Well-known member
Is there a permitted ground size reduction for an EGC (Equipment Grounding Conductor). I am installing a 2000A 480V Equipment subfeed not a service. So I must size off a EGC not a GEC (grounding electrode conductor). Due to the size of the feed I must parallel the runs and in this case 8 times with 350Kcmil AL. According to the code I am not allowed to parallel the EGC down sizes as the ungrounded conductor. So according to the Table 250.122 I must pull a 400Kcmil Al. Is there any permitted reductions like in GEC 22-1/2 or 12-1/2% rule which ever one it is? The installation is all in EMT but I would like to pull a ground also. Any Help on this issue would be great. I am a little rusty on grounding in the code book.