Permited Ground Size Reduction?

r_olson_06

Well-known member
Joined
Feb 12, 2012
Messages
4,160
Location
SD
Is there a permitted ground size reduction for an EGC (Equipment Grounding Conductor). I am installing a 2000A 480V Equipment subfeed not a service. So I must size off a EGC not a GEC (grounding electrode conductor). Due to the size of the feed I must parallel the runs and in this case 8 times with 350Kcmil AL. According to the code I am not allowed to parallel the EGC down sizes as the ungrounded conductor. So according to the Table 250.122 I must pull a 400Kcmil Al. Is there any permitted reductions like in GEC 22-1/2 or 12-1/2% rule which ever one it is? The installation is all in EMT but I would like to pull a ground also. Any Help on this issue would be great. I am a little rusty on grounding in the code book.
 
To avoid these ads, REGISTER NOW!

sparky36000

Well-known member
Joined
Dec 25, 2012
Messages
116
Location
North Dakota
Ace is right, but why are you going with so many parallels with that load? If you went with something like 600MCM XHHW aluminum you could do it with 6 runs of 3" and save 2 400MCM EGC's, not to mention the extra pipe, racks, and labor to install it. How long is your run?
 
To avoid these ads, REGISTER NOW!

ddawg16

Well-known member
Joined
Jul 11, 2008
Messages
21,005
Location
S. California
Ace is right, but why are you going with so many parallels with that load? If you went with something like 600MCM XHHW aluminum you could do it with 6 runs of 3" and save 2 400MCM EGC's, not to mention the extra pipe, racks, and labor to install it. How long is your run?

Some good points......unless there are a lot of elbows along the way.....600 is not the funnest thing to pull.....I just sit back and watch....and it still hurts.....
 

sparky36000

Well-known member
Joined
Dec 25, 2012
Messages
116
Location
North Dakota
Some good points......unless there are a lot of elbows along the way.....600 is not the funnest thing to pull.....I just sit back and watch....and it still hurts.....

If the conduit is run to code, the pull is rigged right and you have a couple apprentices with strong backs and weak minds, it's a piece of cake :D
 
OP
R

r_olson_06

Well-known member
Joined
Feb 12, 2012
Messages
4,160
Location
SD
The run isn't too far about 200' but it still makes fun for bonding all them grounds since most ground lugs are not even remotely close to that size. Thanks for the input.
 