgrade it yet with the electrical provider. I have 50 amps going to the house so I hoped to have 50 amps to the shop too. I should have a 100 amp service in the next 3 months they said.
 

corvette43056

Well-known member
Joined
Mar 24, 2019
Messages
49
Location
ohio
Use that wire I have 200 amp too house 100 amp to garage about 60 ft.

Sent from my SM-N960U using Tapatalk
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
U can use this probably over kill but direct bury
6406404b69977fcd2bc7e8cc6d3b8082.jpg


Sent from my SM-N960U using Tapatalk

Just for information, the wire pictured is URD and is only allowed to be installed outside of the structure. It does not have fire resistant insulation for interior installation.
 

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California
Welp, this is a bit of a mess.

But lets assume you will eventually put in a 100 or 200 A service at the main house. (Your statement of "I should have a 100 amp service in the next 3 months they said." is odd...'they said'? How does a service just get upgraded at your home by unknown people at some unknown point in time? But anyway...)

Throw conduit in the ground, 200 ft, #4 copper wire. 3 pieces of #4, one of #6 for ground. You can use AL...upsize it to #2.

Dont listen to the poster corvette43056 above..he is giving you bad advice. #4 Al for his 100Amp service?
 

OptionalStop

Well-known member
Joined
Mar 23, 2018
Messages
128
Location
Rochester NY
Just for information, the wire pictured is URD and is only allowed to be installed outside of the structure. It does not have fire resistant insulation for interior installation.

I knew this would come up after seeing that wire.

I used URD and passed my inspection 3 weeks ago.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,220
Location
Modesto, CA
I only have a 50 amp service to my farm right know. I have run a larger wire to accomadate a 100 amp service but don't have the permit to upgrade it yet with the electrical provider. I have 50 amps going to the house so I hoped to have 50 amps to the shop too. I should have a 100 amp service in the next 3 months they said.

The issue you may run into is the existing loads on your house.

So what loads do you have in your house?
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
Just for information, the wire pictured is URD and is only allowed to be installed outside of the structure. It does not have fire resistant insulation for interior installation.

Just to add to that, the URD pictured just has a USE-2 rating, which cannot be installed above ground or enter a structure in any way, even in conduit. There is also URD that is dual rated, it also carries a RHH/RHW-2 rating, which can enter a structure as long as it is in a raceway.
 
Last edited:

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California
I knew this would come up after seeing that wire.

I used URD and passed my inspection 3 weeks ago.

I can list half a dozen inspection violations the inspector missed on my last home final. Becuase he missed them doesnt mean they dont exist.

IMO the idea is to build homes that meet code...not pass inspection.



Finally, there was a local home where the county inspector blew it. Total failure/rot/mildew of the crawl space leading to massive losses. Inspector and county were cleaved from the lawsuit by the courts- governmental immunity. The person(s) that did the work were held liable....So an inspection 'ticket' isnt a get out of jail card.
 