Had a good discussion with my electrical consultant (Brother in-law electrician ). My sub-panel is going to be maybe thirty feet from my main 200amp service.
I have a deck off the side of the house which is about 8' from the garage.
My original plan was to bury, in 2" conduit, 2-2-2-4 MHF, after coming in from the back of the panel, and under the house. My panel is on the outside, but all wiring is routed behind the panel and into the crawl space. I would then trench under the front entrance and parallel the deck and to the building. About 30-40' of trenching. 90amp double pole in the main service.
He looked for awhile, walked around a lot and said "Yep, that would work ... but, why don't you do this?".
New plan is to drop down from the bottom of the service box, into 1 1/2" conduit and hang from deck joist with hangers. At the end of the deck, about two feet from the end, there would be a j-box(?). This would drop down into a trench with 24" sweep, six feet of conduit and sweep back up, inside the building and through the concrete pad, and finish at the bottom of the sub-panel.
Wire would be three #1 and a #4 ground ... all aluminum. There would be a 100 amp double pole breaker on both panel and sub-panel.
This cuts the trenching down to a fifth of the original, cheaper and less wire ... and so much easier. He also mentioned using a Cutler-Hammer sub-panel. I'm going to assume they are good
Edit: Cutler-Hammer are EXPENSIVE!!
I have a deck off the side of the house which is about 8' from the garage.
My original plan was to bury, in 2" conduit, 2-2-2-4 MHF, after coming in from the back of the panel, and under the house. My panel is on the outside, but all wiring is routed behind the panel and into the crawl space. I would then trench under the front entrance and parallel the deck and to the building. About 30-40' of trenching. 90amp double pole in the main service.
He looked for awhile, walked around a lot and said "Yep, that would work ... but, why don't you do this?".
New plan is to drop down from the bottom of the service box, into 1 1/2" conduit and hang from deck joist with hangers. At the end of the deck, about two feet from the end, there would be a j-box(?). This would drop down into a trench with 24" sweep, six feet of conduit and sweep back up, inside the building and through the concrete pad, and finish at the bottom of the sub-panel.
Wire would be three #1 and a #4 ground ... all aluminum. There would be a 100 amp double pole breaker on both panel and sub-panel.
This cuts the trenching down to a fifth of the original, cheaper and less wire ... and so much easier. He also mentioned using a Cutler-Hammer sub-panel. I'm going to assume they are good
Edit: Cutler-Hammer are EXPENSIVE!!