Pulling wire questions...

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
.......,so it's all up to the local inspectors
You see...it's really NOT. It's up to local written code amendments. Inspectors CANNOT make up codes, they are simply there to enforce them.
It's guys like you that cave to whatever the inspector wants that lead to inspectors with a god complex.
 
To avoid these ads, REGISTER NOW!

volleyball

Well-known member
Joined
Aug 29, 2011
Messages
4,127
Location
NY, not NYC
It is like fighting with your kids,spouse, parents. You need to pick and choose your battles. Is it worth it to win one and your next 20 jobs all go under the microscope and take extra long time to get passed.
You guys are both right.
How you deal with those inspectors goes a long way. Years ago I went for a permit to put in a patio door in a basement wall with 2 stories above it and the roof on top. They denied it. It wasn't until I got a conversation going that I found the reason, they assumed too much load. I then mentioned the large picture window right over the proposed opening already took the load off of that span. A quick approval came. Now I have a relationship where I get there view and I counter.
Saying that this location demands a higher number of spaces and there is no written code to make it illegal may do the trick. If not going over their head usually works.
 

Bib Overalls

Well-known member
Joined
Dec 4, 2006
Messages
3,318
Location
Jonesboro, Arkansas
Going over someone's head, particularly an inspector that you have to work with on a recurring basis, may get you what you want now but could have ramifications down the line.
 

volleyball

Well-known member
Joined
Aug 29, 2011
Messages
4,127
Location
NY, not NYC
I inferred working with them. But if you need to, don't be afraid. Sometimes it works in your favor and the inspector no longer gives you flack. Just don't rub it in.
 

FordsnFishin

Well-known member
Joined
Dec 30, 2013
Messages
96
Location
Mid-Illernois
True!

Ok so something like this

3 - 220 circuits
5 - single outlet circuits
4 - multi outlet circuits. (Maybe 4 on each?)
1 - circuit for 2 garage door openers. (Or should they be independent?)
2 - for lighting
1 - for exterior lights and outlet
1 - to the furnace

That's only 20.... I'm sure I'm missing something right now though.

Looking alot better. I know you have alot of space in your panel, but really if you want to save some money you can throw those garage door openers on the lighting circuits. Assuming you aren't using ancient lights you picked up from a auction, they shouldn't be too much of a load. The doors you arent going to be using constantly, so it will be a temp load on the circuit, and they usually don't take much to run anyhow.

As already mentioned, 8 receptacles to a circuit is a pretty standard go by. So you throwing 4 on a circuit should be no problem at all.
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
I inferred working with them. But if you need to, don't be afraid. Sometimes it works in your favor and the inspector no longer gives you flack. Just don't rub it in.
I fully agree here.
I have to say, the last time I had to go over an inspector's head was quite a few years ago, and he was a temp fill-in guy for my regular guy who was on holiday. The guy was a complete **** and his supervisor on LI (we're upstate) agreed with him sigh unseen because he could not be bothered. The request was totally uncalled for and it nearly made me change agencies. When my regular guy got back he agreed with me that the other guy was on a power trip.
Outside that one instance I cannot remember having any trouble with an inspector. I guess I am lucky with the guys I use that they have common sense and don't make things up, and they know that I know what I'm doing.

I honestly feel sorry for guys who have to use municipal inspectors.
 

2ManyProjects

Well-known member
Joined
Jul 18, 2013
Messages
757
I'm just about ready to start drilling holes and wiring up my new garage.
I've never done any new structure wiring before.
I'm going to be sheeting with osb so I can hang stuff randomly on the walls.
What is the safest way to run all the wires? Should I drill near the tops of the studs and just bring single wires down to each outlet? How far in should the holes be? Should the wires run behind or in front of the insulation? How big of holes? :dunno:

There are a number of different ways this CAN be done, but some are better than others. Given your desire to be able to "hang stuff randomly on the walls" in the future, you should go to some length to ensure that there WON'T be wires lurking behind wherever you might want to drive a (possibly too long) fastener five years from now (i.e., long after you've forgotten exactly where each wire actually runs). One way to accomplish that is to wire everything at least primarily from the top, drilling ONLY through the top plate. Anywhere you DO need a horizontal run, keep it absolutely as low as possible, while still observing any code restrictions (which may specify a minimum height, due to concerns about flood water and such).

Given your 2x4 framing, you can "legally" drill holes in it of up to one-inch diameter; but this presumes that you get those holes PERFECTLY centered every time. Personally, I'd stick to 3/4-inch, whenever possible; this is still large enough to run at least a couple NM-B cables through (if perhaps a tight fit in the case of something like 10-3 w/g). Also, do NOT make "Swiss Cheese" out of your framing, by drilling multiple holes in close proximity.

