Sounds like this is a detached building.
What is it being fed from, and what is length of run?
Assuming you want 120/240 VAC you will need 3 current carrying conductors and ground.
I would figure out the length and then compare the cost of THHN vs. UF-b...u need 3 runs of #8(unless the length is long) and one run of #10 for ground...
I would figure out the length and then compare the cost of THHN vs. UF-b...u need 3 runs of #8(unless the length is long) and one run of #10 for ground...