Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,796
Underground, & outdoor, conduits are wet locations as defined by the NEC, & NM is allowed in dry locations only.
 
To avoid these ads, REGISTER NOW!

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,271
Location
Penngrove, California
Sounds like this is a detached building.
What is it being fed from, and what is length of run?
Assuming you want 120/240 VAC you will need 3 current carrying conductors and ground.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,275
Location
Modesto, CA
I would figure out the length and then compare the cost of THHN vs. UF-b...u need 3 runs of #8(unless the length is long) and one run of #10 for ground...
 