Finally after years of planning and talking about it. Ive finally finished my solar collector.

19x12. Im estimating 35000btu/hr of heat gained.
 

Attachments

  • 20191204_155908.jpg
    20191204_155908.jpg
    116.9 KB · Views: 406
  • 20191204_094745.jpg
    20191204_094745.jpg
    101.1 KB · Views: 372
  • 20191204_094704.jpg
    20191204_094704.jpg
    154.2 KB · Views: 379
To avoid these ads, REGISTER NOW!

xjfish

Well-known member
Joined
Feb 22, 2014
Messages
1,290
Install looks very nice. Hope it works out well! Do report back with your results.
 
OP
2

2011laramie

Well-known member
Joined
Apr 2, 2012
Messages
161
Location
Central Alberta
Seems to be working.

I need to buy a flow meter or else do some math against the pump curve to try and determine the flow to get some actual math numbers down.
 

Attachments

  • IMG_0516.jpg
    IMG_0516.jpg
    86 KB · Views: 266
  • IMG_0514.jpg
    IMG_0514.jpg
    91.7 KB · Views: 230

Denwood

Well-known member
Joined
Sep 22, 2014
Messages
4,183
Location
Thunder Bay, Ontario, Canada
Awesome project. I did a pile of research/measurements/analysis on my solar pool project, including a live data feed of BTU output. Very interested in your measurements.
https://www.garagejournal.com/forum/showthread.php?t=397005&page=3

Max output on the 12x20' array was 90 000 BTU/hour on a hot day (calculated on actual measured flow of 1548GPH and delta temps via DS18B20 digital probes)...so your estimate of 350 000 K per hour is likely high from a glazed 12x19 in winter sun.

What temps are we seeing on the digital gauge?

Was your shop cold to start? Looks like 40F supply and 90F back? What were outside temps during this time? My guess is that you'll get much better efficiency by ramping flow a lot higher. Your delta between outside temps and return water is quite high...so you're losing a fair bit to heat radiated to ambient outside.
 
Last edited:
OP
2

2011laramie

Well-known member
Joined
Apr 2, 2012
Messages
161
Location
Central Alberta
I got the temp gauges going in and out of the floor, which is a direct feed to the inlet and outlet of the collector. Ya the shop was dead cold for this start up, its been around -10C around alberta lately.

The digital gauge is reading air temp inside the collector box. Pump is plugged into the cooling mode of the digital controller, so when the box gets hot, it turns the pump on to cool the box by bringing in cold glycol.
 
OP
2

2011laramie

Well-known member
Joined
Apr 2, 2012
Messages
161
Location
Central Alberta
Ive been racking my brain how to figure out flow for this pump. I was looking at getting a variable area flow gauge and soldering it in on the vertical riser on the return from the floor. But then i thought, theoretically cant i just take pressure readings off the suction and discharge of the circulator, take that differential psi and multiple that by 2.3 to get feet of head resistance. Than plot that against the pump curve chart?

BTU/hr = GPM x delta T x 500.4

Right now, the pump is on setting one. Im away from the shop for a while cause i left for work. When i get back ill change the pump settings and try different flows.
 

Attachments

  • Screenshot_20191205-153102_Drive.jpg
    Screenshot_20191205-153102_Drive.jpg
    69 KB · Views: 99
  • Screenshot_20191206-002949_Gallery.jpg
    Screenshot_20191206-002949_Gallery.jpg
    53.2 KB · Views: 112
Last edited:

Denwood

Well-known member
Joined
Sep 22, 2014
Messages
4,183
Location
Thunder Bay, Ontario, Canada
You could figure flow, but if you can adjust it, just increase (a lot) to drop your delta. The larger the difference between panel internal temp and outside ambient, the less efficient your system becomes. So if you increase flow so delta between supply and return is just 10C, you’ll likely find that the actual BTUs pulled from your array increases.
 
OP
2

2011laramie

Well-known member
Joined
Apr 2, 2012
Messages
161
Location
Central Alberta
Did a quick pump pressure survey today, on a sunny day on pump setting 1 its around 65000 btu/hr.

