Oldwizard was.

It's rare to see ONLY lighting circuits in houses around here, at least in normal sized houses with 125 amp service.
They’re nearly universal in commercial work, though.

Reducing the wire size for lighting only circuits in a large office building can save a lot, simply because there's so much wire used. 16 AWG wire uses 40% the copper of 14 AWG wire, so the cost savings potential is quite large. in smallish quantities, 16 awg MTW costs 2/3 what 14 AWG MTW does. (I'm list MTW because it's very similar to THHN, which isn't available smaller than 14 awg. larger sizes of stranded thhn are often cross listed as thhn/thhw-2/mtw.) Saving a third on lighting wire when you're using hundreds of miles of the stuff is a big chunk of change.
 

Sumboodie

Well-known member
Joined
Mar 20, 2021
Messages
10,745
Location
AK
They’re nearly universal in commercial work, though.

Reducing the wire size for lighting only circuits in a large office building can save a lot, simply because there's so much wire used. 16 AWG wire uses 40% the copper of 14 AWG wire, so the cost savings potential is quite large. in smallish quantities, 16 awg MTW costs 2/3 what 14 AWG MTW does. (I'm list MTW because it's very similar to THHN, which isn't available smaller than 14 awg. larger sizes of stranded thhn are often cross listed as thhn/thhw-2/mtw.) Saving a third on lighting wire when you're using hundreds of miles of the stuff is a big chunk of change.
Yes, but I was talking about residential.
Would need to be a large house or have unique lighting needs to need to have lights on their own circuits.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,593
Location
Fullerton, CA
Yes, but I was talking about residential.
Would need to be a large house or have unique lighting needs to need to have lights on their own circuits.
Every place I've lived for the last 50 yrs, both large and small, had separate breakers for lighting circuits (Even apartments).
 

Sumboodie

Well-known member
Joined
Mar 20, 2021
Messages
10,745
Location
AK
Every place I've lived for the last 50 yrs, both large and small, had separate breakers for lighting circuits (Even apartments).
So each room had at minimum 2 breakers?

I've lived in 6 houses over the last ~25 years, none had that.
 

Codyboy

Well-known member
Joined
Jan 31, 2019
Messages
1,708
Location
S.E. TEXAS
So each room had at minimum 2 breakers?

I've lived in 6 houses over the last ~25 years, none had that.
When I wired my current house I did similar.

Two bedrooms had a breaker each for receptacles and another breaker for the receptacles on a shared wall between them. Another breaker shared fan/light and had the hallway lights on it.
So 4 breakers for two rooms.
Overkill? Probably.

Basically each room had its own breakers.
Master BR has Probably 3 breakers not counting the master bathroom.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,006
Location
Central Iowa
Just about every place I've been the lighting and receptacles have been on the same circuit, with exceptions of course. I try to put a bedroom to a circuit, will sometimes split three beds to two circuits. There might be a time when a bunch of lights are on one circuit (kitchen, dining, living room, etc) with a separate circuit for the living room and entry recepts. It really depends on how the house is built and where the service is before I make up my mind how everything is going to be.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,006
Location
Central Iowa
The main reason I don't put bedroom lights and outlets on the same circuit is people tend to use 1500 watt space heaters a lot. 2 of them on the same circuit will trip a 15 or 20 amp breaker and if the lights are on it, it'll go dark.
We are about a month away from me getting calls about bad breakers; the first question I ask is if they have a space heater. When the answer is yes, I tell them it will be much cheaper to throw the heater in the nearest dumpster vs me adding a circuit. I also tell them I would be more than happy to take their money, but once again, they can turn the furnace up a couple of degrees and be money ahead.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,593
Location
Fullerton, CA
We are about a month away from me getting calls about bad breakers; the first question I ask is if they have a space heater
I used to do commercial service calls. Every October we'd start getting from calls from offices of blown 20A breakers. Invariably the secretaries felt cold, although the temp was the same 24/7/365.
I'd just see them, advise the manager, wait until the heaters were unplugged and reset the breaker. (no tools):)
 
Last edited:

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,909
since we're talking space heaters, I had to put this in .
space heater & non aluminum receptacle without a copper pigtail
HPIM2779.JPGspace heater & non aluminum receptacle without a copper pigtail

House had Al wire, and someone used a Cu only receptacle on it? Bad news when you put a big load on it, it's the differential thermal expansion that causes the problem. Connections get loose, and have high resistance.

I burnt myself on the plug of a space heater once. Was at someone's house, and unplugged the heater. Damn thing was 400 degrees -- we figured out the receptacle was worn out, and was a loose connection. In a tighter receptacle, it didn't get hot.
 

Sumboodie

Well-known member
Joined
Mar 20, 2021
Messages
10,745
Location
AK
since we're talking space heaters, I had to put this in .
space heater & non aluminum receptacle without a copper pigtail
HPIM2779.JPGspace heater & non aluminum receptacle without a copper pigtail

The ONLY heat in the office at work is from the warehouse, which is ~55*, but need to leave the door open.

So have 2 plug in heaters.
Before when it was -60* outside, I had a case of water bottles on the floor and it froze solid.l and the spideyplants were dying from the cold.

Safety visited and said they can't remain plugged in at night.
Yeah, not coming in and freezing all morning.
 
To avoid these ads, REGISTER NOW!

Dagny

Well-known member
Joined
Jul 25, 2014
Messages
3,019
Location
Northern Wi.
I wish they would make a special recp. for these loads 10 to 15 dollars should do it. There are no recp. that won't eventually look like that with 1500 watts running on it.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,593
Location
Fullerton, CA
since we're talking space heaters, I had to put this in .
space heater & non aluminum receptacle without a copper pigtail
HPIM2779.JPGspace heater & non aluminum receptacle without a copper pigtail
Example.... A lot more is involved here than just time.
Notice the smoke is mostly generated from behind the coverplate, which would indicate heat generated from a loose connection on the sidewire connection (due to the incompatible outlet).
 
Last edited:

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,775
Location
NW Iowa
I've got a bunch of these Hubble P-1945 receptacles in my house. I think I saved them from a school where I was wiring.

These are over 50 years old but have extremely good plug tension. Better than a brand new commercial grade. I have no doubt they could handle a continuous 1500 watt load.

I'd hate to think what they cost back when they were new. I don't know if a 5262 would be roughly equivalent, those are like $13 each today.

KIMG3426.JPG
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,593
Location
Fullerton, CA
The secretaries in mentioned in post 56 had heaters on for 8 hours a day 5 days a week. I've never had to replace a recp.. They were just spec. grade commercial (These were big offices and multiple cubicles).
 
Last edited:

Quickstep192

Well-known member
Joined
Aug 16, 2025
Messages
90
A few years ago, when I was still working, there was a lot of interest in powering LED lighting using Power Over Ethernet. A Cat6e cable would be 23ga or 24ga wire. At 50v, I guess the would still be considered low voltage?
 