I am about to pull 3 strands of #2AWG Southwire stranded AL SIMpull THHN thru 1-1/2" conduit. I have about 90' of straight conduit with a 90deg bend at each end. I have read that one should NOT use wire lube with this cable and I have read it will make my life easier if I use the lube.
What does the collective wisdom here have to say about this? Pull lube with this wire- Yes or no?

Thank you- Jim

 
To avoid these ads, REGISTER NOW!

Firebrick43

Well-known member
Joined
May 12, 2015
Messages
14,018
Location
West central Indiana
I am about to pull 3 strands of #2AWG Southwire stranded AL SIMpull THHN thru 1-1/2" conduit. I have about 90' of straight conduit with a 90deg bend at each end. I have read that one should NOT use wire lube with this cable and I have read it will make my life easier if I use the lube.
What does the collective wisdom here have to say about this? Pull lube with this wire- Yes or no?

Thank you- Jim

It will not hurt to use lube. The people who say you can’t use lube failed to read the entire sticker on the roll.

IMG_0838.jpeg

You absolutely can use lube and it’s required if there are other wires in the raceway.
 

yatg

Well-known member
Joined
Aug 16, 2019
Messages
2,776
Location
Southern Oregon
I am about to pull 3 strands of #2AWG Southwire stranded AL SIMpull THHN thru 1-1/2" conduit. I have about 90' of straight conduit with a 90deg bend at each end. I have read that one should NOT use wire lube with this cable and I have read it will make my life easier if I use the lube.
What does the collective wisdom here have to say about this? Pull lube with this wire- Yes or no?

Thank you- Jim

How far? With 1-1/2 you shouldn't have any problem for 3 #2s unless its a really long run.

If this is for a panel in a detached building, then you need 4 wires (H-H-N-G) or a metal conduit grounded.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,716
Location
NW Iowa
I hate wire lube.

Two 90*s and less than a hundred feet of pipe. I see zero reason to use lube.

If you were maxing out with four bends then I might want to use it.
 
OP
I

ixlr8

Well-known member
Joined
Sep 15, 2009
Messages
435
Location
Mid-Coast Maine---> Eastern Shore Virginia
How far? With 1-1/2 you shouldn't have any problem for 3 #2s unless its a really long run.

If this is for a panel in a detached building, then you need 4 wires (H-H-N-G) or a metal conduit grounded.
Good call on the ground wire, I forgot about that. Yes this is a detached building, no metal conduit, conduit is PVC. In addition to the 3 #2's, I also have a 6-awg SIMpull wire to go in the conduit as well for the ground. The detached building is for boat storage, wood working shop and auto repair with a 4 post lift. Using 70 amp breaker to feed the building.
So far consensus is as long as all the wires are SIMpull, then there should not be a need for wire lube although using wire lube might make the job easier.
 

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
I am about to pull 3 strands of #2AWG Southwire stranded AL SIMpull THHN thru 1-1/2" conduit. I have about 90' of straight conduit with a 90deg bend at each end. I have read that one should NOT use wire lube with this cable and I have read it will make my life easier if I use the lube.
What does the collective wisdom here have to say about this? Pull lube with this wire- Yes or no?

Thank you- Jim


if you are within the conduit fill and not having bend degree total over 360 deg on a run (not LB but sweeps), you can easily do it without a sweat, as long as you don't twist and tangle your wires. Had a run that have 5x 90 degs and less than 50% fill.. that was fun. as weird as it is, it won't pull.

if your wires are in a spool, make sure it is on a roll and on some sort of spool contraptions that doesn't tangle your wires.. you will be fine.
I hang my spool of wires on two ladders and boom stick and some one at the other end to watch and make sure it doesn't tangle up.



 
To avoid these ads, REGISTER NOW!
OP
I

ixlr8

Well-known member
Joined
Sep 15, 2009
Messages
435
Location
Mid-Coast Maine---> Eastern Shore Virginia
if you are within the conduit fill and not having bend degree total over 360 deg on a run (not LB but sweeps), you can easily do it without a sweat, as long as you don't twist and tangle your wires. Had a run that have 5x 90 degs and less than 50% fill.. that was fun. as weird as it is, it won't pull.

if your wires are in a spool, make sure it is on a roll and on some sort of spool contraptions that doesn't tangle your wires.. you will be fine.
I hang my spool of wires on two ladders and boom stick and some one at the other end to watch and make sure it doesn't tangle up.