The insulation should not be an issue. The wire gets stapled to the side of the stud from within a few inches of where it exits the hole to within a few inches of its final destination; and so it will be out of the way for at least most of its run. In the case of any horizontal segments, the wire should be in the middle (depth-wise) of the stud cavity (due to the holes being centered in the studs, if nothing else); in this case, the insulation gets "split" where it passes the wire, with half going behind the wire and half in front of it. Note that you need to get your electrical inspection done BEFORE you put in the insulation, so that the wires remain visible.

I'm going to be running lots of outlets. Probably close to 20 each on their own breaker So I never blow any. So lots of wire to run.

WHOA, NELLIE!!!

That is GROSS overkill, and a huge waste of money & effort.

For your general-purpose 120V outlets, my usual "recipe" will likely suffice: Put one double-gang box every 6-8 feet (maybe 10 feet, at the most) around the entire perimeter of the space, with each of the two duplexes in that box fed from a different breaker than the other one. In relatively small shops, two 20A circuits will normally handle the whole thing. In larger shops (particularly if there will be more than one person working concurrently), split it up further as you see fit; but even so, I SERIOUSLY doubt you'll really need to do so in a 30x30 "one man band" shop. This is relatively easy to do, and requires only two runs of 12-2 NM-B from one outlet box to the next, all the way down the line. Note that the FIRST pair of outlets in the run need to be GFCI types, and the rest of the "daisy chain" runs off the "Load" terminals on those outlets. In theory, you can use a single run of 12-3 from the breaker panel to the first pair of outlets; but personally, I wouldn't. First, it's easy enough to just pull another length of 12-2 off that big spool you're going to buy anyway; second, using 12-3 would require running the whole thing off a common-trip double-pole breaker, which means that if EITHER circuit trips, they ALL go out. Bottom Line: It's just not worth the hassle to save a few pennies on wire, IMCO.

Optionally, add a third 20A circuit in the vicinity of the workbench, especially if you (will) have high-draw 120V tools (bench grinder, drill press, etc.) in that area; but this is still really more for "peace of mind" than to address an actual NEED, as you presumably won't be running more than one of those tools at a time anyway.

Keep the bottom of the boxes at least 49-50 inches off the floor; you'll understand why the first time you try to store a 4x8 sheet of plywood, drywall, etc.

Most permanently installed "machinery" will likely require 240V; the specific current (and thus wiring) requirements will depend on the particular machines in question. Until you/we know exactly what those machines are (or will be), it's pointless to guess at it further.


A 1 or 1 1/4" spade bit will do you some work.

No. A 1-1/4" hole in a 2x4 stud (which is only 3-1/2" wide to start with) is too large, and will not leave sufficient "meat" on either side of the hole. As noted above, even 1-inch is "iffy", because it requires absolute precision in its placement.


Running dedicated lines to thing that will run by themselves (compressor, dust collector, etc) makes sense, but to dedicate everything else is silly.

I agree with that.

It's a 30x30 garage.
Yeah maybe 20 dedicated is a bit over kill.

No doubt about it.

There's going to be 2 - 220 outlets. One for a welder and one for a compressor.

These circuits need to be sized for the SPECIFIC equipment in question; and the proper methods to do that aren't necessarily obvious to the casual observer / DIY-er. Have you purchased these tools yet? If so, what are they, specifically? If not, then you need to make at least a fairly sharp (yet conservative) "educated guess" about what they will be.

Then a few 110's dedicated for power equipment that wont ever move like Drill press, Bench grinder, ban saw...also later probably a mill and lathe.

The drill press and bench grinder are covered above. The rest of that stuff is rather unlikely to run off 120V.

I have 100 amp service for the garage and a 48 circuit box in it. I figure it's better to over do it now then wish I had done it later.

No argument with the basic philosophy; but you are taking it to a silly extreme. And remember, you DO want to leave room for expansion later, because you cannot possibly predict EVERYTHING you're going to want to do in that space five or ten years down the line.

Usually it will just be me working in there but I could easily see 3 people working all at once.

And all using 120V power tools at the same time? THAT is the key issue.


I understand how they are getting it. DO NOT understand why this requirement is being touted for a RESIDENTAL garage.

Nobody has claimed that it is a "requirement". It is a RECOMMENDATION, which is a fundamentally different thing. Building something only to the minimum legally mandated requirement is a good way to ensure disappointment later.


Ok so something like this

3 - 220 circuits
5 - single outlet circuits
4 - multi outlet circuits. (Maybe 4 on each?)
1 - circuit for 2 garage door openers. (Or should they be independent?)
2 - for lighting
1 - for exterior lights and outlet
1 - to the furnace

That's only 20.... I'm sure I'm missing something right now though.

