This is the stuff I'm using. The actual run is about 210'. Some good ideas here. I can use a shop vac at on end and a compressor at the other.
Thanks for all the replies. Looks like something will work.
http://www.homedepot.com/p/Southwir...48479?storeId=10051&langId=-1&catalogId=10053

Poly? Is the proper pvc conduit really that expensive?
We did a job a couple years ago for a LARGE farm that needed a lot of underground primary conduit ran for some padmount transformers. It was roughly 23,000 feet of 5" with vaults about every 700'. We used nothing more than a rigid shop vac with a rag around the hose to help seal it in the end of the pipe. We were able to **** 500lb red polystring with nothing more than a walmart bag tied onto it, with another bag wadded up inside it. I've also done 2" at 1600' with the same shop vac.
It can be done, there's no reason to push string through conduit one stick at a time. The only time I've had an issue vacuuming is when I've waited to **** the string in and the conduit got some moisture in it or filled with water.
250' is gonna take a LOT of lube.
Better contact Tampa for recommendations...





I pulled 260' of cat5e,rg11,5c/22 and a pull string thru 1" of conduit with 3 bends a few weeks ago...no problem. Used regular pull string sucked with vac. Just have someone feed it while you pull...easy
gregtwojeeps;5233488 Put the pull string in it has you glue each length of pipe to the other.[/QUOTE said:Because that is the obvious and easy method. Plus it doesn't involve tools. This is GJ where everything needs to be complicated and use as many tools as possible lol.
But seriously just put the pull string in as your putting in the pipe. If you already have what you plan on pulling through then just install that as you go and eliminate the long pull all together.
EE here. If you can, take the liquid-tite back and get a refund. Forget about conduit. Use black poly water pipe - it's cheap and easy to work with. You aren't pulling in 120 or 240 volt wiring so water pipe is fine. Depending on soil conditions, you have a choice of the thin or thick wall type (different pressure ratings). Depending on presence of rocks and whether small round or sharp larger ones, you may want to bed the pipe in a layer of sand for protection. Bury it min. 24" below grade.
Regardless of whether you use liquid-tite, rigid PVC or poly pipe, make sure there are max. 4 x 90 degree bends. If using poly pipe, especially the low pressure/thin wall type, if it is wavy when placed in the ground, each little wavy bend adds up and can exceed the 4x90 total limit. Nice thing about the poly pipe is you can make large radius sweep bends. Sucking a pull-string through will work fine. I've always just used a piece of plastic garbage bag. You may find it easier to pull a lightweight string through first. Forget about a fish tape. As mentioned, get the pull string in right away.
You might consider installing a pull box about 1/2 way through the run but 250' is not a big deal if conduit/pipe is properly installed. If using water pipe, an ordinary in-ground plastic valve box is fine. You should use lubricant - liquid dishwashing soap or wire lube. You need to be careful not to exceed the max. pulling tension on the cable.
If under a driveway anywhere, pay attention to protection of the pipe/conduit so that it won't get damaged afterwards.
: wheres the facepalm?100% incorrect.
Sucking in a line is MUCH easier than blowing it in, IF you are using the right line. We do it with 3/4" and up ALL the time with ease. Done right 250' will **** in in about 5 seconds, literally. You just CANNOT use the jet line to pull the wire in. You must pull in a pulling rope. I use MuleTape.
A lot of speculation and questioning here, and I'll add. Let clarify this once and for all.
Do you mean liquidtite flexible conduit, as in Sealtite???
Or are you talking about rigid PVC conduit?
If Sealtite, all bets are off. You'll NEVER pull thru 250' of that. Does it even come in 250' lengths? All I have ever seen is 100' rolls.
And pushing Cat cable in will probably go in about 15-20 feet. It's not even close to worth considering.
This is the stuff I'm using. The actual run is about 210'. Some good ideas here. I can use a shop vac at on end and a compressor at the other.
Thanks for all the replies. Looks like something will work.
http://www.homedepot.com/p/Southwir...48479?storeId=10051&langId=-1&catalogId=10053
Thats seal tite,youll be kicking yourself in the nuts by the time you get anything through it more than a couple of feet.![]()
I would NEVER use water pipe as a conduit for any reason, after it's been installed underground anyone digging would have no idea it's anything but a water pipe, at least w/ PVC conduit the gray color would mean it's electrical.
To the OP, lose the sealtite, & buy SCH 40 PVC it will be easier & cheaper as others have said.
OMG 48 comments and counting on how and what is the proper conduit? This is just as silly as that thread about cordage!
File this thread in the ridiculous files.
Seriously, liquid tite sealtite, etc will be a royal PITA to pull through at that distance. Obviously the OP hasnt had much experience with it.
Yeah that would be along the same lines as using PEX for a gas line!
....ROFL. Stick to electrical. PEX is fine for natural gas.
I installed a few hundred feet of 2" PVC for conduit last year, as well as several thousand feet of poly water line.
I will probably use poly water pipe for my network cable runs next time. It's cheap, quicker than rigid PVC conduit, smooth and no fittings. Being buried conduit everything in it has to be rated for the wet anyway, small knicks/etc. won't be a problem like they would be in a gas line.
I'd probably use PEX next time for the water line. The poly is a ***** to terminate without it leaking.
And without question for underground gas it would be MDPE/HDPE/PEX.
i forgot to say red or blue PEX....yellow is the correct PEX for gas line.
In my career, I had to pull cat6 through some old, water filled underground facilities. I found that if I used plenum rated cables, and was careful not to make any cuts in the sheathing, they actually lasted as long as the technology did.

