Proven epoxy anchor system that’s works

James168

Member
Joined
Jan 8, 2019
Messages
13
Location
Garage
I have a 9k 2 post lift. I have a few wedge anchors that are pulling
Out I try hammering them In and retorquing which work for a while but they are starting to pullout again. Concrete is 3500.
I would like to hammer them through and install a threaded rod with epoxy. Which product have you guys used that has been proven to work. Which size rod and whole size

Thank you
 
To avoid these ads, REGISTER NOW!

nitroracer20

Well-known member
Joined
Feb 25, 2018
Messages
238
Location
NY
Hilti RE500 is what we use for structural anchoring threaded rod/wedge anchors etc. great stuff.

Where are you located?
 

NUTTSGT

Super Moderator
Staff member
Joined
Sep 14, 2009
Messages
50,960
Location
Northern Central Ohio
Im in Connecticut.

Thanks for the help everyone

This is why adding a general location helps your fellow members rather than putting faux location like garage, attached or detached.




If the anchors keep pulling out, I'd assume they were either drilled oversize or are now oversize if they keep pulling out.
 

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,728
Location
SE Michigan
I used Sika AnchorFix2 to set anchors for columns. Cannot tell of any issues 4 yrs into it.

I placed in colder weather, I built a cardboard enclosure around the section of wall and had a 1500W space heater running inside of it for half a day prior and the rest of the day after.

Very very important is to get a thin piece of tube (ideally metal) that will reach to the very bottom of the hole and blow, blow, blow, with compressed air until no more dust is coming out. Raise and lower the tube many times and special "bottle brushes" are sold for the same thing. The dust must be fully removed otherwise the epoxy will just bond to the dust which creates a zero-strength connection.

Let the epoxy cure 24 hrs before final torque.
 
Last edited:
OP
J

James168

Member
Joined
Jan 8, 2019
Messages
13
Location
Garage
This is why adding a general location helps your fellow members rather than putting faux location like garage, attached or detached.




If the anchors keep pulling out, I'd assume they were either drilled oversize or are now oversize if they keep pulling out.


I used the appropriate size bit for the anchors I had. 3/4”. Cleaned the hole before inserting anchor. There are drill bits that are 3/4” at the tip only and the shaft is smaller. The bit I had was 3/4 even at the shaft so I think that if you let the drill wonder or tilt slightly it can make the hole bigger. I think that’s what might have happened.
 

LX-Markham

Well-known member
Joined
Apr 27, 2013
Messages
2,929
Location
Markham, Ont.
Surprised to see all the Hilti RE500 responses. We've switched almost exclusively to the HIT-HY 200 adhesive. Not as susceptible to not cleaning the hole out properly.

Hilti also makes a capsule that doesn't require a mixing gun. Just insert the capsule, it mixes in the hole when you insert the anchor.

Best bet: contact Hilti. They are very helpful in specifying the right product.
 
OP
J

James168

Member
Joined
Jan 8, 2019
Messages
13
Location
Garage
I used Sika AnchorFix2 to set anchors for columns. Cannot tell of any issues 4 yrs into it.

I placed in colder weather, I built a cardboard enclosure around the section of wall and had a 1500W space heater running inside of it for half a day prior and the rest of the day after.

Very very important is to get a thin piece of tube (ideally metal) that will reach to the very bottom of the hole and blow, blow, blow, with compressed air until no more dust is coming out. Raise and lower the tube many times and special "bottle brushes" are sold for the same thing. The dust must be fully removed otherwise the epoxy will just bond to the dust which creates a zero-strength connection.

Let the epoxy cure 24 hrs before final torque.

Thank you. I know a guy that used a sika product for his lift he said it’s been ok.
Im just trying to find out reviews from several people because due to my lack of space I want to use the best product so I don’t have to re do concrete.
 

GMCGarage

Well-known member
Joined
Jan 31, 2017
Messages
1,264
I have a 9k 2 post lift. I have a few wedge anchors that are pulling
Out I try hammering them In and retorquing which work for a while but they are starting to pullout again. Concrete is 3500.
I would like to hammer them through and install a threaded rod with epoxy. Which product have you guys used that has been proven to work. Which size rod and whole size

Thank you

Hilti HIT HY 200

Problem is hammering through might damage the underside of the slab, blowout, etc that you are now putting a anchor in a damaged hole.

How thick is your slab at the lift?

Might be a good idea to have a new base plate made that is epoxied down, and then the lift bolted to studs welded onto that. Get those anchors in some clean holes
 
OP
J

James168

Member
Joined
Jan 8, 2019
Messages
13
Location
Garage
The slab is 6” with rebar. and drilled through it when I put the anchors so I should be able to hammer it through. If not I’m screwed. He holes are 3/4”. So I would have to drill the hole to 7/8? And use a 3/4 rod? How much of the rod need to be embedded
What do you about the epoxy not leaking down once you try to advance the rod in the hole?
 
To avoid these ads, REGISTER NOW!

NUTTSGT

Super Moderator
Staff member
Joined
Sep 14, 2009
Messages
50,960
Location
Northern Central Ohio
I used the appropriate size bit for the anchors I had. 3/4”. Cleaned the hole before inserting anchor. There are drill bits that are 3/4” at the tip only and the shaft is smaller. The bit I had was 3/4 even at the shaft so I think that if you let the drill wonder or tilt slightly it can make the hole bigger. I think that’s what might have happened.


That's very possible as to what is causing your issue.

