I'm in the process of planning for a 12'x14' shed.

It will need one 15A circuit to supply overhead lighting and an outdoor light.

There is a detached garage about 30' away from the planned shed site with a subpanel from the house which is about 30' from both. (triangle of buildings)

The question is.... can I get away with running one circuit from the detached garage to the shed? Or will a subpanel in the shed from the house be required? Or maybe something else? what's normal?

I'm in High Point NC, and I know everywhere is different; just looking for the rule-of-thumb.

Thanks,
 
To avoid these ads, REGISTER NOW!

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
you can run one circuit to the shed. more than that and you would need a subpanel in the shed.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
mrb is correct, you are allowed to run one circuit to another structure (otherwise unpowered), any more and you have to run a sub feed and panel, etc.

The single circuit is allowed to be a multi-wire, ie. one neutral, and two opposing phase hots on a common trip double pole breaker (ie, a 240v breaker).

Charles
 

Gary S

Well-known member
Joined
Dec 27, 2008
Messages
2,972
Location
Bismarck, ND
If you are running a wire, make it #12 and use a 20 amp breaker instead of a 15 amp. The first time you plug in a big power tool out there, you will thank yourself.
Do it the easy way. Dig the trench and put in conduit. Then fill back in the dirt and pull your wire through it later when you have the building finished and ready for power. This way, if something ever goes wrong with the wire, you pull it out and pull in a new wire and never have to dig the trench again.
 
To avoid these ads, REGISTER NOW!

Motofixxer

Well-known member
Joined
Oct 10, 2009
Messages
681
Yep and oversize the conduit maybe even add a second small conduit for some low voltage. Maybe not for a small shed but at least upsize the conduit so if you wanna add a second floor for a MIL suite you will be ready. :)
 

WVBrady

Well-known member
Joined
May 5, 2005
Messages
1,679
Location
WV
If you are running a wire, make it #12 and use a 20 amp breaker instead of a 15 amp. The first time you plug in a big power tool out there, you will thank yourself.
Do it the easy way. Dig the trench and put in conduit. Then fill back in the dirt and pull your wire through it later when you have the building finished and ready for power. This way, if something ever goes wrong with the wire, you pull it out and pull in a new wire and never have to dig the trench again.

If you don't put the conductor in when you put in the conduit, I would be sure and put in a heavy cord so that you can pull the conductor later.
 

Random Guy

Well-known member
Joined
Jun 16, 2009
Messages
155
If you are running a wire, make it #12 and use a 20 amp breaker instead of a 15 amp. The first time you plug in a big power tool out there, you will thank yourself.
Do it the easy way. Dig the trench and put in conduit. Then fill back in the dirt and pull your wire through it later when you have the building finished and ready for power. This way, if something ever goes wrong with the wire, you pull it out and pull in a new wire and never have to dig the trench again.

I would also use conduit big enough so that if you ever decided to pull a bigger service to a subpanel (i.e. you decide to put some power tools in the shop and want to put a 60 amp subpanel in there) all you would have to do is pull the new feeder through the pipe. You might could also use the wire you would be taking out of the conduit to pull the new conductors!
 

Gary S

Well-known member
Joined
Dec 27, 2008
Messages
2,972
Location
Bismarck, ND
OP
B

ben1000

Active member
Joined
Dec 3, 2009
Messages
25
Excellent,

The subpanel in the garage is on the opposite side from where the shed will be. I should be able to run romex from the subpanel along the rafters in the garage then down the wall and out into conduit. Then, at the shed, from the conduit to the rest of the circuit as 'normal'*.

*Normal is a relative term, I've done a fair bit of interior wiring but have never really dealt with underground or the transition from inside to outside. The way the planning department works here I only get 2 questions/strikes as a 'homeowner without contractor' before they require a contractor to finish the project or it be torn down; so I don't want to waste those on anything simple.
 