Anyone using 16/2 NM-B and 10A breakers ? Lighting circuits ?

Isn't that three things?Two things I don't need in my truck, another size wire and 2 more refrigerants.

I think the code needs to be revised to allow 16/2 NM cable. No reason not to use it for hardwired dedicated loads plus with copper prices these days it'd save $$$.
Nope.
2023 NEC 210.23A permits 10A ckts but table 210.24 requires #14 Copper for the 10A ckt. So what's the point at this time?
Why does the 16/2 exist then?
Assuming the post I quoted is correct, then how is it compliant on a fire alarm circuit?I've used it on fire alarm power circuits.
I think the code needs to be revised to allow 16/2 NM cable. No reason not to use it for hardwired dedicated loads plus with copper prices these days it'd save $$$.
A few electricians I know don't bother with 14 gauge anymore even.Two things I don't need in my truck, another size wire and 2 more refrigerants.
If they use 16/2 with a 15A breaker !It really isn't a lot in savings, plus having to find 10A breakers ( and stock them ).
The good part is joey homeowner will buy the cheaper wire and burn down their house with some regularity ...
Is that an exception in NEC ?I've used it on fire alarm power circuits.
If they use 16/2 with a 15A breaker !
Is that an exception in NEC ?
If they use 16/2 with a 15A breaker !
So 16/2 on a 10A is OK for an alarm but not a light?760.27 Only copper conductors shall be permitted to be used for fire alarm systems. Size 18 AWG and 16AWG conductors shall be permitted to be used.
So 16/2 on a 10A is OK for an alarm but not a light?
Chapter 7 is special equipment and yes it details ampacity and ocp values for #18 and #16 CU for fire alarms, this is not the scope of your original post, so it is noise to you. Read the articles in chapter 2 that I already posted for your intended purpose.Is that an exception in NEC ?
What NEC version are you referring to? It's not even referenced as edited or deleted in NEC 2023. 760.43 in 2023 NEC states equivalent verbiage.760.27 Only copper conductors shall be permitted to be used for fire alarm systems. Size 18 AWG and 16AWG conductors shall be permitted to be used.
Fire alarms are part of specialized equipment found in chapter 7 of NEC and these subsequent chapters can override requirements in chapter 2 & 3. Just like chapter 4 for motor circuit conductor ampacity.Assuming the post I quoted is correct, then how is it compliant on a fire alarm circuit?
especially when the labor is the same effort.The results of being cheap when buying materials can be very Expensive to correct.
What NEC version are you referring to? It's not even referenced as edited or deleted in NEC 2023. 760.43 in 2023 NEC states equivalent verbiage.
Who said anyone was "angry"?No idea why you'd be "angry" over being slightly overkill on maybe 1 circuit in a house.
The NEC has all kinds of dubious "exceptions". Welder circuits are allowed to pair a 50a outlet and breaker with 12 gauge wire as long as you label the outlet "welder only". Ignoring that modern inverter welders have very high duty cycles and that when the sticker falls off in 5 years, someone could plug in whatever they want.So 16/2 on a 10A is OK for an alarm but not a light?
It's just that with modern LED lighting, it's unnecessary to run 12 or 14 gauge wiring for lighting circuits. A single 8a 16awg circuit could provide 950w continous power. I think my entire house has maybe 300w worth of lights? So it's wasteful to use 14 or 12 when a single 16g circuit at 8a could light three homes.
The 80% rule for continuous loads still is valid, which would pretty much eliminate the use of incandescent loads exceeding 8A.That only works until some knucklehead replaces the LEDs with incandescent bulbs because 'Murica!
Who said anyone was "angry"?
It's just that with modern LED lighting, it's unnecessary to run 12 or 14 gauge wiring for lighting circuits. A single 8a 16awg circuit could provide 950w continous power. I think my entire house has maybe 300w worth of lights? So it's wasteful to use 14 or 12 when a single 16g circuit at 8a could light three homes.
The NEC has all kinds of dubious "exceptions". Welder circuits are allowed to pair a 50a outlet and breaker with 12 gauge wire as long as you label the outlet "welder only". Ignoring that modern inverter welders have very high duty cycles and that when the sticker falls off in 5 years, someone could plug in whatever they want.
Don't forget about the motor sizing rule that will let you put a 40A breaker on a 12awg wire going to a motor, on the assumption the motor's overload will protect the wire. Just hope there are never any partial shorts somewhere or no one accidentally changes out the motor for something bigger.
Do you think that is going to stop anyone? The only thing that will keep someone from overloading the circuit is the breaker tripping.The 80% rule for continuous loads still is valid, which would pretty much eliminate the use of incandescent loads exceeding 8A.
That applies to 16/2 @10A as much as it does 14/2@15A and 12/2@20A...Do you think that is going to stop anyone? The only thing that will keep someone from overloading the circuit is the breaker tripping.
It applies to all wires sizes and types. Do you think people actually take the 80% of continuous load into consideration when adding/changing things? They don't. Look at my reply, then what I was replying to, then look at what that was a reply to.That applies to 16/2 @10A as much as it does 14/2@15A and 12/2@20A...
I was agreeing with you/adding to your point. They argument was irrelevant as people will be dumb with anything that can be plugged/wired in, not just 16/2It applies to all wires sizes and types. Do you think people actually take the 80% of continuous load into consideration when adding/changing things? They don't. Look at my reply, then what I was replying to, then look at what that was a reply to.
I've seen a lot of 20 amp 120 circuits humming along at 20+ amps 24/7. Eventually the breaker fails; the solution is usually to put in a new breaker since nobody want's to spend the money to do it right and "It's been like that for years".I was agreeing with you/adding to your point. They argument was irrelevant as people will be dumb with anything that can be plugged/wired in, not just 16/2