600SL
Well-known member
I would like to run two duplex outlet circuits with an outlet every 5 feet and each circuit powering every other outlet. It would save a lot of trouble if I could pass the EMT conduit right through the box to avoid bending around the boxes. I cannot find anything in the code that says you cannot do this but I never seen it done. I have attached a picture to show how the conduit would either pass through or terminate within the boxes.
The only thing I can think of is that I would have to subtract the volume of the EMT from the box volume. This should still leave plenty of volume because I will be using 3.5" deep boxes. The code states that conductors that pass through the box don't count but it doesn't say anything about conduit passing through the box.
Your thoughts?
John
The only thing I can think of is that I would have to subtract the volume of the EMT from the box volume. This should still leave plenty of volume because I will be using 3.5" deep boxes. The code states that conductors that pass through the box don't count but it doesn't say anything about conduit passing through the box.
Your thoughts?
John