No ground outlet
FMC1959
Montreal, Canada / Upstate NY
I am sure this has been discussed, but I did some searches and could not find my exact situation.
I have a very old house. I would say about a third of the outlets are 2 wire and no ground. In some instances, it is possible to run a ground to the outlet. Where it is not easy without ripping out the wall, can replacing the standard receptacle with a GFCI work? Would the GFCI cover all the safety needs that a ground does, and is it legal according to code? How would the GFCI be wired, just black to hot, white to neutral and leave the ground lug empty? GFCI's typically cover outlet downstream, in this case would it also cover downstream outlets with no ground?
rlitman
Long Island
... can replacing the standard receptacle with a GFCI work? Would the GFCI cover all the safety needs that a ground does, and is it legal according to code? How would the GFCI be wired, just black to hot, white to neutral and leave the ground lug empty? GFCI's typically cover outlet downstream, in this case would it also cover downstream outlets with no ground?
Yes. Yes. Exactly. GFCIs only protect downstream outlets when those are wired via the "load" connections. If you do that, you can install standard grounded outlets on the downstream protected side, provided you place the stickers on them that state they are GFCI protected.
cgrutt
Im not an electrician but understand the GFCI will work without having a ground and will offer protection to downstream ungrounded outlets if wired properly. It won't provide a true ground path however so equipment plugged into those outlets will still not have a ground pathway if there's internal fault.
F
FMC1959
"however so equipment plugged into those outlets will still not have a ground pathway if there's internal fault." OK, so what does this mean regarding safety for people and the equipment.
rlitman
Long Island
Absolutely nothing. You're 100% safer with a GFCI protected ungrounded appliance than a grounded appliance without GFCI protection.
cgrutt
People would likely be protected from severe shock. Equipment, esp sensitive electronics e.g. tvs, computers, cameras, alarms, etc may not be protected from electrical surges. Built in surge suppression etc may not work. All I was saying is installing a GFCI on ungrounded outlets doesn't provide a ground pathway.
rlitman
Long Island
Right. 2/3 of a surge protector's ability would be cut off by removing the ground path (because you lose the L-G and N-G pathways, but you do still have the L-N path). It's not remotely a life safety issue, and if you have surge protection at the panel it probably doesn't even matter, but yes, without a good ground path, a surge strip doesn't work very well.
cgrutt
I never said it was a life safety issue and stated it would provide GFCI protection to downstream outlets.
First, the original purpose of the ground wire was so if the appliance shorted the hot to the case (think toaster) and you touched the case, YOU did not become the "path of least resistance" to ground !
Second, (at least in theory) a GFCI works by comparing the amount of CURRENT going through the "hot" lead and then returning on the neutral lead. It trips if they are different. So if a person provides a path to ground, then some current will not be on the return lead.
Wrench97
Southeastern Pa
If the device is not 3 prong don't worry about the ground it doesn't need or use one.
If you are using it for A/C window units or grounded computer equipment I would run a new wire with a ground or install a new outlet as older homes never have enough outlets per room normally.
F
FMC1959
My walls are sometimes sheetrock, otherwise plaster, on lathe and a sub panel of 1" think wood. Many walls have shredded newspaper for insulation. Like I stated at the outset, I would add a wire if it was not very complicated.
Not always true. equipment that needs a ground wire to function properly such as a surge arrestor, UPS etc, will not work properly or be 100% safer with a GFCI vs a properly grounded receptacle.
walta
Dutzow Missouri
I am not the code expert but from what I understand, adding a single grounding conductor wire and still using the existing wires for hot and neutral is technically possible in a code compliant way it is almost impossible to actually make it happen.
I think the rules require the new wire to follow the same path as the original within a few inches. Finding single conductor wire that is rated for use outside of conduit seems unlikely. Maybe one of the expert will tell us more.
If I misunderstood and your plan is to abandon /replace the old cable and bring that circuit up to the current code that is a much better plan.
