Question about 2-2-2-4 al wire

green.bubbly

Well-known member
Joined
Dec 14, 2008
Messages
2,156
Location
Lafayette, LA
I was looking online at Home Depot and saw they sold 2-2-2-4 aluminum service entrance wire. Assuming the "4" is the ground, why is it a larger gauge? Surely I am not understanding something...
 
To avoid these ads, REGISTER NOW!

RPH

Well-known member
Joined
Dec 17, 2006
Messages
4,190
Location
Michigan Thumb
The four is smaller than the two. Wire gauges are a weird scale, 12 gauge is bigger than a fourteen and a ten is bigger than a twelve. And so it goes until you hit the ought series 2/0, 4/0 the wire gets bigger until you hit the mcm series. Then the numbers make sense. Bigger number, bigger cable in the mcm series. Not sure who came up with the gages for wire and sheet metal but I would bet it’s an British holdover.
 
OP
G

green.bubbly

Well-known member
Joined
Dec 14, 2008
Messages
2,156
Location
Lafayette, LA
The four is smaller than the two. Wire gauges are a weird scale, 12 gauge is bigger than a fourteen and a ten is bigger than a twelve. And so it goes until you hit the ought series 2/0, 4/0 the wire gets bigger until you hit the mcm series. Then the numbers make sense. Bigger number, bigger cable in the mcm series. Not sure who came up with the gages for wire and sheet metal but I would bet it’s an British holdover.



Ok, that is what I thought. I was confused because I thought the 2-2-2-4 was ought size.

Thanks
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,950
The four is smaller than the two. Wire gauges are a weird scale, 12 gauge is bigger than a fourteen and a ten is bigger than a twelve. And so it goes until you hit the ought series 2/0, 4/0 the wire gets bigger until you hit the mcm series. Then the numbers make sense. Bigger number, bigger cable in the mcm series. Not sure who came up with the gages for wire and sheet metal but I would bet it’s an British holdover.

Brown and Sharpe. it's as american as you can get. It's actually a very sensible system, there's a reason it's still in use 150 years later. Direct area measurements might be clearer, but they're harder to work with.
 

RPH

Well-known member
Joined
Dec 17, 2006
Messages
4,190
Location
Michigan Thumb
You nailed that one.
“ In 1856, clockmakers Joseph R. Brown and apprentice-turned-partner Lucian Sharpe had begun to manufacture precision measuring tools in Pawtucket, R.I. One that was sorely needed was an accurate measuring gage for wire. (Readers will note that I prefer the spelling gage, commonly accepted in reference to wire, and accepted as a variant for gauge by the American Heritage Dictionary.)

Sharpe suggested producing sizes of wire in a regular geometric progression. Until that time, wire-measuring tools were made by English manufacturers and were, to say the least, variable in quality and accuracy. Sharpe took 50 of his new low-cost gages to a meeting of brass manufacturers of Connecticut, centered in the Naugatuck Valley. A gage consisted of a flat circular piece of steel with precision-machined slots corresponding to the different sizes of wire.

It was a big hit. Brown & Sharpe wire gages became the standard well into the 20th century. Eventually, Sharpe's progressive system became adopted as the AWG, or American Wire Gage, which we use today. “
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
12,000
Location
Austin, TX
Be aware - I found that it's cheaper to order this wire online than it is at HD... At least in lengths of 75' or more.

Other is that SER is typically (outdoor only) - probably can't be used to feed an interior panel... (Just in case you're thinking about doing it that way).
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,596
Location
Fullerton, CA
Other is that SER is typically (outdoor only)

?????
SER is pemitted indoors as well as outside, but may not be used underground
The ground in the MHF is actually larger than it need be.
With the ampacity limited to 90A, it could be #6
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,232
Location
Modesto, CA
Be aware - I found that it's cheaper to order this wire online than it is at HD... At least in lengths of 75' or more.

Other is that SER is typically (outdoor only) - probably can't be used to feed an interior panel... (Just in case you're thinking about doing it that way).

say what? :wtf::wtf::headscrat:headscrat
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Mostly but maybe not all of it. I showed mine to the AHJ and asked about inside conduit - "not required". Easy enough.

I'm not aware of any assembled wire that is listed as "Mobile Home Feeder" to not have multiple insulation ratings allowing it to be installed inside of a structure.
 

OptionalStop

Well-known member
Joined
Mar 23, 2018
Messages
128
Location
Rochester NY
My local electrical inspector advised me that my 2-2-2-4 MHF wire can be direct buried however must be in conduit outside of the ground, and inside structure.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,232
Location
Modesto, CA
Mostly but maybe not all of it. I showed mine to the AHJ and asked about inside conduit - "not required". Easy enough.

Loose conductors are not permitted to be installed inside walls without being in conduit.

MHF is made up of 4 loose conductors not having an overall jacket.

Your inspector is wrong.
 
Last edited:

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,871
Location
NW Iowa
We don't need no stinkin' staples, we don't need no stinkin' cable with a sheath...

Probably one of those guys that cuts off the ground in romex.

:headscrat
 