So I'm to the point of planning electric in my 40x48 pole barn.

I'm planning on 2 outlets at every post, each on a different circuit, Lights, and a few outside lights and outlets. The panel is on the back wall in the corner.

I have 3 main questions.

#1
For the 2 outlets at each post, can I use 12-2-2 and run only one wire, but still be able to have 2 different circuits?

#2
For the front wall outlets, the run will be 48 feet up the Side wall, then have outlets start and run for 40' across the front wall. Is 12-2 gonna be sufficient for this as well?

#3
For the cieling lights, everything is open now, but I do plan on insulation, vapor barrier, and white metal. For you that have been there, what's the easiest way to go about wiring the lights? Put boxes and outlets or just leave the wire hang out of the cieling? I think I'm set on t5 Ho's, but haven't come up with a lay out, done any of that math (that'll be a whole other thread). I do want 3 switches so I can control either side and the middle.
 
To avoid these ads, REGISTER NOW!

rburke65

Well-known member
Joined
Nov 10, 2007
Messages
12,349
Location
Canfield, Ohio
The 12-2-2 is a little expensive I hear but labor saving. You can use it and run 2 circuits with the seperate neutrals. And I think you will be ok on you question #2 and #3 as well. Did I say "I think"?....,
 

racintj

Well-known member
Joined
Mar 16, 2015
Messages
127
I did near the same as you on a 33x60 shop. Ran quads at each post, with left outlet on separate circuit as the right. You can share the neutral, but they have to be on the correct breakers in the panel. I'm not an electrician so I can't think of the right terminology at this moment.

12 ga wire will be fine. I pulled 12 ga through conduit. Shared neutral for each quad, and ran one shared ground that grounded to each box and outlet. Ran #6 copper wire from box to 2 x 5/8" x 8' copper rods driven in the ground more than 6' apart.

I used stranded wire.
 
Last edited:

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,185
Location
SE MI
I am planning on 2 outlets at every post, each on a different circuit, Lights, and a few outside lights and outlets. The panel is on the back wall in the corner.

I have 3 main questions.

#1
For the 2 outlets at each post, can I use 12-2-2 and run only one wire, but still be able to have 2 different circuits?
That is a "multi-wire branch circuit". Use 12/3. Black to one outlet, red to the other. They share a neutral and the breakers need to be of opposite "poles'.
 

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,728
Location
SE Michigan
1) I feel like this isn't a good idea as it sets up a troubleshooting conundrum for you or someone else down the road. Better to keep it simple and reliable and put more wire under the staples. Copper is currently a good value. The other reason I don't like it, I have seen and troubleshot a shared neutral situation with 7 conductors in a tray cable, where it induced a 48vac voltage in a circuit which was powered off. That's an oddity to stay away from.

2) if you are using a GFI breaker for inspected work, I believe you will be limited to 10 outlets per GFI and thus per circuit.

3) Personally I like the largest round box in the ceiling, it can be anything from a duplex outlet to a direct wire thru a coverplate, to an inverted Edison-base fixture. If you want to upgrade a specific location to a 4-bulb T5HO for critical work, its right there without need to undo hard-wiring. However, for inspected work, I believe you will be required to have a GFI outlet controlling other outlets.
 
OP
H

HunterDan

Well-known member
Joined
Apr 21, 2011
Messages
185
Location
Maryland
The old wizard, when you say "opposite poles", do you mean opposite hot legs in the panel?

I am not required to have any inspections (although o do want to keep things code compliant), except for having a gfci on my door opener outlets. But yes, outlet runs will start with. Gfi.

So for boxes, am I good to go with all plastic new work boxes?
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,185
Location
SE MI
The old wizard, when you say "opposite poles", do you mean opposite hot legs in the panel?
Yes. Typically they are mounted next to each other, but that is not a requirement. You do NOT want the handles of the breakers linked together.

12/3 is black, white and red so the hots are easy to see.
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,758
Yes. Typically they are mounted next to each other, but that is not a requirement. You do NOT want the handles of the breakers linked together.

12/3 is black, white and red so the hots are easy to see.

Depending on the code edition, it's required to use handle ties for multi-wire circuits and on opposite legs as having them on the same leg opens up the possibility of burning up the neutral.

See 210.4(B), handle tie required in the 2008, 2011, 2014 NEC editions.
 
OP
H

HunterDan

Well-known member
Joined
Apr 21, 2011
Messages
185
Location
Maryland
So in my panel, I would have the 12-3, 20 amp single breaker/red wire to one hot leg, black wire/single 20 amp breaker to the other hot leg, correct?
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,185
Location
SE MI
Depending on the code edition, it's required to use handle ties for multi-wire circuits and on opposite legs as having them on the same leg opens up the possibility of burning up the neutral.

See 210.4(B), handle tie required in the 2008, 2011, 2014 NEC editions.

IANALE. Learn something new every day !
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,185
Location
SE MI
So in my panel, I would have the 12-3, 20 amp single breaker/red wire to one hot leg, black wire/single 20 amp breaker to the other hot leg, correct?

Based on what Norcal just posted, get a 240V 20A breaker. Wire the black to one screw and the red to the other. That's it !
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
On a MWBC the difference of using two single pole breakers with handle ties over a common trip double pole is if one circuit trips due to a fault you won't lose power on the other circuit. Using a double pole common trip will take out both circuits if there is a fault on either one. If the MWBC is powering a line-to-line load then DP common trip breaker must be used.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,758
On a MWBC the difference of using two single pole breakers with handle ties over a common trip double pole is if one circuit trips due to a fault you won't lose power on the other circuit. Using a double pole common trip will take out both circuits if there is a fault on either one. If the MWBC is powering a line-to-line load then DP common trip breaker must be used.


If the load is line to line then it must comply w/ 210.4(C), there are a couple of exceptions to that requirement. 210.4(D) also has conductor grouping requirements for multiwire circuits in a panelboard.
 
Last edited:

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
If the load is line to line then it must comply w/ 410.4(C), there are a couple of exceptions to that requirement. 410.4(D) also has conductor grouping requirements for multiwire circuits in a panelboard.

I believe you meant 210.4
 