Plastic Elec conduit question

Motown 454

Well-known member
Joined
Sep 25, 2008
Messages
1,359
Hi guy's can plastic electrical conduit go in a wall behind Sheetrock? Thinking for a compressor 32 amp run load. Do I still need 6 ga. or can it be 8 in the thhn wire?

Thanks
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I assume you'll be doing 2 #8 and 1 #10 for ground. You can get by with 1/2". If you add a third #8 for a neutral (Don't need it) you'll need to jump up to 3/4".
 
To avoid these ads, REGISTER NOW!
OP
M

Motown 454

Well-known member
Joined
Sep 25, 2008
Messages
1,359
I already have the wire from A job I was on , its all #8 so I'll use the 3/4".
Thanks for your help.
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Don't use 1/2". That stuff is worthless regardless of what the NEC fill charts tell you. There is a reason our shop doesn't use 1/2" pvc and rigid. Use 3/4, you'll be glad you did.
 