My wife and I are doing all the electrical in our new garage and bedroom addition, aside from the new panel, and I have a question on the wall boxes I have for my 50amp outlets. I wanted some extra room for wiring up the 6-2 romex so I went with a plastic 2 gang box. After I got back home and started installing things I noticed The knockouts were too small for the wiring so I cut a hole in the side and installed a wire clamp. When the electrician I hired came to upgrade our service and install my new sub panel said he had never seen that done before and didn't know if the inspector would give me a hard time about it. I know I saw some 2 gang boxes at the store with plastic clamps already built in like this so I didn't think it would matter. Thoughts? I already have them installed and really don't want remove them unless I have to.


Thanks!
Rasky




 
To avoid these ads, REGISTER NOW!

jim111

Well-known member
Joined
Nov 18, 2015
Messages
93
Location
tx
The clamp is installed backwards if it matters to your inspector
 

Stuff

Well-known member
Joined
Aug 31, 2013
Messages
572
The inspector could say that the plastic box is not listed for this field modification.
 

Cmreschke

Well-known member
Joined
Feb 15, 2014
Messages
775
Location
North of Detroit
^^^this. For the the first 5 years of my residential career we drilled out 1/2" holes in plastic cut in boxes and used them for island and meninsula plugs. We installed ent fittings and surf tube for sleeving. It was always kosher until they decided that it was a violation of listing. As that plastic box wasn't designed for drilling a hole. I think it's **** personally. They told us if it was meant to have holes in it then the manufacturer would put some in it. I call hog wash. Some steel and some Carlon pvc boxes don't have any kos in them, are we not suppose to make our own in those?
 

bczygan

Well-known member
Joined
Nov 4, 2009
Messages
22,002
Location
DETROIT! Arsenal of Scrappers
Can you use these for surface mounting of 30 and 50A receptacles?

151901-ProductImageURL.jpg


Bill
 

Cmreschke

Well-known member
Joined
Feb 15, 2014
Messages
775
Location
North of Detroit
I don't have the size of the box in front of me but its 6s won't fit in that box with a 50 amp range plug I'd bet physically with the 6 inches of free conductor required, plus ground splice and all. If you say you put a 30 amp in with 10s hey I believe it. I've seen 10 gallons of **** in a 5 pound bucket too. Doesn't mean it was legal though. Ymmv. The receptacle shown above 8s designed for a 2 gang box or 4 square with raised cover.
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
I dont know how you couldnt fit the wire in with the clamps in box. You could cut the tab between the two and put it that way,but the wire usually will fit in the single spot
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
The inspector could say that the plastic box is not listed for this field modification.

And I would agree with the inspector. Use a 4X4 or 4 11/16 square box with a 2 gang ring mounted to a block
 

Cmreschke

Well-known member
Joined
Feb 15, 2014
Messages
775
Location
North of Detroit
And I would agree with the inspector. Use a 4X4 or 4 11/16 square box with a 2 gang ring mounted to a block

In a day and age where we are allowed to construct our own junction boxes, this is just silly not allowing a 1/2 or 3/4 inch hole to be made in a plastic box.
 

gregtwojeeps

Well-known member
Joined
Jul 30, 2013
Messages
5,096
Location
Ky
Get the 2 and 1/8 " deep box though with 1/2" plaster ring shown on bottom pic. Use 5/8 " ring even better . . Just be sure ring will be flush with finished wall surface. Be sure box is secured well. jmo


050169002322lg.jpg





050169007785lg.jpg
 
Last edited:

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,752
Location
SE Michigan
And I would agree with the inspector. Use a 4X4 or 4 11/16 square box with a 2 gang ring mounted to a block

^^^^ This. You want a metal box anyway in my opinion. This is a setup where you have to push and pull with decent force on the plug. If the plastic threads strip out you get to start over and do it again. The metal box forces you to put a more serious wood block behind it, not the cheap nails. Nothing irritates me more than spongy electrical boxes.

Home Depot around here seems to have a big advantage over Lowes in this department, they have a full lineup of Raco 4" dished covers. In other words, the receptacle mounts to the ring, the ring is screwed into the diagonal corners of the box. The ring is trim and structural, all at the same time.

Edit: check out Raco 810C.
 
Last edited:
To avoid these ads, REGISTER NOW!

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon

Attachments

  • 52171-WB.jpg
    52171-WB.jpg
    41.8 KB · Views: 54
  • 785991167801lg.jpg
    785991167801lg.jpg
    10.4 KB · Views: 52
  • 050169007785lg.jpg
    050169007785lg.jpg
    32.8 KB · Views: 45

TTA89

Well-known member
Joined
Feb 23, 2014
Messages
230
Location
New Hampshire
Great timing... I'm going to install my 6/2 50amp welder receptacles and I was going to use the plastic 2 gang boxes. You guys make a great point about pushing and pulling on the plugs. I'm going to try the deep metal boxes, I have 2x6s so it shouldn't be a problem. My biggest problem is finding the right parts at Home Depot... Most of the time I have a picture with no name. "Do you know where I can find this?" ha ha.
 
