Questions about adding 220v circuits

To avoid these ads, REGISTER NOW!
OP
V

VoodooCLD

Well-known member
Joined
Sep 12, 2014
Messages
412
It must meet code cause it was signed off multiple times a year ago when the building was complete. The new unit will be going farther down the wall which is towards the garage door.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,020
Location
Modesto, CA
Doesnt mean it met code. Inspectors miss stuff all the time.

Also since youre changing it, you would need to add an outlet.

Unfortunately, your #10 feeder doesnt have a neutral so you will need to run a new feeder or a separate feed for the outlet
 
Last edited:
To avoid these ads, REGISTER NOW!

acer66

Well-known member
Joined
Dec 4, 2010
Messages
4,418
Location
Western North Carolina
I would just replace your existing disconnect with one that has also receptacle or maybe you can upgrade yours if you can run some extra wires in the conduit.

It is convenient to have a receptacle anyway imho.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
I would just replace your existing disconnect with one that has also receptacle or maybe you can upgrade yours if you can run some extra wires in the conduit.

It is convenient to have a receptacle anyway imho.
It is only a 10/2 coming from the sub panel in the shop, so no neutral. You can not get 120 volts from this power source.
 

acer66

Well-known member
Joined
Dec 4, 2010
Messages
4,418
Location
Western North Carolina
It is only a 10/2 coming from the sub panel in the shop, so no neutral. You can not get 120 volts from this power source.
Yes, you are right I was hoping that that conduit might run in a way that he can get the needed wires in the box but I have to admit I am not up to date with every post here.
 