I agree but like any circuit without knowing the load the only signal you'll get is a tripped breaker
That's why nearly every home improvement store stocks 30 amp single pole breakers.........
I agree but like any circuit without knowing the load the only signal you'll get is a tripped breaker
There is no code requirement to label the receptacle, odd as it is…as long as you label the outlet "welder only".
They’re nearly universal in commercial work, though.Oldwizard was.
It's rare to see ONLY lighting circuits in houses around here, at least in normal sized houses with 125 amp service.
Yes, but I was talking about residential.They’re nearly universal in commercial work, though.
Reducing the wire size for lighting only circuits in a large office building can save a lot, simply because there's so much wire used. 16 AWG wire uses 40% the copper of 14 AWG wire, so the cost savings potential is quite large. in smallish quantities, 16 awg MTW costs 2/3 what 14 AWG MTW does. (I'm list MTW because it's very similar to THHN, which isn't available smaller than 14 awg. larger sizes of stranded thhn are often cross listed as thhn/thhw-2/mtw.) Saving a third on lighting wire when you're using hundreds of miles of the stuff is a big chunk of change.
Every place I've lived for the last 50 yrs, both large and small, had separate breakers for lighting circuits (Even apartments).Yes, but I was talking about residential.
Would need to be a large house or have unique lighting needs to need to have lights on their own circuits.
So each room had at minimum 2 breakers?Every place I've lived for the last 50 yrs, both large and small, had separate breakers for lighting circuits (Even apartments).
When I wired my current house I did similar.So each room had at minimum 2 breakers?
I've lived in 6 houses over the last ~25 years, none had that.
Every place I've lived for the last 50 yrs, both large and small, had separate breakers for lighting circuits (Even apartments).
Aside from going dark if the breaker trips, it's not like lights add much load to a room.Around here, outlets and lights are on the same circuit.
This fits well with the 'cheapest possible' mantra that prevalent in house wiring.
We are about a month away from me getting calls about bad breakers; the first question I ask is if they have a space heater. When the answer is yes, I tell them it will be much cheaper to throw the heater in the nearest dumpster vs me adding a circuit. I also tell them I would be more than happy to take their money, but once again, they can turn the furnace up a couple of degrees and be money ahead.The main reason I don't put bedroom lights and outlets on the same circuit is people tend to use 1500 watt space heaters a lot. 2 of them on the same circuit will trip a 15 or 20 amp breaker and if the lights are on it, it'll go dark.
I used to do commercial service calls. Every October we'd start getting from calls from offices of blown 20A breakers. Invariably the secretaries felt cold, although the temp was the same 24/7/365.We are about a month away from me getting calls about bad breakers; the first question I ask is if they have a space heater
Kitchen appliances can draw 1500 watts or more. They don't need special receptacles.There are no receptacles that won't eventually look like that with 1500 watts running on it.
Kitchen appliances can draw 1500 watts or more. They don't need special receptacles.
My crockpot does and what does a 15 or 20 circuit have to do with the outlet melting?But kitchens have 20 amp circuits and the appliances don't run continuously.
You show me a crockpot that uses 1500 watts!My crockpot does and what does a 15 or 20 circuit have to do with the outlet melting?
This says nothing about the duration of the load.I wish they would make a special recp. for these loads 10 to 15 dollars should do it. There are no recp. that won't eventually look like that with 1500 watts running on it.
Example.... A lot more is involved here than just time.

Our crockpots do 301W and the other is 275W.You show me a crockpot that uses 1500 watts!
More like 150 watts, probably less.
1450W for a "roaster"Look up 22 qt "crock pots"
Hence the quotes.1450W for a "roaster"
A crockpot that uses 1500w? wow that must be SOME crockpot? industrial? mine only uses a few hundred wattsMy crockpot does and what does a 15 or 20 circuit have to do with the outlet melting?
Big difference between a crockpot and a roaster. Even a roaster isn't continuous. They cycle off the thermostat.1450W for a "roaster"