Rebel Pioneer Mini Split Install

To avoid these ads, REGISTER NOW!
OP
J

jonathan75

Well-known member
Joined
Mar 27, 2013
Messages
1,451
Location
NC

"2nd Standing Test

Open the core tools and allow the system to continue the evacuation process until the vacuum level is 500 microns or less. Then repeat the "standing test" to determine of there is a decrease in leak rate after the stabilization of the vacuum. If there is no leak, the 2nd leak rate in the system the leak rate should be considerably less than the first indicating progress in the job of dehydration."

I will have to calculate my own leak rate since my gauge does not have that feature. But after mine stabilized my leak rate was very little. It does not say in the link you provided that it has to stay under 500 during the standing test. It just says to check for decrease in leak rate after it stabilized.
 
OP
J

jonathan75

Well-known member
Joined
Mar 27, 2013
Messages
1,451
Location
NC
Finish or last should stay below.
Maybe I misinterpreted you description.

I only ran it for around 10 mins max. Probably was not enough to get the moisture out of the lines and gauge. After sitting all night I will run it again for longer and see what happens. Right now it is at 1060 and it has been a few hours. So probably the gauge is reading moisture and not a leak.
 

sevenzeronova

Well-known member
Joined
Mar 23, 2014
Messages
53
New charging hoses out gas when new. Probably your rise.
Really should use vacuum rated hoses. They are usually black and micron rated.
 
OP
J

jonathan75

Well-known member
Joined
Mar 27, 2013
Messages
1,451
Location
NC
New charging hoses out gas when new. Probably your rise.
Really should use vacuum rated hoses. They are usually black and micron rated.

I think I am going to have to make due with what I have and draw a line. There seems to be a never ending list of tool upgrades I can do. I can probably spend more for tools then I have for the Mini Split.
 

smokey0810

Well-known member
Joined
Mar 29, 2013
Messages
3,056
Location
Canyon, Texas
I left a foot of room between the wall and the back of the condensor. All other sides are open and accessible. U sure purchased a ton of equipment for this job....
 
OP
J

jonathan75

Well-known member
Joined
Mar 27, 2013
Messages
1,451
Location
NC
I got the outdoor unit on the ground today. It is not very level beside my garage so I had to flatten the ground out and put down some rock for drainage. It turned out deeper then I wanted but it does not get very much rain there most of the time. I plan to use some metal edging on the back side to divert the water around the pad. Also I will put some weed fabric down behind and around the unit with some mulch on top so no trimmers will need to get close.
 

Attachments

  • IMG_4161-1.jpg
    IMG_4161-1.jpg
    63.6 KB · Views: 207
  • IMG_4175-1.jpg
    IMG_4175-1.jpg
    136.2 KB · Views: 284
  • IMG_4173-1.jpg
    IMG_4173-1.jpg
    149.5 KB · Views: 249
  • IMG_4170-1.jpg
    IMG_4170-1.jpg
    155.1 KB · Views: 248
  • IMG_4169-1.jpg
    IMG_4169-1.jpg
    154.9 KB · Views: 203
  • IMG_4165-1.jpg
    IMG_4165-1.jpg
    156.4 KB · Views: 203
  • IMG_4162-1.jpg
    IMG_4162-1.jpg
    159.1 KB · Views: 207

smokey0810

Well-known member
Joined
Mar 29, 2013
Messages
3,056
Location
Canyon, Texas
Not trying to be capt buzzkill here, but u sure u have enough room between the wall and the back of your condenser? Looks REAL good otherwise. Nice install.
 
OP
J

jonathan75

Well-known member
Joined
Mar 27, 2013
Messages
1,451
Location
NC
Not trying to be capt buzzkill here, but u sure u have enough room between the wall and the back of your condenser? Looks REAL good otherwise. Nice install.

The base is more then 12 inches. The unit is a little further away then that because of where it sits on the base.
 