I would love to use PVC but I do not have any straight runs at all. I'm sure I could heat it and bend it but that would be a days work in itself, as I have about 25' to 50' large radius bending to do.
I just ran 4 #8 THHN through 50 ft of 3/4" EMT. I not concerned about 1 Cat 6 cable in a 3/4" conduit.
This does not look like a challenge.
You won't push a fish tape through even 100' of coreline if it's laid out straight, you'll have to use a mouse and cheese, tie a string to its tail and hold cheese at the other end, send it through and it will pull the string for you.
Customer believed that when she asked how we would get a rope through 650' of 3".
Not so far fetched! Didn't phone and electric companies use ferrets to pull cables through conduit years ago?
I would love to use PVC but I do not have any straight runs at all. I'm sure I could heat it and bend it but that would be a days work in itself, as I have about 25' to 50' large radius bending to do.
I just ran 4 #8 THHN through 50 ft of 3/4" EMT. I not concerned about 1 Cat 6 cable in a 3/4" conduit.
This does not look like a challenge.
I'll repeat, use a strong pull rope, plenty of lubricant, and only bury after a successful continuity check. Although it may not "look like a challenge" looks are deceiving. And report back on how all this went for ya.
You seem to have left the bold part out in your OP which would have helped the people out on GJ in knowing ....while they were helping you on your project while replying.
I must ask with all due respect, why ask for advice on GJ when you were going to do the project the way you wanted anyway ?
The unfortunate part is that you'll NEVER come back here and admit what a hard time it was and what a terrible idea it was to use Sealtite for such a long underground run.And of course I got plenty of answers advising me not to use liquid tight.
There's no harm done, that's how you learn, by trying it.
MTW Ω
That's a ridiculous answer, that's not how you learn, especially when you have people you can ask who have already been there, done that.
For example, when I'm training apprentices, I expect them to pay attention and realize there is a reason behind why we do things a certain way. That doesn't mean he tries all the wrong ways first, "because that's how you learn, by trying it."


That's a ridiculous answer, that's not how you learn, especially when you have people you can ask who have already been there, done that.
For example, when I'm training apprentices, I expect them to pay attention and realize there is a reason behind why we do things a certain way. That doesn't mean he tries all the wrong ways first, "because that's how you learn, by trying it."
You seem to have forgotten that I never asked which type of conduit was the preferred type. I asked how to pull through 250' of liquid tight. And I got plenty of great answers like using vacuum cleaners and the availability of 240' fish lines.
And of course I got plenty of answers advising me not to use liquid tight.
Thanks for the extra commentary.
You seem to have forgotten that I never asked which type of conduit was the preferred type. I asked how to pull through 250' of liquid tight. And I got plenty of great answers like using vacuum cleaners and the availability of 240' fish lines.
And of course I got plenty of answers advising me not to use liquid tight.
Thanks for the extra commentary.
I am not posting this in a mean spirited manner but simply attempting to put some clarification on why I made the comment above... that you replied to above. ....
When a poster comes to a electrical forum that has a lot of qualified electricians helping people out, the poster bears some responsibility for framing their question to where the posters can better understand the issue at hand. Yes, you did state your OP question about pulling the LAN cable through over a 200 ft. run of 3/4 " LT flex.... You got some great replies and even a simplistic reply like mine that required no tools, just simply tie a 1/2" hexnut on the pull string and drop it through each stick of PVC before you glued it...then drop the whole run of glued conduit in to the ditch and back fill... Then pull in a cleaning rag and stronger rope in with the already installed pull string..
You did not state that physical barriers would inhibit you from running straight PVC conduit once the electricians on here recommended not using LT flex. If you had came back and mentioned WHY you wanted to use flex, the posters would have been guiding you on how to run PVC in curved runs. Simply because to a pro sparky..trying to run conductors through 200 ft. of LT flex.... just doesn't suit well and is not the correct application for the raceway. I see now you are going to run the flex and I am sure you will make it work out well for you. Good luck on your project![]()
And of course I got plenty of answers advising me not to use liquid tight.
.
maybe i am missing the point. Why not just put direct bury cable in the ground then? You seem to be concerned about ease of install and not so much changing the cable in the future.
http://www.amazon.com/ethernet-wate...1446642842&sr=8-1&keywords=direct+burial+cat6
http://www.amazon.com/ethernet-wate...1446642842&sr=8-2&keywords=direct+burial+cat6
http://www.amazon.com/filled-floode...446642842&sr=8-13&keywords=direct+burial+cat6
all the options above are way cheaper than your current wire+nm conduit and obviously much easier to install since you just drop it in the ditch and go. Plus you can run 3-4 lines for the future in case one gets damaged.
I suggest you make a good as-built utilities going into the ditch should you ever need to bring something else out.

Maybe I am missing the point. Why not just put direct bury cable in the ground then? You seem to be concerned about ease of install and not so much changing the cable in the future.
http://www.amazon.com/dp/B00AWQ13R6/?tag=atomicindus08-20
http://www.amazon.com/dp/B00CA2X5W6/?tag=atomicindus08-20
http://www.amazon.com/dp/B005AIP8Z4/?tag=atomicindus08-20
All the options above are way cheaper than your current wire+nm conduit and obviously much easier to install since you just drop it in the ditch and go. Plus you can run 3-4 lines for the future in case one gets damaged.
I suggest you make a good as-built utilities going into the ditch should you ever need to bring something else out.