Pulling MHF thru 2" PVC

Mr onetwo

Well-known member
Joined
Apr 6, 2011
Messages
2,005
Location
Coastal Maine
Good morning all, I am looking for advice for a short pull I will be attempting in a week or so.I have an existing 2" pvc conduit that goes from the 200 amp meter/disconnect on the pole over to my garage.Total run is under 20ft with 2 sweeps underground and an LB at the end.I am removing the existing 2-2-2-4 MHF 100amp feed to the garage and replacing it with 2/0-2/0-2/0-1 to feed a new 150amp panel.There will also be a longer piece of 2-2-2-4 coming back to splice into the 90amp feed over to the house.I have Polaris connectors for that. Both existing 100 amp breakers will be removed and the opening blocked off.Conduit fill calculator says this is legal and I believe I can remove both the ground and neutral conductors if it makes things easier.I will have some mule tape and a helper on hand.HI really don't want to run another conduit if possible.Has anyone pulled this much aluminum thru 2" pvc? Tips or tricks or helpful hints are appreciated.
 

Attachments

  • pole 9ww.JPG
    pole 9ww.JPG
    318.9 KB · Views: 48
  • IMG_0222.JPG
    IMG_0222.JPG
    762.5 KB · Views: 46
  • IMG_0219.JPG
    IMG_0219.JPG
    526.9 KB · Views: 52
To avoid these ads, REGISTER NOW!

briceandy4

Member
Joined
Oct 22, 2023
Messages
8
I will have to look at the code book and check wire fill. That seems like it would be a bit tight to me. One of the biggest problems will be that LB. Wire fill for condulets is actually pretty low. I would check and see if it is stamped with the volume. Other than that I would suggest using a lot of soap for the pull. Personally I would avoid yellow 77 as it can harden overtime and removing those wires in the future may be even more difficult. Something like this would work.

 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,390
Location
VT
OP
M

Mr onetwo

Well-known member
Joined
Apr 6, 2011
Messages
2,005
Location
Coastal Maine
Sorry for the confusion...both in same conduit.It has been suggested that I replace the LB with a 12x12x4 pvc junction/pull box.
 

briceandy4

Member
Joined
Oct 22, 2023
Messages
8
Sorry for the confusion...both in same conduit.It has been suggested that I replace the LB with a 12x12x4 pvc junction/pull box.
Without having my code book in front of me I can’t say for sure if it would be code compliant with the LB but I know it will be tough to work the wires in there. If you’re able to pull the LB and replace it with a larger pull box like a 12x12 it will be more than enough room and will make your life easier.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,967
Location
Central Iowa
It's going to be enough of a ***** that I wouldn't even try it. You can't remove the neutrals, but can eliminate the smaller ground, but that defeats the purpose of MHF. Get individual conductors, those are still gonna be tough to get through the LB but with enough cussing, it can happen.
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
31,920
Location
Coronado, CA
Just because you can force it through and meet the minimum requirements of the NEC dose not make it a good idea.

Lots of lubricant and bigger connection boxes will be your friends.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,411
Location
Richmond, VA
It's going to be enough of a ***** that I wouldn't even try it. You can't remove the neutrals, but can eliminate the smaller ground, but that defeats the purpose of MHF. Get individual conductors, those are still gonna be tough to get through the LB but with enough cussing, it can happen.
Swearing makes the ******** world go 'round
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,752
Swearing makes the ******** world go 'round
When using this computer there are issues with boxes popping up without me wanting them & so frequently blurt out "goddammit" and my German Shepard/Husky "cat"frequently will come over when I do blurt it out, but trying to stop because some people get offended by using the Lords name in vain, I am just a heathen but we all need to consider the feelings of others to some extent.

As to calling my dog a cat, if you are around him you would understand, he will open his eyes if you call his name and will not move otherwise, ignoring you like a cat, which I think comes with the Husky in him.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
When using this computer there are issues with boxes popping up without me wanting them & so frequently blurt out "goddammit" and my German Shepard/Husky "cat"frequently will come over when I do blurt it out, but trying to stop because some people get offended by using the Lords name in vain, I am just a heathen but we all need to consider the feelings of others to some extent.

As to calling my dog a cat, if you are around him you would understand, he will open his eyes if you call his name and will not move otherwise, ignoring you like a cat, which I think comes with the Husky in him.
My cats act like dogs. He chases balls and comes when i call his name….
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,752
My cats act like dogs. He chases balls and comes when i call his name….
Had a couple of cats that were full of personality, one was born under my bed, the other cat liked junk food. Sadly both are gone & still miss them.
 
