No ground outlet

FMC1959

Well-known member
Joined
Feb 9, 2014
Messages
2,317
Location
Montreal, Canada / Upstate NY
I am sure this has been discussed, but I did some searches and could not find my exact situation.

I have a very old house. I would say about a third of the outlets are 2 wire and no ground. In some instances, it is possible to run a ground to the outlet. Where it is not easy without ripping out the wall, can replacing the standard receptacle with a GFCI work? Would the GFCI cover all the safety needs that a ground does, and is it legal according to code? How would the GFCI be wired, just black to hot, white to neutral and leave the ground lug empty? GFCI's typically cover outlet downstream, in this case would it also cover downstream outlets with no ground?
 
To avoid these ads, REGISTER NOW!

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,596
Location
Long Island
... can replacing the standard receptacle with a GFCI work? Would the GFCI cover all the safety needs that a ground does, and is it legal according to code? How would the GFCI be wired, just black to hot, white to neutral and leave the ground lug empty? GFCI's typically cover outlet downstream, in this case would it also cover downstream outlets with no ground?
Yes. Yes. Exactly. GFCIs only protect downstream outlets when those are wired via the "load" connections. If you do that, you can install standard grounded outlets on the downstream protected side, provided you place the stickers on them that state they are GFCI protected.
 

cgrutt

Well-known member
Joined
Mar 4, 2016
Messages
8,243
Im not an electrician but understand the GFCI will work without having a ground and will offer protection to downstream ungrounded outlets if wired properly. It won't provide a true ground path however so equipment plugged into those outlets will still not have a ground pathway if there's internal fault.
 
OP
F

FMC1959

Well-known member
Joined
Feb 9, 2014
Messages
2,317
Location
Montreal, Canada / Upstate NY
Im not an electrician but understand the GFCI will work without having a ground and will offer protection to downstream ungrounded outlets if wired properly. It won't provide a true ground path however so equipment plugged into those outlets will still not have a ground pathway if there's internal fault.
"however so equipment plugged into those outlets will still not have a ground pathway if there's internal fault." OK, so what does this mean regarding safety for people and the equipment.
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,596
Location
Long Island
"however so equipment plugged into those outlets will still not have a ground pathway if there's internal fault." OK, so what does this mean regarding safety for people and the equipment.
Absolutely nothing. You're 100% safer with a GFCI protected ungrounded appliance than a grounded appliance without GFCI protection.
 

cgrutt

Well-known member
Joined
Mar 4, 2016
Messages
8,243
"however so equipment plugged into those outlets will still not have a ground pathway if there's internal fault." OK, so what does this mean regarding safety for people and the equipment.
People would likely be protected from severe shock. Equipment, esp sensitive electronics e.g. tvs, computers, cameras, alarms, etc may not be protected from electrical surges. Built in surge suppression etc may not work. All I was saying is installing a GFCI on ungrounded outlets doesn't provide a ground pathway.
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,596
Location
Long Island
People would likely be protected from severe shock. Equipment, esp sensitive electronics e.g. tvs, computers, cameras, alarms, etc may not be protected from electrical surges. Built in surge suppression etc may not work. All I was saying is installing a GFCI on ungrounded outlets doesn't provide a ground pathway.
Right. 2/3 of a surge protector's ability would be cut off by removing the ground path (because you lose the L-G and N-G pathways, but you do still have the L-N path). It's not remotely a life safety issue, and if you have surge protection at the panel it probably doesn't even matter, but yes, without a good ground path, a surge strip doesn't work very well.
 

cgrutt

Well-known member
Joined
Mar 4, 2016
Messages
8,243
Right. 2/3 of a surge protector's ability would be cut off by removing the ground path (because you lose the L-G and N-G pathways, but you do still have the L-N path). It's not remotely a life safety issue, and if you have surge protection at the panel it probably doesn't even matter, but yes, without a good ground path, a surge strip doesn't work very well.
I never said it was a life safety issue and stated it would provide GFCI protection to downstream outlets.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,138
Location
SE MI
It won't provide a true ground path however so equipment plugged into those outlets will still not have a ground pathway if there's internal fault.
First, the original purpose of the ground wire was so if the appliance shorted the hot to the case (think toaster) and you touched the case, YOU did not become the "path of least resistance" to ground !

Second, (at least in theory) a GFCI works by comparing the amount of CURRENT going through the "hot" lead and then returning on the neutral lead. It trips if they are different. So if a person provides a path to ground, then some current will not be on the return lead.
 

Wrench97

Well-known member
Joined
Jun 23, 2018
Messages
12,085
Location
Southeastern Pa
If the device is not 3 prong don't worry about the ground it doesn't need or use one.
If you are using it for A/C window units or grounded computer equipment I would run a new wire with a ground or install a new outlet as older homes never have enough outlets per room normally.
 