I did todays pressure survey with no sun so the glycol was actually at minus 10°C, which would have more pumping resistance than warm glycol. So theoretically with hot glycol it might actually be recovering more btu.

Hoping tomorrow is more sunny so i can run some more numbers

Also, with to collector at 65°C and it -6°C outside, its losing roughly 18000 btu/hr through the glazing. Im hoping i can run it on setting 2.
 
Last edited:

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,675
Location
Maine
Nice, I have something similar in my shop. I built my collector into my south wall using ideas from www.builditsolar.com . My signature has a link to my build, keeps my shop around 50 generally. Its tough right now as there is less than 9 hours daylight in Maine right now. Go a few days without sun and the temp drops. Lowest I've seen it is 39. I'm not getting the delta T you are. My thermometers on radiant manifold are screwed up so I can't really tell. I just guessed on my pump, 009 Taco stainless, it was cheap off Ebay :thumbup:
I will say once its been running its been pain free. Done nothing to it since its start up except change out differential controller.

I use woodstove to get temps up if I'm out there for any length of time.
 
OP
2

2011laramie

Well-known member
Joined
Apr 2, 2012
Messages
161
Location
Central Alberta
A few pics from construction of the panel. Theres five banks of risers with flat black painted aluminum plates that i bent in the ole all manual hammer press lol(it was all 6" wide rolled flashing that i cut into 4ft sections and then hammered the groove into for a tight fit against the risers. Its got 1.5" polyiso insulation behind the aluminum flashing that the painted risers are attached too. Inside ive got 1" supply and return manifolds and piping over to the distribution header into the floor. The floor has 1500 feet of oxy barrier pex on 12.5" centers (cheated the distances to get 1500 ft of pex to fit in a 1700sq ft bay.

This solar heated bay was going to be cold storage side of the shop, so if it has temp swings thats ok. Ill have a boiler system on the other side and ill pipe glycol over for a hydronic fan coil unit that i can turn on so if i wanna work on the solar heated bay i can heat it as i want too
 

Attachments

  • 20170815_170742.jpg
    20170815_170742.jpg
    149.6 KB · Views: 154
  • 20181119_164546.jpg
    20181119_164546.jpg
    150.7 KB · Views: 159
  • 20190804_175101.jpg
    20190804_175101.jpg
    122.3 KB · Views: 155
  • 20190824_213808.jpg
    20190824_213808.jpg
    148.6 KB · Views: 167
  • 20190825_173905.jpg
    20190825_173905.jpg
    148.5 KB · Views: 156
  • 20190824_213752.jpg
    20190824_213752.jpg
    116.7 KB · Views: 167
  • 20190826_114559.jpg
    20190826_114559.jpg
    153.6 KB · Views: 173
OP
2

2011laramie

Well-known member
Joined
Apr 2, 2012
Messages
161
Location
Central Alberta
Ya walrus, your shop is where i got the initial idea from. I asked you a few questions on your thread.

Right now the attic insulation isnt complete so every night the slab cools right down. Im planning on finishing the attic insulation this week.
 

HoosierBuddy

Well-known member
Joined
May 9, 2006
Messages
2,918
Location
Southern Indiana
Very cool project.

On calculating flow...dumb idea, but instead could you just measure flow?

Thinking you might have a drain somewhere that you could put a gallon jug under and use a stop watch to measure how many seconds it takes to fill?

Not sure if that's possible or not...

Again...super job!

Phil
 

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,675
Location
Maine
Ya walrus, your shop is where i got the initial idea from. I asked you a few questions on your thread.

Right now the attic insulation isnt complete so every night the slab cools right down. Im planning on finishing the attic insulation this week.

Be interesting to hear how it works once insulation is finished up. I've been watching a timber frame "barn" , really a home, being built. They are running a propane heated floor while doing the insulation on top of the roof. 9 inches of sheet foam over tongue and groove 2 bys. They say every time they get another section done the temps go up in building .
 
