Pool & Spa Electrical

BB Sig

Well-known member
Joined
May 16, 2018
Messages
139
Location
Florida
I'm currently building a slab to place a spa/hot tub on and we will be getting an above ground pool within 20 feet of the spa. Because of the slopped ground, one side is ~ 2' higher than the other side. There will be a deck ~ 4' off the ground so the spa is 1' above the deck.

Can I run a sub panel (outdoor rated) out there and place it a foot under the deck for a little protection from the rain? The panel would be under a piece of tin ~ 6' from the spa.

Current spa is 110 but I figure I should run 220 in case we end up going bigger in the future. Not sure what the pool motor will need yet so I was going to run 60 amps to take care of the spa, pool and lights.

80' run from panel to where I want to place the panel so I am going to use 4 AWG copper in a 1.5" conduit. I am going to run water to fill said pool and spa and a spare 1" conduit in case I ever decided to run a internet and or cable out there.

Am I missing anything? :dunno:

Barry
North Florida
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
Dont put the subpanel under the deck. it needs to be accessible.

also, the hot tub will need to be GFCI protected with a disconnect nearby.
 
To avoid these ads, REGISTER NOW!

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
Spa disconnect cannot be closer than 6 ft from the wall of the spa, but must be within sight.

60 amps might be cutting it close for all of that depending on the size of the spa, they usually require a 50 or 60 amp circuit. You may want to go a little larger on the feeders to the panel.
 
OP
B

BB Sig

Well-known member
Joined
May 16, 2018
Messages
139
Location
Florida
Spa disconnect cannot be closer than 6 ft from the wall of the spa, but must be within sight.

60 amps might be cutting it close for all of that depending on the size of the spa, they usually require a 50 or 60 amp circuit. You may want to go a little larger on the feeders to the panel.
I'll keep that distance in mind! The spa is currently a 6x6 on a 120V 20amp circuit. The pad I am building is 8x8 in case we want a bigger one later. Up sizing the feeders might be a good idea.

Would 80 amps cut it?

Barry
North Florida
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
I'll keep that distance in mind! The spa is currently a 6x6 on a 120V 20amp circuit. The pad I am building is 8x8 in case we want a bigger one later. Up sizing the feeders might be a good idea.

Would 80 amps cut it?

Barry
North Florida
80 would probably be good. Or you can just run #2 aluminum feeders and put it on a 90 amp breaker and have a little extra if ever needed. There isn't a big cost difference .

Sent from my SM-G960U using The Garage Journal mobile app
 