OP
J

jonathan75

Well-known member
Joined
Mar 27, 2013
Messages
1,451
Location
NC
Today I did the electrical work. Nothing exciting or challenging to report. Here are some pictures to help others. Tomorrow will be cutting and flaring.

I spaced the hole for the electrical wire just right so the screws to hold the box would hit the stud.
 

Attachments

  • IMG_4188-1.jpg
    IMG_4188-1.jpg
    35.9 KB · Views: 316
  • IMG_4186-1.jpg
    IMG_4186-1.jpg
    43.1 KB · Views: 295
  • IMG_4182-1.jpg
    IMG_4182-1.jpg
    98.8 KB · Views: 244
  • IMG_4180-1.jpg
    IMG_4180-1.jpg
    93.7 KB · Views: 232
  • IMG_4179-1.jpg
    IMG_4179-1.jpg
    71.8 KB · Views: 229
  • IMG_4178-1.jpg
    IMG_4178-1.jpg
    56.1 KB · Views: 213
  • IMG_4177-1.jpg
    IMG_4177-1.jpg
    56.3 KB · Views: 223
Last edited:
OP
J

jonathan75

Well-known member
Joined
Mar 27, 2013
Messages
1,451
Location
NC
More electrical work pictures....
 

Attachments

  • IMG_4203-1.jpg
    IMG_4203-1.jpg
    75.1 KB · Views: 275
  • IMG_4200-1.jpg
    IMG_4200-1.jpg
    90.4 KB · Views: 255
  • IMG_4196-1.jpg
    IMG_4196-1.jpg
    76.9 KB · Views: 270
  • IMG_4195-1.jpg
    IMG_4195-1.jpg
    124.6 KB · Views: 270
  • IMG_4192-1.jpg
    IMG_4192-1.jpg
    107.4 KB · Views: 248
  • IMG_4191-1.jpg
    IMG_4191-1.jpg
    115.6 KB · Views: 249
  • IMG_4190-1.jpg
    IMG_4190-1.jpg
    40.3 KB · Views: 314
OP
J

jonathan75

Well-known member
Joined
Mar 27, 2013
Messages
1,451
Location
NC
:needpics:
 

Attachments

  • IMG_4216-1.jpg
    IMG_4216-1.jpg
    67.6 KB · Views: 203
  • IMG_4215-1.jpg
    IMG_4215-1.jpg
    90.2 KB · Views: 179
  • IMG_4213-1.jpg
    IMG_4213-1.jpg
    81.9 KB · Views: 201
  • IMG_4208-1.jpg
    IMG_4208-1.jpg
    89.3 KB · Views: 177
  • IMG_4207-1.jpg
    IMG_4207-1.jpg
    107.7 KB · Views: 193
  • IMG_4206-1.jpg
    IMG_4206-1.jpg
    103.2 KB · Views: 203
  • IMG_4204-1.jpg
    IMG_4204-1.jpg
    89.3 KB · Views: 188
OP
J

jonathan75

Well-known member
Joined
Mar 27, 2013
Messages
1,451
Location
NC
More electrical pr0n. "I say whip it, Whip it good!"
 

Attachments

  • IMG_4229-1.jpg
    IMG_4229-1.jpg
    57.4 KB · Views: 259
  • IMG_4228-1.jpg
    IMG_4228-1.jpg
    61.5 KB · Views: 237
  • IMG_4226-1.jpg
    IMG_4226-1.jpg
    65.3 KB · Views: 258
  • IMG_4224-1.jpg
    IMG_4224-1.jpg
    68 KB · Views: 229
  • IMG_4223-1.jpg
    IMG_4223-1.jpg
    60 KB · Views: 205
  • IMG_4222-1.jpg
    IMG_4222-1.jpg
    100.7 KB · Views: 229
  • IMG_4218-1.jpg
    IMG_4218-1.jpg
    149.7 KB · Views: 239
Last edited:
OP
J

jonathan75

Well-known member
Joined
Mar 27, 2013
Messages
1,451
Location
NC
The good news is I got it running today, the bad news is that the squirrel cage fan is not balanced because of some missing blades. When I turned it on some blades fell out and it was rattling. The imbalance is causing the whole unit to vibrate and shake really bad. I really hope Parker Davis can send me a new squirrel cage that I can replace easily without messing with the refrigerant. The coils seem in the way so I really hope it can be done. Such a shame too because I really took my time to make sure everything was right. I don't want to replace the whole indoor unit because it is leak free and working!
 