OP
2

2011laramie

Well-known member
Joined
Apr 2, 2012
Messages
161
Location
Central Alberta
We finished the roof tuesday afternoon. 235 bags of cellulose blown up there. But of course, get that done and i had to leave again for work. I might order a temperature logger online and set it up to take readings every 30 minutes or something.
 
To avoid these ads, REGISTER NOW!
OP
2

2011laramie

Well-known member
Joined
Apr 2, 2012
Messages
161
Location
Central Alberta
Seems to be working good, lots of air bubbles floating around.( system doesnt have an air separator installed yet) the other day it kicked on at 930 am. And ran till probably 430.
 

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,675
Location
Maine
Seems to be working good, lots of air bubbles floating around.( system doesnt have an air separator installed yet) the other day it kicked on at 930 am. And ran till probably 430.

Do you have expansion tank? You really need the air scoop. The length of time running sounds about right except I'm dark at 4.30 :shocking:
 

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,406
Location
N CA
I am of the opinion that tapping into solar energy is still in it's infancy.

I would agree with you, but unless it is a diy built collector bank as discussed here the economics of solar thermal just aren't there. the best return for the solar dollar today is PV.
 
OP
2

2011laramie

Well-known member
Joined
Apr 2, 2012
Messages
161
Location
Central Alberta
Well its -22C outside, i checked the shop first thing in the morning and it was -6 inside.

Sun has kinda been trying to make an appearance most of the day. I went out and it was 18 in the collector then it warmed up more and started the pump (starts at 25C).

These pics were within minutes of the pump starting.
 

Attachments

  • 20200111_135832.jpg
    20200111_135832.jpg
    108.2 KB · Views: 79
  • 20200111_135653.jpg
    20200111_135653.jpg
    73.7 KB · Views: 83
  • 20200111_135940.jpg
    20200111_135940.jpg
    87.5 KB · Views: 57
OP
2

2011laramie

Well-known member
Joined
Apr 2, 2012
Messages
161
Location
Central Alberta
More of the light cloud cover, so no direct sun, but the collector did fire up at around 11am today.

Shop was -8C this morning.
 

Attachments

  • Screenshot_20200112-112101_Gallery.jpg
    Screenshot_20200112-112101_Gallery.jpg
    52 KB · Views: 41
Last edited:
OP
2

2011laramie

Well-known member
Joined
Apr 2, 2012
Messages
161
Location
Central Alberta
Beautiful sunny morning here today. But extremely cold.

Went out at 9:45am to see how its doing and suprised it was running already. Sun is still on quite an angle from the east and the lean to is casting a shadow still.

Shop was -10C inside, not bad givin the temps overnight and no other heat source.
 

Attachments

  • 20200115_094536.jpg
    20200115_094536.jpg
    147.5 KB · Views: 57
  • 20200115_094750.jpg
    20200115_094750.jpg
    63.2 KB · Views: 54
  • 20200115_094703.jpg
    20200115_094703.jpg
    92.8 KB · Views: 55
  • Screenshot_20200115-100652_Gallery.jpg
    Screenshot_20200115-100652_Gallery.jpg
    57.8 KB · Views: 50
  • 20200115_094435.jpg
    20200115_094435.jpg
    100.9 KB · Views: 41
  • 20200115_094437.jpg
    20200115_094437.jpg
    82.5 KB · Views: 42
  • 20200115_094440.jpg
    20200115_094440.jpg
    136.9 KB · Views: 51
Last edited:

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,675
Location
Maine
My shop was 50 today, we had some sun yesterday so that helped and I had woodstove going last weekend. Temps have been warm for January, 32 today.
 

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,675
Location
Maine
Cold and no sun, shop was down to 44 yesterday. Probably hit 30s if I don't work out there but today I'll have wood stove going while I make a bracket for my solar charger
 
OP
2

2011laramie

Well-known member
Joined
Apr 2, 2012
Messages
161
Location
Central Alberta
10:45am sun,
Pump on highest setting
60F going into floor, 42F return temp.
4.2gpm on the new flow gauge.
Air separator installed and moved expansion tank to tie into air separator.

