Hey guys how would you recommend I install my Quincy 230v air compressor model qt-54.
What size breaker/wiring etc?
Thanks for your help
What size breaker/wiring etc?
Thanks for your help
Per the specs you should use a 50 Amp breaker. The distance from your electrical panel to the compressor will determine the size of the wire needed.
Sent from my iPhone using Tapatalk
You dont need 8/3 since u dont need the neutral. 8/2 would suffice. And u could try a 30a breaker and see if it holds. Otherwise 40a should be fine.
OP, hope you don't mind if I hijack this thread for a moment. I also just bought a Quincy QT-54 and I have a question about wiring it. I bought it used and the previous owner didn't have any starter or capacitor wired to it. The motor was simply connected to the pressure switch, and the pressure switch was connected to the line power. Is that correct, or should I get a starter?
Also, I read that the motor needs some kind of overload protector, since in this case the breaker mostly protects ground faults (which is why it can be oversized for the wire). My motor has a thermal overload reset button on it. Is that the same thing? Do I need any additional protective devices?
I snapped this picture this morning. It looks like it's rated for 26 FLA. I'm guessing this close enough to the 28 FLA the motor is rated at?
I snapped this picture this morning. It looks like it's rated for 26 FLA. I'm guessing this close enough to the 28 FLA the motor is rated at?
I would suggest a starter. Once those contacts begin to arc and carbon up, they will act like a resistor and will cause the start up winding in the motor to draw more current and burn out the start up windings. Ask me how I know....
I would suggest a starter. Once those contacts begin to arc and carbon up, they will act like a resistor and will cause the start up winding in the motor to draw more current and burn out the start up windings. Ask me how I know....

Ok one more question: Since the motor is 21 FLA, do I use that number to determine wire size (21 x 1.25) or do I still use the 28 FLA from the NEC? I'm going to use Romex for part of the run where it's inside a wall, and conduit where it's exposed in the garage. Total distance roughly 50 ft.
Originally I was going to use 8/2 since 28 x 1.25 = 35 amps. Now I'm thinking I can use 10/2. And even if I do use 8/2, apparently 10 gauge THHN is fine in conduit, so would I splice the 8/2 Romex to 10 gauge THHN?
Thought of another question: does the ground wire also need to be #10, or can I get away with using a smaller wire?
Per the specs you should use a 50 Amp breaker. The distance from your electrical panel to the compressor will determine the size of the wire needed.