Attachments

  • IMG_4312-1.jpg
    IMG_4312-1.jpg
    81.3 KB · Views: 210
  • IMG_4314-1.jpg
    IMG_4314-1.jpg
    53.2 KB · Views: 248
OP
J

jonathan75

Well-known member
Joined
Mar 27, 2013
Messages
1,451
Location
NC
Here are some pictures of what I did today. It took some practice but I finally got the flares looking good. Actually my first flare already looked better then the factor flare. The factory flare had a ridge on it and it was not as deep as it should be.
 

Attachments

  • IMG_4256-1.jpg
    IMG_4256-1.jpg
    152.1 KB · Views: 335
  • IMG_4254-1.jpg
    IMG_4254-1.jpg
    49.7 KB · Views: 264
  • IMG_4250-1.jpg
    IMG_4250-1.jpg
    95.8 KB · Views: 273
  • IMG_4245-1.jpg
    IMG_4245-1.jpg
    75.6 KB · Views: 284
  • IMG_4244-1.jpg
    IMG_4244-1.jpg
    57.8 KB · Views: 275
  • IMG_4241-1.jpg
    IMG_4241-1.jpg
    103.1 KB · Views: 240
  • IMG_4238-1.jpg
    IMG_4238-1.jpg
    71.6 KB · Views: 260
OP
J

jonathan75

Well-known member
Joined
Mar 27, 2013
Messages
1,451
Location
NC
After I pulled down the vacuum for over a hour I tested to make sure it would not raise up too high after I shut the pump off. I went by the LG instructions of not over 1000 in 10 mins. But I did get it down to 97 Microns!
 

Attachments

  • IMG_4293-1.jpg
    IMG_4293-1.jpg
    118.3 KB · Views: 225
  • IMG_4281-1.jpg
    IMG_4281-1.jpg
    122.6 KB · Views: 149
  • IMG_4275-1.jpg
    IMG_4275-1.jpg
    116.6 KB · Views: 144
  • IMG_4272-1.jpg
    IMG_4272-1.jpg
    90.7 KB · Views: 252
  • IMG_4263-1.jpg
    IMG_4263-1.jpg
    74.7 KB · Views: 166
  • IMG_4261-1.jpg
    IMG_4261-1.jpg
    146.9 KB · Views: 167
OP
J

jonathan75

Well-known member
Joined
Mar 27, 2013
Messages
1,451
Location
NC
I pressure tested it by allowing the refrigerant to flow in some after I did the vacuum. I closed the valve back down and tested all the connections.

Such a shame it blows cold and works so well but shakes because of the squirrel cage. :( I really hope Parker Davis comes through for me on Monday and can ship me the new part soon. Has anyone replaced a squirrel cage fan in a mini split before? Can you usually get it out without messing with the coils or refrigerant?
 

Attachments

  • IMG_4314-1.jpg
    IMG_4314-1.jpg
    53.2 KB · Views: 153
  • IMG_4312-1.jpg
    IMG_4312-1.jpg
    81.3 KB · Views: 139
  • IMG_4316-1.jpg
    IMG_4316-1.jpg
    51.6 KB · Views: 209
  • IMG_4305-1.jpg
    IMG_4305-1.jpg
    109.5 KB · Views: 163
  • IMG_4307-1.jpg
    IMG_4307-1.jpg
    138.9 KB · Views: 158

sevenzeronova

Well-known member
Joined
Mar 23, 2014
Messages
53
If it is similar to a mitsubishi, sanyo, fujitsu. You should have no problem changing the the blower wheel. Left side has a sealed bearing . Right side is attached with set screw to motor. A lot a screws in cover and sub cover. But I have replaced many without pumping system down.
 