Without calculating the variables for the 50/50 glycol and using just water numbers.

4.2gpm x (60-42) x 500.4 = 37800BTU/hr. Not as good as i originally thought, but back to where i expected it. Flow gauge was a nice touch.

12:30, the most direct sun without a single trace of a cloud. = 45000btu/hr.

The glycols warmed up a bit, so its easier to pump
 

Attachments

  • 20200125_105557.jpg
    20200125_105557.jpg
    85.1 KB · Views: 44
  • 20200125_105357.jpg
    20200125_105357.jpg
    87.9 KB · Views: 54
Last edited:

Denwood

Well-known member
Joined
Sep 22, 2014
Messages
4,183
Location
Thunder Bay, Ontario, Canada
45K BTU sounds pretty good given the cold temps..and a lot more inline with what I was predicting for your array. I'd measured a max of 90K BTU in an hour (during a hot summer day) from our solar pool array @12'x20'...and that was mounted to a hot asphalt roof.

It would be worth trying to up that flow x2 and repeat your measurements. I suspect you could raise efficiency a lot as 60F in means you're loosing a lot to ambient still. You can add a pump in series to double(ish) your flow.

You really need to know your slab temp to find that sweet spot with respect to flow/efficiency.

Btw, I don't think you've posted your array construction details. Would be great to see what you did there. Thanks again for posting real data :)
 
Last edited:

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,675
Location
Maine
You are getting much bigger Delta Ts on your collector than I am. Not sure why? I'm only getting 3 or 4 degrees. The February sun is helping to get the temps in collector up and temps in shop are warmer .
 
OP
2

2011laramie

Well-known member
Joined
Apr 2, 2012
Messages
161
Location
Central Alberta
Im not sure Walrus,

My temp probe is measuring air temp and is fastened to one of the black absorbers, so that might be skewing the number a bit.

What are you temps in and out of your collector?
 

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,675
Location
Maine
Im not sure Walrus,

My temp probe is measuring air temp and is fastened to one of the black absorbers, so that might be skewing the number a bit.

What are you temps in and out of your collector?

My temps out of collector are a few degrees warmer than the floor. Collector temps can go over a hundred but outlet temps are still a few degrees over the floor temps. Might be able to get that delta T higher with better collectors or by slowing down flow so fluid stays in collector longer? I haven't messed with it as my shop is in the 50s and if not a few sticks of wood gets it in the 60s.

You should be seeing some big collector temps now
 

Denwood

Well-known member
Joined
Sep 22, 2014
Messages
4,183
Location
Thunder Bay, Ontario, Canada
That high delta is a strong indicator that flow needs to go up a lot. Do that and efficacy will also increase with less loss from the array to ambient outside temps. You really need to measure the fluid temp at array exit, )not the air temp in the collector) to dial in flow for max efficiency.

Walrus. 3-4 degrees sounds about right. A high delta means a lot of efficiency loss, particularly if ambient temps are low. Your array is always radiating heat back to ambient. Keeping that delta as low as possible will dramatically change the system efficiency. This is just about maximizing BTUs to your slab and does not apply to a non-stratified domestic water system where a higher delta would be the goal.

If you have a Zwave hub in your home, you can monitor the fluid temps:
1: Use a thermowell in-line to your plumbing.
2. Pick up a few DS18B20 sensors ($10 each)
3. Use the Fibaro Universal sensor to connect up to four sensors.

I take this data and combine with flow measurements to graph real time BTU performance of our solar array. If interested I can post a few links on the project. Hundredgraphs.com plugs into this data for free: https://community.smartthings.com/t/smartthings-swimming-pool-solar-heat-automation-diy/131994/5

This is the live graph of my system. It’s a bit misleading at this moment as it’s winter here so the roof temp and a few other sensors are offline.

https://www.hundredgraphs.com/public/denwood

Sensors 1, 3 and 5 are live and correct as the Zwave/Ds18b20 sensors are solar powered and power themselves all year. One is measuring ground temps, the other two are in the drained pool plumbing :)

In any case, the sensors and graphs really helped sort out system efficiency so my flow target ended up around 1500 GPH. I also observed that max gain due to the array and roof configuration was actually 2-3pm every day at a high of about 98 000 BTU/hour.
 