Hilti HIT HY 200

Problem is hammering through might damage the underside of the slab, blowout, etc that you are now putting a anchor in a damaged hole.

How thick is your slab at the lift?


Very good point, what is the depth of the concrete and are you "sure" it's the correct depth ?
 
OP
J

James168

Member
Joined
Jan 8, 2019
Messages
13
Location
Garage
That's very possible as to what is causing your issue.




Very good point, what is the depth of the concrete and are you "sure" it's the correct depth ?

Yes I’m sure it’s 6” i was there when they did it. I measured the cavity before they poor concrete
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,604
Location
Long Island
I used the appropriate size bit for the anchors I had. 3/4”. Cleaned the hole before inserting anchor. There are drill bits that are 3/4” at the tip only and the shaft is smaller. The bit I had was 3/4 even at the shaft so I think that if you let the drill wonder or tilt slightly it can make the hole bigger. I think that’s what might have happened.

What sort of a drill did you use? I've had better luck getting clean holes with an SDS than with a hammer drill.

Hammer drills require much more spinning time to get to depth, which means you'll get a more oversized hole, that makes for a poor fit with a wedge anchor that requires close tolerances. An SDS has much more impact power, which makes for a tighter fitting hole as it sinks the bit much faster, however, with larger SDS capacity drills, you'll get more blowout on the back side. The only good answer I have to this is to ease off before your bit exits.
 
OP
J

James168

Member
Joined
Jan 8, 2019
Messages
13
Location
Garage
What sort of a drill did you use? I've had better luck getting clean holes with an SDS than with a hammer drill.

Hammer drills require much more spinning time to get to depth, which means you'll get a more oversized hole, that makes for a poor fit with a wedge anchor that requires close tolerances. An SDS has much more impact power, which makes for a tighter fitting hole as it sinks the bit much faster, however, with larger SDS capacity drills, you'll get more blowout on the back side. The only good answer I have to this is to ease off before your bit exits.

Hammer drill. Sure I’ll keep that in mind if I have to redo concrete hopefully epoxy saves me. The wedge anchors didn’t fail instantly. Been using the lift since summer but every time I go retorque I see a few that are popping out slightly. As per manual if more that 2 1/4” above grade then There is not enough embedment and I think I will be there by mid year, I’m just planning ahead for what’s coming
 
Last edited:

Flail

Well-known member
Joined
Aug 5, 2016
Messages
412
Location
Kin folk said, “Californias the place you wanna be
The slab is 6” with rebar. and drilled through it when I put the anchors so I should be able to hammer it through. If not I’m screwed. He holes are 3/4”. So I would have to drill the hole to 7/8? And use a 3/4 rod? How much of the rod need to be embedded
What do you about the epoxy not leaking down once you try to advance the rod in the hole?

Pack sand down in base of hole. Check that it’s packed down to very bottom of slab. Pack it hard. Drizzle in a few ml of epoxy and let it set. This will plug the bottom of the hole so the new epoxy doesn’t run out when you put in the new stud.
 
OP
J

James168

Member
Joined
Jan 8, 2019
Messages
13
Location
Garage
Pack sand down in base of hole. Check that it’s packed down to very bottom of slab. Pack it hard. Drizzle in a few ml of epoxy and let it set. This will plug the bottom of the hole so the new epoxy doesn’t run out when you put in the new stud.

Cool thank you!!
 
OP
J

James168

Member
Joined
Jan 8, 2019
Messages
13
Location
Garage
Update apple to hilti rep- they recommended the hy 200. Of the rod is 3/4. Then to drill 7/8 hole. I forgot to ask about the rods they sell.

Has anyone used their rods? Or which rod do you recomend. I saw hilti has regular threaded rods and some that have a cones and groves on the part of the rod that gets embedded

Also ask my lift manufactured they said epoxy was ok they said to buy it at homedepot :0
 

LX-Markham

Well-known member
Joined
Apr 27, 2013
Messages
2,929
Location
Markham, Ont.
Has anyone used their rods? Or which rod do you recomend. I saw hilti has regular threaded rods and some that have a cones and groves on the part of the rod that gets embedded
Depending on installation conditions and procedures they will recommend either the HIT-Z or the HAS rod. You are likely okay with the HAS (regular) threaded rod. Ask the HILTI rep.
 
OP
J

James168

Member
Joined
Jan 8, 2019
Messages
13
Location
Garage
Thanks all I think I’m leaning toward the hit-z. They say provides the best anchoring also no need to clean holes, not that I won’t clean them but I guess it’s more forgiving

So how have you guys prevent the epoxy from leaking out the bottom. The hilti rep did not know- just said you are not supposed to drill through the concrete lol.
 

Nuccio

Well-known member
Joined
Sep 12, 2010
Messages
64
Location
Northern NJ
Thanks all I think I’m leaning toward the hit-z. They say provides the best anchoring also no need to clean holes, not that I won’t clean them but I guess it’s more forgiving

So how have you guys prevent the epoxy from leaking out the bottom. The hilti rep did not know- just said you are not supposed to drill through the concrete lol.
If you use the Hilti 200 epoxy and there is no void in the bottom I it should not leak out it is more of a thick paste not a liquid. I have used cases of it to set rebar and anchors.

Sent from my SM-T817V using Tapatalk
 

lukedwag

Well-known member
Joined
Aug 5, 2007
Messages
202
It has limited places to go. Just buy enough so you can pump the holes full and drop the rod in. HY200 is a great product
 