OP
J

jonathan75

Well-known member
Joined
Mar 27, 2013
Messages
1,451
Location
NC
If it is similar to a mitsubishi, sanyo, fujitsu. You should have no problem changing the the blower wheel. Left side has a sealed bearing . Right side is attached with set screw to motor. A lot a screws in cover and sub cover. But I have replaced many without pumping system down.

Thank you for your feedback. It makes me feel a little better that I should be able to do it without much trouble. Hopefully they have the part in stock.
 
To avoid these ads, REGISTER NOW!
OP
J

jonathan75

Well-known member
Joined
Mar 27, 2013
Messages
1,451
Location
NC
Today I had a chance to make things look a little neater. I still have to cover everything on the wall but I bundled the lot up together for now.

I cut metal edging to fit around the pad so the ground won't fall into it. The pad is embedded some to make it level. After that I put down landscape fabric and mulched. My son helped a lot with this one. He got excited when we found a rock in the mulch.
 

Attachments

  • IMG_4339-1.jpg
    IMG_4339-1.jpg
    78.4 KB · Views: 302
  • IMG_4338-1.jpg
    IMG_4338-1.jpg
    55.1 KB · Views: 291
  • IMG_4337-1.jpg
    IMG_4337-1.jpg
    67.9 KB · Views: 333
  • IMG_4325-1.jpg
    IMG_4325-1.jpg
    117.6 KB · Views: 361
  • IMG_4321-1.jpg
    IMG_4321-1.jpg
    137.9 KB · Views: 283
  • IMG_4371-1.jpg
    IMG_4371-1.jpg
    145.6 KB · Views: 296
  • IMG_4370-1.jpg
    IMG_4370-1.jpg
    140.4 KB · Views: 316
OP
J

jonathan75

Well-known member
Joined
Mar 27, 2013
Messages
1,451
Location
NC
I put the drain tube to the end of the mulched area. Hopefully the mulch won't clog it up, I will keep my eye on it.
 

Attachments

  • IMG_4340-1.jpg
    IMG_4340-1.jpg
    156.8 KB · Views: 227
  • IMG_4342-1.jpg
    IMG_4342-1.jpg
    148.8 KB · Views: 209
  • IMG_4348-1.jpg
    IMG_4348-1.jpg
    63.1 KB · Views: 256
  • IMG_4350-1.jpg
    IMG_4350-1.jpg
    53.9 KB · Views: 272

JakeKohl

Well-known member
Joined
Feb 23, 2012
Messages
1,365
Location
Greenville, SC
Jonathan,

That drain tube will eventually clog since it is below the mulch. It should be elevated so it can drip several inches above the ground.
 
OP
J

jonathan75

Well-known member
Joined
Mar 27, 2013
Messages
1,451
Location
NC
Jonathan,

That drain tube will eventually clog since it is below the mulch. It should be elevated so it can drip several inches above the ground.

Thank you for the tip Jake. I will cut it shorter and fasten it to the wall. I probably should of used PVC pipe because this hose likes to curl up and won't stay straight. That is why I had a rock on the end to keep it from curling.
 
OP
J

jonathan75

Well-known member
Joined
Mar 27, 2013
Messages
1,451
Location
NC
Good news, Parker Davis is shipping me a new squirrel cage fan today. They said I can replace it without messing with the coils or charge. I should get it by the end of the week.
 

TheWhiteMamba

Well-known member
Joined
Aug 20, 2013
Messages
121
Location
The Armpit of California
Great write up and pics!!

