First off thank you for this forum. I stumbled across it while I was researching subpanel installs. I apologize if this question has already been covered.
Were getting a new inground pool installed in a couple months. Before that happens my plan is to have the subpanel already installed and ready for the equipment. The equipment is going to be...
140k btu heatpump 36 amps
VS pool pump. 10.5 amps
Salt Water Gen. ? They only told me it's 110 or 220 and needs 20a circuit
Pool light. 4 led not sure on amps
10x20 Pool building with fridge and random lights etc.
Subpanel is going to be around 185' from the meter socket. (I have 2 open breaker sockets there)
My plan was to pull 2-2-2-4 to the 100amp panel. In the panel I was going to make sure the Neutral was not connected to the ground bar in any way. I was also going to install 2 grounding rods
So I work at a Power Plant. During lunch break I went to the electric shop and had a set down with the guys. They seemed to think what I'm doing is over kill. They told me a 60amp panel would be fine and that I would only need to pull 3 wires and just hook up the ground to the grounding rods.
Since then I have read so many articles and watched so many youtube videos my head is spinning. So what is your guys thought?
Were getting a new inground pool installed in a couple months. Before that happens my plan is to have the subpanel already installed and ready for the equipment. The equipment is going to be...
140k btu heatpump 36 amps
VS pool pump. 10.5 amps
Salt Water Gen. ? They only told me it's 110 or 220 and needs 20a circuit
Pool light. 4 led not sure on amps
10x20 Pool building with fridge and random lights etc.
Subpanel is going to be around 185' from the meter socket. (I have 2 open breaker sockets there)
My plan was to pull 2-2-2-4 to the 100amp panel. In the panel I was going to make sure the Neutral was not connected to the ground bar in any way. I was also going to install 2 grounding rods
So I work at a Power Plant. During lunch break I went to the electric shop and had a set down with the guys. They seemed to think what I'm doing is over kill. They told me a 60amp panel would be fine and that I would only need to pull 3 wires and just hook up the ground to the grounding rods.
Since then I have read so many articles and watched so many youtube videos my head is spinning. So what is your guys thought?