Walta
F
FMC1959
Surge arrestor. I have an APC, 10 foot cord and decent features, I would say medium duty. Plugged into a GFCI outlet that does not have a ground. It will work as a power bar, but the surge arrestor protection is lost, is that what you are saying?
mm08822
There would only be protection between hot and neutral.
Nothing between hot - grd or neutral to grd.
F
FMC1959
What does this mean in layman terms?
To me a surge suppressor is supposed to save delicate equipment from electrical spikes or surges when there are power failures, or when the power flickers. So how does this translate to "There would only be protection between hot and neutral. Nothing between hot - grd or neutral to grd." I understand the very basic concept of a surge when power comes back on, what you say hot & neutral & grd ,I do not understand. The equipment is protected or it is not protected?
cgrutt
Sorry but it depends. Generally, surge protectors work by diverting voltage spikes (from lightening, etc) to ground, so with no ground your sensitive electronics may not be protected. Believe specialized surge protectors are available that divert surges through neutral wire but not sure how effective these are. UPS systems may absorb small surges but generally believe these often require equipment ground as well.
If there is a surge, it wont be able to shunt it to grnd.
This is why surge arrestors, UPSs etc typically have a building wiring fault indicator on them to alert you to an issue with the grnd connection on the receptacle.
Theres several protections in a UPS and surge arrestor. Thats why he stated that
F
FMC1959
OK, all good to know information. Anything sensitive that really needs a surge protector, I will make sure it is on a properly grounded outlet. Anything ungrounded, I will install GFCI's and only plug in stuff that is either not sensitive or not expensive if it gets blown., like fans, lights, radios, ...etc.
trashfire10
AND a sticker that says "No Equipment Ground."
In most normal outlets around your home how many 3 prong devices do you have plugged in?
Surprisingly, a lot !
At my daughters first house, none of the outlets were grounded. In the "home office", the power strip for all of the computer stuff had a ground pin as did many of the devices.
Same was true in the living room. Needed a power strip for TV, stereo, game console, etc.
I really despise those stupid 3 to 2 prong adapters. They tend to fall out of the receptacle.
mikedodge
Computer stuff usually is grounded but it doesn't matter if the power strip for the TV is grounded when none of the stuff plugged into it is grounded.
Part of our house is in the same situation without the outlets having a ground to connect to. For any place that it's been needed a GFCI was installed but other then that it's never been an issue and we weren't going to rewire everything for it.
F
FMC1959
What is IF? Your way of saving face? I previously asked for clarification on surge protectors, and I started this thread. If someone puts a hole in your comment, no need to make a childish comment to show you did not know the correct answer. Thanks again to wyliesdiesels for his expertise and clarification.
mikedodge
Save face on what??? I said exactly what I meant. It was already stated that something needs to be grounded IF it's being used as a surge suppressor. The comment I quoted said nothing about that and was only about devices with a ground pin in general. No mention at all if that power strip is being used for that purpose or not. So IF.
Keep up your own childish comments, must make you feel good.
cpakalolo
The NEC provides an allowance for GFCI to be used on two wire outlets. The NEC also says that you can run a ground wire on the outside of the house and extend it into each outlet. The only time I have changed a whole house to GFCI was my own. It was just temporary until I did a re-wire for the whole house. I would go with the GFCI over the extra ground because you would have to invent some things to do it I imagine. The reason the law goes into your home here is because you will eventually sell and they also care about your family. My father sold his farm and I can't imagine what the new owner is going through because the electrical and plumbing are atrocious. I ran some of that stuff when I was a kid.
mikedodge
No problem, I should have been less hard.
it's all good. I think it would have helped if the forum actually included the quotes from the reply that someone is quoting. It seems like sometimes some of the context behind peoples replies gets lost.
Wrench97
Southeastern Pa
Use the +quote button to include multiple quotes.
mikedodge
Then you have to manually add them and make sure the forum didn't mess up the order. Not worth the time. Most forums if you quote a reply that has quotes in it it includes them automatically.