One question I have though and it has been bothering me for a few days before I start my install, what wiring are you using for your installation and where did you get it from?

I really don't want to run 12-3 Indoor NM inside a conduit to the outdoors (even tho some people say its ok and some don't) but it is about impossible to find 12-3 outdoor anywhere unless you pony up $200+ for a 250' bundle!

Do you or anyone else have any tips you could share?
 
OP
J

jonathan75

Well-known member
Joined
Mar 27, 2013
Messages
1,451
Location
NC
Great write up and pics!!

One question I have though and it has been bothering me for a few days before I start my install, what wiring are you using for your installation and where did you get it from?

I really don't want to run 12-3 Indoor NM inside a conduit to the outdoors (even tho some people say its ok and some don't) but it is about impossible to find 12-3 outdoor anywhere unless you pony up $200+ for a 250' bundle!

Do you or anyone else have any tips you could share?

I think outdoor rated is more important for direct burial. If the wire is inside a conduit along a wall I don't feel it is necessary. For my case it is just going through a wall right inside a box, it is not exposed to the elements. I just use what I had laying around which was regular 10-3. At least I have room to grow in the future if necessary but I am still using a 20 amp breaker.

From the box to the unit you can use a ready made whip for around $10 that is water tight.
 

TheWhiteMamba

Well-known member
Joined
Aug 20, 2013
Messages
121
Location
The Armpit of California
That is kind of what I was thinking and am going to be going that route seeing as I can't find outdoor wire anywhere that is not in bulk. My unit will be going out off a wall on the garage and not be more than 8 feet from my breaker box anyways (so not buried), and is under a cove, and in central California where we get about 3 inches of rain a year, so I am thinking it should be good. Thanks for the insight.

I hope you get squared away on the squirrel cage! I have the same vibration dampeners as you and hope they work!
 
OP
J

jonathan75

Well-known member
Joined
Mar 27, 2013
Messages
1,451
Location
NC
I hope you get squared away on the squirrel cage! I have the same vibration dampeners as you and hope they work!

I am going to do a final level tweak with the bolts on the dampeners. Also I get a little ticking noise from the unit when running. If I press one side down it stops, so I will tweak on the bolts and play with it until the noise goes away.
 

smokey0810

Well-known member
Joined
Mar 29, 2013
Messages
3,056
Location
Canyon, Texas
Thank you for making everyone pay more for these because you didn't read the directions and evacuate the system.


Appreciate the insult...Actually, the directions do not say anything about having to evac the system, and they make it seem like the heat exchanger is in the main wall unit. Nice to see your first official post was to cut someone down.
 

smokey0810

Well-known member
Joined
Mar 29, 2013
Messages
3,056
Location
Canyon, Texas
Jonathan, I would certainly recommend cleaning the filters in the wall unit every 2 weeks per the instructions. They get pretty dirty, and can be just rinsed with water. I enjoy my unit greatly.
 
OP
J

jonathan75

Well-known member
Joined
Mar 27, 2013
Messages
1,451
Location
NC
Appreciate the insult...Actually, the directions do not say anything about having to evac the system, and they make it seem like the heat exchanger is in the main wall unit. Nice to see your first official post was to cut someone down.

He was a little hard on you. We all make mistakes and that is how we learn. Actually their cost on these parts are probably very low. If you have the 9000 BTU version I think it starts on page 13. The bottom part on page 14 is funny because they tell you how to do it without a vacuum pump but tell you not to do it! :lol: It is like telling you *********** someone but please don't kill anybody.

attachment.php


Jonathan, I would certainly recommend cleaning the filters in the wall unit every 2 weeks per the instructions. They get pretty dirty, and can be just rinsed with water. I enjoy my unit greatly.

I heard about this, they will get clogged fast. I wonder if we can find better filters for the unit? In my garage it does not matter but for the house I would want something better.

BTW, really like your install. Looks sweet!

