Question for the legit Sparkies (I am not one).
A friend asked me a question about his duplex which is under construction in Florida (prior was destroyed during hurricane). He owns both units (lives in one, rents adjacent unit).
There is a SINGLE 400A service which serves both units; owner did not want to pay the separate meter few to have a meter on each unit. There is a shared laundry room, and the 200A main breaker panels for each unit are located there. The configuration is shown below in the graphic I made after talking with him this morning (hopefully its clear). I don't know if there are ground rods or a UFER.

Unit 1 (Owners residence) is fully backed up by an automatic generator to pick up all the loads in his residence. He would like to be able to run the mini-split and fridge in Unit 2 during loss of power events. The 200A main breaker panels are side by side with just a stud between them.
His electrician suggested installing a generator interlock with backfeed breaker at the Unit 2 panel (which is a sub panel), a piece of conduit with ******* between the panels, and a matching size breaker in the Unit 1 panel. I do not know the proposed breaker sizes nor the loads of the minisplit and the fridge.
As far as we know, the disconnect at Unit 2 only breaks L1 and L2 which we believe is same for the Generac ATS. The N-G bonds occur at the disconnect and in the ATS, with a common G at the meter can. Generator is 4-wire feed with separate N&G.
So - is his electrician's approach sound?
Thanks for your help.
A friend asked me a question about his duplex which is under construction in Florida (prior was destroyed during hurricane). He owns both units (lives in one, rents adjacent unit).
There is a SINGLE 400A service which serves both units; owner did not want to pay the separate meter few to have a meter on each unit. There is a shared laundry room, and the 200A main breaker panels for each unit are located there. The configuration is shown below in the graphic I made after talking with him this morning (hopefully its clear). I don't know if there are ground rods or a UFER.

Unit 1 (Owners residence) is fully backed up by an automatic generator to pick up all the loads in his residence. He would like to be able to run the mini-split and fridge in Unit 2 during loss of power events. The 200A main breaker panels are side by side with just a stud between them.
His electrician suggested installing a generator interlock with backfeed breaker at the Unit 2 panel (which is a sub panel), a piece of conduit with ******* between the panels, and a matching size breaker in the Unit 1 panel. I do not know the proposed breaker sizes nor the loads of the minisplit and the fridge.
As far as we know, the disconnect at Unit 2 only breaks L1 and L2 which we believe is same for the Generac ATS. The N-G bonds occur at the disconnect and in the ATS, with a common G at the meter can. Generator is 4-wire feed with separate N&G.
So - is his electrician's approach sound?
- On Loss of Offsite Power, the ATS takes care of Unit 1 and separates it from the grid (L1 and L2 only to my knowledge).
- Unit 2 is black on loss of offsite power. The disconnect is still enabled (pass thru). The owner would then rack off all of the breakers in Unit 2, flip the Unit 2 interlock taking it off the grid, enable the back feed breaker, then enable only its AC and fridge breakers.
- Although the N-G bonds occur in two separate devices (disconnect and the ATS), electrically the seem to be the same to my untrained mind via the common G at the meter can.
Thanks for your help.