Outlet protection...?

Tim Fitzgerald

Well-known member
Joined
Dec 1, 2013
Messages
60
Location
Anacoco, La
building a 30x14 room inside my shop. interior wall back side faces open part of my shop.., problem is I have to put outlets on both sides of wall. Does the NEC say anything about this type scenario. I understand the whole issue of putting metal protection plates where wiring runs through studs, but got to thinking from the back side of wall (facing shop) it would be possible for someone to drive a long screw through a wire because the back of the outlet and wiring buts against the sheetrock...? I suppose it couldnt be pierced by a drywall screw but then again I dont want an inspector to snag me for it....
 
To avoid these ads, REGISTER NOW!
To avoid these ads, REGISTER NOW!

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Your holes, not wires, must be an 1 1/4" or more from the face of the studs. If less than that, you must use nail plates.

So if you use a 1" bit you have to be centered exactly in the middle. Most guys use a 7/8" bit to have a little fudge factor. Still, plan on using nail plates, it's very hard to get EVERY hole perfectly in the middle.

I usually overdo it on the nailplates but they're cheap and I've never had to fix a wire hit by a drywaller yet. Knock on wood.
 