Thank you, I am looking forward to completing the install. My replacement fan was delayed one day so I won't get it until Friday now. After that and putting the gutter and wrap over the line set and it will be done!
 

Attachments

  • Pioneer Funny.jpg
    Pioneer Funny.jpg
    53.7 KB · Views: 1,560

Random Guy

Well-known member
Joined
Jun 16, 2009
Messages
155
Safer. There is a difference. R410a (the new stuff) doesn't damage the ozone, but it does contribute to the greenhouse effect.
 
OP
J

jonathan75

Well-known member
Joined
Mar 27, 2013
Messages
1,451
Location
NC
New freon is supposed to be environmentally safe...lol

Safer. There is a difference. R410a (the new stuff) doesn't damage the ozone, but it does contribute to the greenhouse effect.

"I read somewhere once that the reason R12 was phased out was because DuPont was about to lose the patent on it. DuPont spent a **** load of cash to lobby the decision and have it replaced with R22 which they still held a patent on. I always thought it was the environuts that caused this, I was pretty shocked to find out it was DuPont themselves." willyd

That was not the first place I heard someone talk about it was because of patent reasons. I am sure when the patent will expire on R-410A it will be "unsafe" as well.
 
OP
J

jonathan75

Well-known member
Joined
Mar 27, 2013
Messages
1,451
Location
NC
I replaced the cage fan. It was 2.5 hours of ladder hell. Keep in mind I have a lot of electromechanical experience professionally and it was a frustrating fix. Of course if I had to do it again it would be much faster and not so frustrating. The learning process while your legs are getting bruised on a ladder for over 2 hours is not fun.

If you approach this repair from a very logical standpoint that if you remove enough screws you can get the fan out it won't work. I still have not got over the fear of copper lines filled with precious freon. You have to get over that fear of bending copper to get this repair done. The only way to get the fan out is to lift the left side of the coil out and up which bends the right side. This is only after you remove everything from the right side to get the motor out. The only picture I have is with the cover off, I was too frustrated and tired to take more pictures after I started getting into it.

Anyway it is done and running smooth and cold! :beer:
 

Attachments

  • IMG_4427-1.jpg
    IMG_4427-1.jpg
    62.1 KB · Views: 246
  • IMG_4419-1.jpg
    IMG_4419-1.jpg
    103.3 KB · Views: 364
OP
J

jonathan75

Well-known member
Joined
Mar 27, 2013
Messages
1,451
Location
NC
I finally found a bigger dryer vent. It was in the siding section and not where the other dryer vents are. I cut the gutter in the back side and slipped it over the line set and attached the dryer vent after removing the back side of it that would normally attach to the house. To make the line set level I had to put more of a curve in the line to take up some extra. I left too much because I didn't have confidence in my flaring skills yet so I gave myself more room so if I had to cut and flare again it wouldn't end up being too short. It is not perfect but it was my first time so next time hopefully it will look better. Maybe next time I will pay extra to get a real line set cover and keep the lines shorter so less extra hanging around.

Run the drain tube up onto the base slab and use a clamp to hold it in place.

Thank you for the tip.
 

Attachments

  • IMG_4430-1.jpg
    IMG_4430-1.jpg
    73.2 KB · Views: 412
  • IMG_4431-1.jpg
    IMG_4431-1.jpg
    66.5 KB · Views: 323
  • IMG_4432-1.jpg
    IMG_4432-1.jpg
    127.4 KB · Views: 291
  • IMG_4434-1.jpg
    IMG_4434-1.jpg
    58.4 KB · Views: 294
  • IMG_4435-1.jpg
    IMG_4435-1.jpg
    77 KB · Views: 285
  • IMG_4439-1.jpg
    IMG_4439-1.jpg
    117.4 KB · Views: 313
  • IMG_4462-1.jpg
    IMG_4462-1.jpg
    95.3 KB · Views: 312
Last edited:
To avoid these ads, REGISTER NOW!
Top Bottom