Thank you for the conduit fill calculator, I hadn't seen that before. Plugging in the numbers I come up with 18% fill and a 4.5% chance of a jam. Looks like this is going to work out fine.
I just have 4 loose loops of the wire, not on a spool. Still, two ladders and a pole will make feeding easier than trying to untangle each loop as I am feeding it. Thanks for that idea as well.
Now to bury the conduit and pull the wire.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,479
Location
Richmond, VA
Thank you for the conduit fill calculator, I hadn't seen that before. Plugging in the numbers I come up with 18% fill and a 4.5% chance of a jam. Looks like this is going to work out fine.
I just have 4 loose loops of the wire, not on a spool. Still, two ladders and a pole will make feeding easier than trying to untangle each loop as I am feeding it. Thanks for that idea as well.
Now to bury the conduit and pull the wire.
Make sure you keep all the conduit bells facing the same way and pull into them.

Also, get the conduit fully glued up before pulling any wire
 

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
Buy more tools. A 12v or 24v winch with poly rope… they do sell one specific for electrical work. My googlefoo sucked can’t find it now. But it does exist.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,893
Location
NJ
1729254198625.pngI'll clarify so it remains within the context of this thread.......

The question to the OP is.... Are you pulling the conductors by yourself or is there help available to feed the conductors into the conduit while someone is on the other end pulling simultaneously?
 

BreeStephany

ALLIANCE MEMBER
Joined
May 19, 2012
Messages
851
Location
Oregon
Lube never hurts, just make sure to CLEAN up after pulling. Wipe down the conductors with a rag to remove excess lube and to clean up any that may be in the enclosures you are pulling from / to.

With that said, pulling lube does somewhat solidify into a residue, so don't fill the conduit with lube when pulling.

As others have said, use a vacuum to **** in pull string, but DO NOT use the pull string to pull your conductors. Pull string will cut into the 90s and get stuck in place, as well as compromise the conduit when you put some force behind it.

Tie on a small piece corner of a grocery bag to make a balloon in the conduit and vacuum it in, then use mule tape or a similar, larger softer pull rope to pull in your conductors.

Spend a couple of extra dollars, get yourself a roll of 3M Super33+, strip out about a 1' of each of the conductors, cut off 1/2~2/3 of the conductor strands, tie a strong loop in your pull rope, loop your stripped conductors through the loop, use a pair of pump pliers to make the pulling head as small as possible and then wrap the head in Super33+. Super33+ is STRONG and really stretches, so do tight wraps. Wrap the head so that it has a smooth, gradual transition from the pull rope diameter to the diameter of your combined conductors.

3x #2's and a #6 in a 1-1/2" conduit should be a pretty easy pull at around ~20% conduit fill, especially at only 90', but still make your life easy and spend a few minutes making up the pulling head correctly.

Early on in my electrical career, I lost too many conductors midway through a pull and/or had MISERABLE pulls due to cheap tape and poorly made heads.

Just my two cents!
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,967
Location
Central Iowa
Lube never hurts, just make sure to CLEAN up after pulling. Wipe down the conductors with a rag to remove excess lube and to clean up any that may be in the enclosures you are pulling from / to.

With that said, pulling lube does somewhat solidify into a residue, so don't fill the conduit with lube when pulling.

As others have said, use a vacuum to **** in pull string, but DO NOT use the pull string to pull your conductors. Pull string will cut into the 90s and get stuck in place, as well as compromise the conduit when you put some force behind it.

Tie on a small piece corner of a grocery bag to make a balloon in the conduit and vacuum it in, then use mule tape or a similar, larger softer pull rope to pull in your conductors.

Spend a couple of extra dollars, get yourself a roll of 3M Super33+, strip out about a 1' of each of the conductors, cut off 1/2~2/3 of the conductor strands, tie a strong loop in your pull rope, loop your stripped conductors through the loop, use a pair of pump pliers to make the pulling head as small as possible and then wrap the head in Super33+. Super33+ is STRONG and really stretches, so do tight wraps. Wrap the head so that it has a smooth, gradual transition from the pull rope diameter to the diameter of your combined conductors.

3x #2's and a #6 in a 1-1/2" conduit should be a pretty easy pull at around ~20% conduit fill, especially at only 90', but still make your life easy and spend a few minutes making up the pulling head correctly.

Early on in my electrical career, I lost too many conductors midway through a pull and/or had MISERABLE pulls due to cheap tape and poorly made heads.

Just my two cents!
That's the best advice so far. Make a decent pulling head and the wire will almost pull itself in with the assistanceof two guys. Make a monstrosity of a head and it will take 12 people, five gallons of lube, three monkeys, a forklift, some dynamite, and every cuss word ever uttered.
 