Last edited:

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,675
Location
Maine
That high delta is a strong indicator that flow needs to go up a lot. Do that and efficacy will also increase with less loss from the array to ambient outside temps. You really need to measure the fluid temp at array exit, )not the air temp in the collector) to dial in flow for max efficiency.

Walrus. 3-4 degrees sounds about right. A high delta means a lot of efficiency loss, particularly if ambient temps are low. Your array is always radiating heat back to ambient. Keeping that delta as low as possible will dramatically change the system efficiency. This is just about maximizing BTUs to your slab and does not apply to a non-stratified domestic water system where a higher delta would be the goal.

If you have a Zwave hub in your home, you can monitor the fluid temps:
1: Use a thermowell in-line to your plumbing.
2. Pick up a few DS18B20 sensors ($10 each)
3. Use the Fibaro Universal sensor to connect up to four sensors.

I take this data and combine with flow measurements to graph real time BTU performance of our solar array. If interested I can post a few links on the project. Hundredgraphs.com plugs into this data for free: https://community.smartthings.com/t/smartthings-swimming-pool-solar-heat-automation-diy/131994/5

This is the live graph of my system. It’s a bit misleading at this moment as it’s winter here so the roof temp and a few other sensors are offline.

https://www.hundredgraphs.com/public/denwood

Sensors 1, 3 and 5 are live and correct as the Zwave/Ds18b20 sensors are solar powered and power themselves all year. One is measuring ground temps, the other two are in the drained pool plumbing :)

In any case, the sensors and graphs really helped sort out system efficiency so my flow target ended up around 1500 GPH. I also observed that max gain due to the array and roof configuration was actually 2-3pm every day at a high of about 98 000 BTU/hour.
Cool, got any pics of your panels or other parts of your system.?
 

Denwood

Well-known member
Joined
Sep 22, 2014
Messages
4,183
Location
Thunder Bay, Ontario, Canada
Keep in mind that my system is for solar pool heating so some of the system variables are different. It's not glazed (unglazed is more efficient for pool solar, but definitely not for space heating) and it's mounted to a black asphalt roof. Attic radiant heat almost certainly is a factor so some BTUs are being harvested from the attic itself and not just sun.

My solar heating thread is here: https://www.garagejournal.com/forum/showthread.php?t=397005&page=1

I added to the system by page 3..and this year am installing yet another 80 square feet of collector.

Having a defined body of water makes BTU calcs a bit simpler. Max gain in a day based on measured flow and temp delta given the known volume of water was about 470 000 BTU. Max BTU/hour I observed was about 90 000, with outside ambient temps in the 85F range.

The principles though of matching flow to a low delta and pumping max BTUs into a heat sink is the same though. With a slab and inside space you really need to know three things:

1. The slab temp (so your're never actually cooling your slab!!)
2. Fluid array Input temp (likely very close to slab temp)
3. Fluid array Output temp (should never be less than your slab temp)

Pumps like the Taco solar series below put it all in one package:
https://www.tacocomfort.com/product..._speed_solar_control_00_circulator/index.html

These change the flow automatically based on delta temps..so are likely the best choice for in floor solar radiant where you aren't using a stratified storage tank. You just need to monitor the 3 factors above to make sure you are never inadvertently cooling your slab! Those cheap temp sensors (DS18B20 ) are perfect for this application if you're rolling your own control system.
 
Last edited:
OP
2

2011laramie

Well-known member
Joined
Apr 2, 2012
Messages
161
Location
Central Alberta
Still havnt got the shops boiler system fired up. Soon though.

The only source of heat is the solar system currently.

I bought a temperature logger for the recent cold snap we had.
The outside temp is temp 1
The inside temp is temp 2

The coldest the inside of the shop got was -9°C, the low range for the outdoor sensor was set at -35°C and you can see it hit that for a few nights. You can see the little spikes on the inside temp was days when the solar collector fired up.
 