OP
R

RaskyR1

Well-known member
Joined
Oct 11, 2010
Messages
57
Location
Minnesota, USA
Thanks for all the reply's guys. It seems like it really depends on the inspector so I'm just going to email him the pics to see if he has issues with it before I go ahead and replace it, since it's already installed. My wife has talked to him a few times now and he's been very helpful. I chose plastic boxes simply because I will be washing cars inside often and it just seemed to make more sense, no other reason.

It is a 50amp (6-50R) that is going there but I also have (2) 30 amp outlets going in as well and just held it up for a picture reference. It will be used for EV charging as I work on new Tesla's occasionally and the owners appreciate a full charge when they pick up their cars.





I dont know how you couldnt fit the wire in with the clamps in box. You could cut the tab between the two and put it that way,but the wire usually will fit in the single spot

That was an option too but as noted above that would technically be modifying the plastic box, no? The metal clamp idea was a suggestion from a friend who used to be an electrician after I mentioned seeing these Carlon boxes, which are essentially doing the same thing.

a041396b-0921-410b-aa93-31af6973f019_1000.jpg
 

sands35

Well-known member
Joined
May 29, 2012
Messages
936
Location
St. Joseph, MI
Last edited:
OP
R

RaskyR1

Well-known member
Joined
Oct 11, 2010
Messages
57
Location
Minnesota, USA
But they have been listed for the application.

True :)

You could use these:

http://www.garvinindustries.com/electrical-junction-boxes/6-square-junction-boxes/1-1-2-to-3-deep

Nice and big.

Assuming 30 amps, that would be #10 wire. A box fill calculator says min 15 square inches (if I did it right....), which would be anything, but a 4-11 box would be better given the slightly larger volume over a 4 square.

http://www.constructionmonkey.com/calculations/electrical/boxfill

I actually ran 8-2 romex to the 30amp boxes in case I wanted/needed to change them to 40amp later.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,913
Location
Richmond, VA
Unless fixing it will cause a big disruption, I personally would not reach out and ask. Seems like you are welcoming the failure that might not have been issued otherwise. That said, i would use a metal box too.
 
OP
R

RaskyR1

Well-known member
Joined
Oct 11, 2010
Messages
57
Location
Minnesota, USA
Unless fixing it will cause a big disruption, I personally would not reach out and ask. Seems like you are welcoming the failure that might not have been issued otherwise. That said, i would use a metal box too.

Thanks! It will be a few weeks before the inspection and I still need to run wire for all the overhead lights so I may just take your (and the others above) advice and swap them out for metal boxes.
 

rexer

Well-known member
Joined
Sep 4, 2012
Messages
195
Location
Earth
I mounted my 50 amp receptacle box for my welder just below the panel box with 8/2 wire and a plastic blue box.

Didn't want too start cutting all the sheet rock..

I guess its ok, nice and tight when I put the plug in and take it out..
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,049
Location
Coronado, CA
If you do decide to stay with the plastic box and it breaks, be prepared for a thousand "We told you to switch to a metal box" messages.
 

TTA89

Well-known member
Joined
Feb 23, 2014
Messages
230
Location
New Hampshire
Noobie question here... If you use one of the 4 inch metal boxes, how do you ground it with 6/2 wire coming in?
 

TTA89

Well-known member
Joined
Feb 23, 2014
Messages
230
Location
New Hampshire
6/2 means 2 insulated wires and 1 uninsulated ground in a bundle.

Right... So I figure you build a ground tail off the box with whatever, 12 or 14 gauge and then how do you connect it to the 6 gauge wire that is going to the receptacle? In a 12 or 14 gauge scenario I would wire nut the feed wire ground, the box ground tail and a tail from the receptacle right? But in this case the wire is too thick with 6 gauge so whats do you do?

Maybe I'm overthinking this... :headscrat
 

Jsf721

Well-known member
Joined
Dec 23, 2012
Messages
4,129
Location
LI, NY
Rasky. It's jsfm35x. Hit the inspector with a old rupes and get a mark II. Lol
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
The grounding conductor in 6/2, and 6/3 NM is 10 AWG, run a little extra cable into the metal box and wrap the 10 gauge bare conductor around a ground screw, no need for splices & a quick and easy way to bond the box. 12 AWG is not acceptable for a grounding pigtail above 20 amperes.
 
OP
R

RaskyR1

Well-known member
Joined
Oct 11, 2010
Messages
57
Location
Minnesota, USA
How did you cut the hole in the side of the box?

hole saw bit and then a dremel tool to smooth it out. :)

Rasky. It's jsfm35x. Hit the inspector with a old rupes and get a mark II. Lol

LOL! Small world! How's it going man? :)

The grounding conductor in 6/2, and 6/3 NM is 10 AWG, run a little extra cable into the metal box and wrap the 10 gauge bare conductor around a ground screw, no need for splices & a quick and easy way to bond the box. 12 AWG is not acceptable for a grounding pigtail above 20 amperes.

Thanks for the tip!
 