To avoid these ads, REGISTER NOW!
OP
F

FMC1959

Well-known member
Joined
Feb 9, 2014
Messages
2,317
Location
Montreal, Canada / Upstate NY
If the device is not 3 prong don't worry about the ground it doesn't need or use one.
If you are using it for A/C window units or grounded computer equipment I would run a new wire with a ground or install a new outlet as older homes never have enough outlets per room normally.
My walls are sometimes sheetrock, otherwise plaster, on lathe and a sub panel of 1" think wood. Many walls have shredded newspaper for insulation. Like I stated at the outset, I would add a wire if it was not very complicated.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,002
Location
Modesto, CA
Absolutely nothing. You're 100% safer with a GFCI protected ungrounded appliance than a grounded appliance without GFCI protection.

Not always true. equipment that needs a ground wire to function properly such as a surge arrestor, UPS etc, will not work properly or be 100% safer with a GFCI vs a properly grounded receptacle.
 

walta

Well-known member
Joined
Jan 13, 2017
Messages
2,311
Location
Dutzow Missouri
I would add a wire if it was not very complicated.
I am not the code expert but from what I understand, adding a single grounding conductor wire and still using the existing wires for hot and neutral is technically possible in a code compliant way it is almost impossible to actually make it happen.

I think the rules require the new wire to follow the same path as the original within a few inches. Finding single conductor wire that is rated for use outside of conduit seems unlikely. Maybe one of the expert will tell us more.

If I misunderstood and your plan is to abandon /replace the old cable and bring that circuit up to the current code that is a much better plan.

Walta
 
OP
F

FMC1959

Well-known member
Joined
Feb 9, 2014
Messages
2,317
Location
Montreal, Canada / Upstate NY
Not always true. equipment that needs a ground wire to function properly such as a surge arrestor, UPS etc, will not work properly or be 100% safer with a GFCI vs a properly grounded receptacle.
Surge arrestor. I have an APC, 10 foot cord and decent features, I would say medium duty. Plugged into a GFCI outlet that does not have a ground. It will work as a power bar, but the surge arrestor protection is lost, is that what you are saying?
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,901
Location
NJ
Surge arrestor. I have an APC, 10 foot cord and decent features, I would say medium duty. Plugged into a GFCI outlet that does not have a ground. It will work as a power bar, but the surge arrestor protection is lost, is that what you are saying?
There would only be protection between hot and neutral.

Nothing between hot - grd or neutral to grd.
 
OP
F

FMC1959

Well-known member
Joined
Feb 9, 2014
Messages
2,317
Location
Montreal, Canada / Upstate NY
What does this mean in layman terms?
To me a surge suppressor is supposed to save delicate equipment from electrical spikes or surges when there are power failures, or when the power flickers. So how does this translate to "There would only be protection between hot and neutral. Nothing between hot - grd or neutral to grd." I understand the very basic concept of a surge when power comes back on, what you say hot & neutral & grd ,I do not understand. The equipment is protected or it is not protected?
 

cgrutt

Well-known member
Joined
Mar 4, 2016
Messages
8,243
To me a surge suppressor is supposed to save delicate equipment from electrical spikes or surges when there are power failures, or when the power flickers. So how does this translate to "There would only be protection between hot and neutral. Nothing between hot - grd or neutral to grd." I understand the very basic concept of a surge when power comes back on, what you say hot & neutral & grd ,I do not understand. The equipment is protected or it is not protected?
Sorry but it depends. Generally, surge protectors work by diverting voltage spikes (from lightening, etc) to ground, so with no ground your sensitive electronics may not be protected. Believe specialized surge protectors are available that divert surges through neutral wire but not sure how effective these are. UPS systems may absorb small surges but generally believe these often require equipment ground as well.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,002
Location
Modesto, CA
Surge arrestor. I have an APC, 10 foot cord and decent features, I would say medium duty. Plugged into a GFCI outlet that does not have a ground. It will work as a power bar, but the surge arrestor protection is lost, is that what you are saying?
If there is a surge, it wont be able to shunt it to grnd.

This is why surge arrestors, UPSs etc typically have a building wiring fault indicator on them to alert you to an issue with the grnd connection on the receptacle.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,002
Location
Modesto, CA
To me a surge suppressor is supposed to save delicate equipment from electrical spikes or surges when there are power failures, or when the power flickers. So how does this translate to "There would only be protection between hot and neutral. Nothing between hot - grd or neutral to grd." I understand the very basic concept of a surge when power comes back on, what you say hot & neutral & grd ,I do not understand. The equipment is protected or it is not protected?
Theres several protections in a UPS and surge arrestor. Thats why he stated that
 
OP
F

FMC1959

Well-known member
Joined
Feb 9, 2014
Messages
2,317
Location
Montreal, Canada / Upstate NY
OK, all good to know information. Anything sensitive that really needs a surge protector, I will make sure it is on a properly grounded outlet. Anything ungrounded, I will install GFCI's and only plug in stuff that is either not sensitive or not expensive if it gets blown., like fans, lights, radios, ...etc.
 