Still overkill.

As noted above, the 240V stuff needs to be addressed separately. But fourteen 120V circuits is just silly. AT MOST (and with a big nod to the idea of multiple folks working simultaneously), four or five "general purpose" 20A/120V circuits (i.e., feeding each "half" of the space from a different "pair" of 20A circuits, with one more added in the workbench/tool area for good measure) will be MORE than adequate, even accounting for that drill press, bench grinder, blast cabinet, etc.

Two circuits for ALL of the the interior lighting will be quite sufficient. The exterior lighting can near-certainly be "piggy-backed" onto these same two circuits, unless you're planning on several HUGE Metal-Halide floods or similar.

The exterior outlets should NOT be on the same circuit(s) as your lights. But again, unless you're planning on (several) huge loads, they CAN be on the same circuits as your general-purpose interior outlets.

Ideally, the garage door openers would be on their own circuit (one @ 20A will near-certainly do); but this is mostly to avoid the need to GFCI-protect that circuit (which will also require that the GDOs be hard-wired -- but that's OK; they're not going anywhere).

The (presumably gas-fired) furnace does not really need its own circuit; but if you really want to, go for it. What it DOES need is a conspicuously placed and easily accessible Emergency Shut-Off switch, with an appropriately labeled (and usually red) switch plate.

So that's nine 120V circuits, MAX; and I'm being generous.


Garage door openers could go 1 on each lighting circuit.

MAYBE, depending on the relative loads. But probably not a good idea in any event.


OMG. I thought this would be a huge shop and 20 breakers might be reasonable. A 20x20?!

Actually, he said 30x30; but your point is well-taken.

4 walls, 3 without garage doors on them let's assume. If you want to go ********, do three MWBC circuits, one for each GD-less wall, with each receptacle split.

Given the need for the outlets to be GFCI-protected, MWBCs cannot be used except possibly for the initial run from the panel to the first pair of outlets; and as noted above, even that comes with a down side. IMCO, it's just not worth it.

 

kenfain

Well-known member
Joined
May 12, 2013
Messages
298
Location
just west of Walton
I'd like to jump in here and make a point. The doors being on their own circuit might help security. You can't trick an un powered garage door into opening. Thieves have been known to use a fake signal that's created by one of several methods. When I flip the breaker, that door can only be opened from the inside. And you guys just gave the op plenty of space in his panel. I think it's a good use of dedicated circuit. Makes me feel better when I'm at work. Of course, nothing is totally secure. Bring a couple slices of ham, the dog probly let anyone right in.
 

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
Given the need for the outlets to be GFCI-protected, MWBCs cannot be used except possibly for the initial run from the panel to the first pair of outlets; and as noted above, even that comes with a down side. IMCO, it's just not worth it.

They certainly can, and four 12-2 in one double box is much less fun to work with than two 12-3 :) I have this setup in my barn. Looks like the breakers are still quite expensive though, which *****. It'd be cheaper to run a different GFCI at each outlet!

Separate feeds is definitely the much more economical way to go.
 

CoopVA

Well-known member
Joined
Jan 20, 2014
Messages
2,144
Location
Virginia
I pretty much agree with everything you say here. What is the issue with running 12/3 on separate breakers to the first outlet from the panel to the first outlet and then to the rest... Is it the potential between phases in one box? You can also use GFI breakers and not have to use GFI recepticals... Is it needing separate neutrals for the GFI?


Sent from my iPad using Tapatalk
 
Last edited:

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
The shared neutral on a straight MWBC is what causes the problem for using GFCI outlets. The solution is to use a GFCI breaker. Also the breaker needs to be a DP or singles with a handle tie, not separate.

I pretty much agree with everything you say here. What is the issue with running 12/3 on separate breakers to the first outlet from the panel to the first outlet and then to the rest... Is it the potential between phases in one box? You can also use GFI breakers and not have to use GFI recepticals... Is it needing separate neutrals for the GFI?


Sent from my iPad using Tapatalk
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
I always run 12-3 to first outer and then 12-2 to other outlet with two gfi to protect the lines, never had any issues with it making gfi go bad. But also helps with not having to go to panel if gfi trips.
 

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
The shared neutral on a straight MWBC is what causes the problem for using GFCI outlets. The solution is to use a GFCI breaker. Also the breaker needs to be a DP or singles with a handle tie, not separate.

Only issue is a DP GFCI 20A is like $140, single pole is $40-50 and a GFCI receptacle can be had for $5-10. :)

You cannot use singles with a handle tie for a GFCI MWBC, because it's sensing current from each hot and then making sure it all comes back on the neutral. Separate GFCI breakers handle tied together would not be able to do that.
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Yep.. you're correct. I didn't really think about it when I said two singles tied together. My mind was more on the fact that a MWBC can't be on separated breakers.