OP
M

Mr onetwo

Well-known member
Joined
Apr 6, 2011
Messages
2,005
Location
Coastal Maine
Would an 8x8x4 box help or do I have to go up to a 12x12x4? Also what if I pull the 2/0-2/0-2/0-1 back to the pole along with 2- #2 XHHW conductors for the hots back to the house? The neutral and ground for the house is already at the pole.Just trying to use the MHF that I shouldn't have bought in the first place, but if I have to eat it then so be it.:sad:
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,390
Location
VT
Would an 8x8x4 box help or do I have to go up to a 12x12x4? Also what if I pull the 2/0-2/0-2/0-1 back to the pole along with 2- #2 XHHW conductors for the hots back to the house? The neutral and ground for the house is already at the pole.Just trying to use the MHF that I shouldn't have bought in the first place, but if I have to eat it then so be it.:sad:
I'm having a hard time visualizing the 2 runs in the same conduit. Can you do an overhead sketch showing what you're planning?

We might be able to suggest other ways that cost less/are easier.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,411
Location
Richmond, VA
Would an 8x8x4 box help or do I have to go up to a 12x12x4? Also what if I pull the 2/0-2/0-2/0-1 back to the pole along with 2- #2 XHHW conductors for the hots back to the house? The neutral and ground for the house is already at the pole.Just trying to use the MHF that I shouldn't have bought in the first place, but if I have to eat it then so be it.:sad:
Box sizing is done by conduit size and direction of the pull. If going through at 90 degrees, I believe it is 6x conduit, so you'd need 12x12.

Eithet way, 8x8 is better than a LB, but I'd go 12x12 if you really want to do this with all the wire in one pipe

At 20 feet, the cost is low enough that I wouldn't fight with the wrong wire
 
To avoid these ads, REGISTER NOW!

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,967
Location
Central Iowa
Maybe I missed something, maybe there's another thread explaining what is going on, but why are you wanting to feed the house panel from the garage panel by passing through the meter main, bypassing the breaker that is already there for the house? You could make this a whole bunch easier by leaving the house panel alone.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
When using this computer there are issues with boxes popping up without me wanting them
If you use Firefox you can get the Adblock extension. It blocks both ads and popups and can be disabled if you wish. The extension icon is at the top right and looks like a jigsaw puzzle piece. It will save you some swearing.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,390
Location
VT
Maybe I missed something, maybe there's another thread explaining what is going on, but why are you wanting to feed the house panel from the garage panel by passing through the meter main, bypassing the breaker that is already there for the house? You could make this a whole bunch easier by leaving the house panel alone.
This is what I was having a hard time visualizing.

Assuming you're correct, the OP plan makes even less sense then before.
 
OP
M

Mr onetwo

Well-known member
Joined
Apr 6, 2011
Messages
2,005
Location
Coastal Maine
New 150 amp panel in garage with battery/inverter for emergency backup.Using the meter/disconnect as a pass thru to splice into existing house feed.Originally was going to be a diesel generator...too many logistical problems with that source of em power.
 
OP
M

Mr onetwo

Well-known member
Joined
Apr 6, 2011
Messages
2,005
Location
Coastal Maine
I am just going to bite the bullet and get the XHHW. *****, but it's my fault.Most important question...can I just bring the hots out to the pole to splice?I don't know why you would need to bring the neutral and ground back out since it is already out on the pole.Fill is acceptable with Southwire calculator either way
 

Attachments

  • fill.JPG
    fill.JPG
    85.2 KB · Views: 35
  • fill 2.JPG
    fill 2.JPG
    89 KB · Views: 30
  • interlock plan.JPG
    interlock plan.JPG
    184.9 KB · Views: 25
OP
M

Mr onetwo

Well-known member
Joined
Apr 6, 2011
Messages
2,005
Location
Coastal Maine
I ordered the wire and found a pretty good deal on a 12x12x6 pvc pull box.I will post up the results when we are done.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,752
If you use Firefox you can get the Adblock extension. It blocks both ads and popups and can be disabled if you wish. The extension icon is at the top right and looks like a jigsaw puzzle piece. It will save you some swearing.
The boxes are not adverts do not have much of a problem with ads, they are related to the operating system.
 