Mr onetwo
Well-known member
Good morning all, I am looking for advice for a short pull I will be attempting in a week or so.I have an existing 2" pvc conduit that goes from the 200 amp meter/disconnect on the pole over to my garage.Total run is under 20ft with 2 sweeps underground and an LB at the end.I am removing the existing 2-2-2-4 MHF 100amp feed to the garage and replacing it with 2/0-2/0-2/0-1 to feed a new 150amp panel.There will also be a longer piece of 2-2-2-4 coming back to splice into the 90amp feed over to the house.I have Polaris connectors for that. Both existing 100 amp breakers will be removed and the opening blocked off.Conduit fill calculator says this is legal and I believe I can remove both the ground and neutral conductors if it makes things easier.I will have some mule tape and a helper on hand.HI really don't want to run another conduit if possible.Has anyone pulled this much aluminum thru 2" pvc? Tips or tricks or helpful hints are appreciated.


..thanks Mike