.....

You cannot use singles with a handle tie for a GFCI MWBC, because it's sensing current from each hot and then making sure it all comes back on the neutral. Separate GFCI breakers handle tied together would not be able to do that.
 

CoopVA

Well-known member
Joined
Jan 20, 2014
Messages
2,144
Location
Virginia
Makes sense... Threw me for a loop there with the double breaker....


Sent from my iPad using Tapatalk
 

2ManyProjects

Well-known member
Joined
Jul 18, 2013
Messages
757
Given the need for the outlets to be GFCI-protected, MWBCs cannot be used except possibly for the initial run from the panel to the first pair of outlets; and as noted above, even that comes with a down side. IMCO, it's just not worth it.

They certainly can, and four 12-2 in one double box is much less fun to work with than two 12-3 :)

I was presuming GFCI outlets, as opposed to GFCI breakers; but the point remains...

The MWBC can't be used "downstream" of the GFCI device(s), because the common Neutral will effectively ALWAYS be "out of balance" with either of the Hots, thus tripping the GFCI(s).

And as you later point out, economically, "forcing the issue" with a dual-pole GFCI breaker is effectively prohibitive.

 

CoopVA

Well-known member
Joined
Jan 20, 2014
Messages
2,144
Location
Virginia
Why not just pull 12/4 for the two GFI circuits and be done with it?


Sent from my iPad using Tapatalk
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
Why not just pull 12/4 for the two GFI circuits and be done with it?


Sent from my iPad using Tapatalk

Are you talking with gfci I breakers, in that case just pull two 12-2 romex and just go to outlets with no splices. If your talking gfci outlets the 12-3 works.
 

2ManyProjects

Well-known member
Joined
Jul 18, 2013
Messages
757
Why not just pull 12/4 for the two GFI circuits and be done with it?

I suppose that could work. Obviously, 12/4 is not as commonly available as 12/2 and 12/3, and I'm not sure how the costs would compare. Hmmmm... Not too surprisingly, a quick (but hardly exhaustive) Google check implies that it would actually be MORE expensive than two runs of 12/2:

https://www.platt.com/platt-electri...ltiple/1222NMBGX250C/product.aspx?zpid=526460

https://www.platt.com/platt-electri...Multiple/122NMBGX250C/product.aspx?zpid=62408

And besides, with a nod to the K.I.S.S. Principle, he's most likely already going to have a big spool of 12/2 sitting there anyway, for all the other "stuff", so why not just use it?

 

Speed4Life

Well-known member
Joined
Jan 27, 2014
Messages
234
If you've never done any wiring, get this book. Previous to buying my home all I'd ever done with electrical is low volatage and installing ceiling fans with my dad. This book is a great foundation for electrical knowledge and pretty comprehensive. I've used it for a lot of wiring projects on my house and if there's something I don't understand about what they did or the diagrams I seek additional instruction. Just make a good plan, take your time, follow code, and double/triple check everything before you button up the walls.

http://www.amazon.com/Black-Decker-Complete-Guide-Wiring/dp/1589236017/ref=sr_1_1?s=books&ie=UTF8&qid=1391540940&sr=1-1&keywords=black+and+decker+electrical+wiring
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
Why not just pull 12/4 for the two GFI circuits and be done with it?


Sent from my iPad using Tapatalk
Because not everyone wants 3/4 of a roll of 12/4 sitting around.
WHY not just run 12/3 to the first and then split from there?
Or just run two 12/2's?

There are a lot of simple options here as opposed to buying an unnecessary $150 roll of wire.
 

CoopVA

Well-known member
Joined
Jan 20, 2014
Messages
2,144
Location
Virginia
Because not everyone wants 3/4 of a roll of 12/4 sitting around.

WHY not just run 12/3 to the first and then split from there?

Or just run two 12/2's?



There are a lot of simple options here as opposed to buying an unnecessary $150 roll of wire.


Pulling one cable is simpler than pulling two... Yeah, it costs 93 cents a foot compared to 74 cents a foot for 2ea 12/2 cables...

It's an option.


Sent from my iPad using Tapatalk
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
Pulling one cable is simpler than pulling two... Yeah, it costs 93 cents a foot compared to 74 cents a foot for 2ea 12/2 cables...

It's an option.


Sent from my iPad using Tapatalk
My point is you and I have it on the truck. A DIY will sit on the 150' of it that's left for years.
 

volleyball

Well-known member
Joined
Aug 29, 2011
Messages
4,127
Location
NY, not NYC
My local supply place sells anything they carry in rolls in by the foot. I've never asked for 12/4 so I am assuming. They are not open now to find the price.
 