Receptacle not compatible with Aluminium

The Cobbler

Super Moderator
Staff member
Joined
Oct 24, 2013
Messages
25,988
Location
Niagara Region, Ontario, Canada
Picture of my friends , had a heater plugged in to this receptacle .
diagnosis was aluminum wiring and not a compatible outlet.
They bought the condo 4 or so years ago, knowing it has partial aluminum wiring, not aware the receptacles had issues .

scary
 

Attachments

  • HPIM2779.JPG
    HPIM2779.JPG
    223.2 KB · Views: 42
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
Picture of my friends , had a heater plugged in to this receptacle .
diagnosis was aluminum wiring and not a compatible outlet.
They bought the condo 4 or so years ago, knowing it has partial aluminum wiring, not aware the receptacles had issues .

scary

None of the Decora® style switches, or receptacles, have the CO/ALR, rating, (AL/CU is used for 30A & larger devices), so people wanting to upgrade their devices are going to have problems if they have aluminum, or aluminum alloy branch circuit wiring.
 

gmcgeo

Well-known member
Joined
Mar 11, 2019
Messages
3,701
with the price of copper sky high, i have seen contractors turning to aluminum wiring..... Oh boy
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
None of the Decora® style switches, or receptacles, have the CO/ALR, rating, (AL/CU is used for 30A & larger devices), so people wanting to upgrade their devices are going to have problems if they have aluminum, or aluminum alloy branch circuit wiring.
They make aluminum devices for less than 30 amps, just not decora
 
Last edited:

Bucko

Well-known member
Joined
Aug 23, 2021
Messages
679
As they say, homes are generally built right of in an area that has building codes, its what the homeowner does in the years after that causes issues. I would not buy a home with aluminum branch wiring unless a rewire was budgeted before occupancy. Alot of insurance carriers are refusing to insure homes with it or dropping them when their system says they are due for a 4-point inspection (generally homes over 30 but some now calling for it at 15 years), and its found.
 

gmcgeo

Well-known member
Joined
Mar 11, 2019
Messages
3,701
correct, and ppl are hiring anybody off the street, non qualified to get the work done. where i am nobody wants to work and the ppl who will work do not know what they are doing. :dunno: so like i said, i have been seeing and hearing contractors doing it.
 

gmcgeo

Well-known member
Joined
Mar 11, 2019
Messages
3,701
As they say, homes are generally built right of in an area that has building codes, its what the homeowner does in the years after that causes issues. I would not buy a home with aluminum branch wiring unless a rewire was budgeted before occupancy. Alot of insurance carriers are refusing to insure homes with it or dropping them when their system says they are due for a 4-point inspection (generally homes over 30 but some now calling for it at 15 years), and its found.
Hopefully these inspections are catching these things. I would suspect they are
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
They make aluminum devices for less than 30 amps, just not decora
CO/ALR, is for devices below 30A, AL/CU, is for 30A & above, I mentioned the difference in marking as a FYI, not that they were not available.
 

alien

Well-known member
Joined
Nov 18, 2015
Messages
379
correct, and ppl are hiring anybody off the street, non qualified to get the work done. where i am nobody wants to work and the ppl who will work do not know what they are doing. :dunno: so like i said, i have been seeing and hearing contractors doing it.
Where are they buying Aluminum branch circuit cable?
 

kbuhagiar

Well-known member
Joined
Dec 27, 2005
Messages
1,759
Location
Escondido, CA
with the price of copper sky high, i have seen contractors turning to aluminum wiring..... Oh boy
Aluminum wiring for branch circuits? I didn't think it was available here in the US (or anywhere else) in 12 or 14 gauge. I know it's used for feeder cable...but branch wiring? That's news to me.
 

csp

Well-known member
Joined
Mar 23, 2010
Messages
5,720
Location
Franktown, CO
with the price of copper sky high, i have seen contractors turning to aluminum wiring..... Oh boy
Why do I get the feeling that you're referring to feeder wire, not individual branch circuits in the home?

Feeder wire in aluminum is perfectly acceptable if it's the right size and type.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,593
Location
Fullerton, CA
Aluminum wiring for branch circuits? I didn't think it was available here in the US (or anywhere else) in 12 or 14 gauge. I know it's used for feeder cable...but branch wiring? That's news to me.
#14 aluminum wire was never produced. (Because #12 is rated for 15Amps, the minimum breaker size in regular use). #12 and 10 are solid, #8 and larger are stranded.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
Aluminum wiring for branch circuits? I didn't think it was available here in the US (or anywhere else) in 12 or 14 gauge. I know it's used for feeder cable...but branch wiring? That's news to me.
Very common in the late 1960's & early 1970's, in mobile homes, & multi family dwellings, tract homes, it became aluminum alloy conductors in the early 70's which improved the product.

BTW, there seem to be a big push for copper clad aluminum conductors in the NEC.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,073
Location
Modesto, CA
correct, and ppl are hiring anybody off the street, non qualified to get the work done. where i am nobody wants to work and the ppl who will work do not know what they are doing. :dunno: so like i said, i have been seeing and hearing contractors doing it.
you obviously think that people can just walk into a hardware store and buy aluminum branch circuit wiring sized #12 and #10. in reality they cant. It hasnt been made for years and years so your comment makes no sense here.
 
OP
T

The Cobbler

Super Moderator
Staff member
Joined
Oct 24, 2013
Messages
25,988
Location
Niagara Region, Ontario, Canada
This building was built int he early/mid 70's when aluminum was very common place for circuits . They were aware of part of the unit being aluminum prior to purchase . I have done 2 bathroom & a kitchen reno for them. the wire that comes from the panel thru conduit is copper. the BX that feeds the receptacles & switches is aluminum .
The approved fix ( or the proper way ) to use Decora with aluminum is pigtail copper with approved marettes , and it was not done in this case.
the average home owner that changes receptacles & switches has no idea of how to properly treat aluminum and it's very common to have this scenario.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
Aluminum NM sheathed cable is still allowed by the NEC but not manufactured anymore, the only way to use it today is to find new old stock (NOS) AL NM, the only problem is that NOS AL cable is NM cable with a 60°C rating, & it is required to have a 90°C rating, NM-B since the mid 1980's. I am not a fan of either Aluminum Alloy, or copper clad AL, branch circuit wiring, copper clad AL, is sized like AL, but is terminated with ordinary/ standard devices.
 

haveissues

Well-known member
Joined
Feb 9, 2011
Messages
379
Location
Hudson Valley NY
you obviously think that people can just walk into a hardware store and buy aluminum branch circuit wiring sized #12 and #10. in reality they cant. It hasnt been made for years and years so your comment makes no sense here.
I very recently saw copper clad nm wire for sale somewhere, but can't remember where. It was online, not local and I remember thinking wow, some knucklehead is going to use this stuff without knowing (or caring) what it is.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,073
Location
Modesto, CA
I very recently saw copper clad nm wire for sale somewhere, but can't remember where. It was online, not local and I remember thinking wow, some knucklehead is going to use this stuff without knowing (or caring) what it is.
That would be NOS and not useable since as Norcal pointed out, is not properly rated.

Someone probably dug it out of a garage somewhere and dusted it off

Do you have any pics?
 

haveissues

Well-known member
Joined
Feb 9, 2011
Messages
379
Location
Hudson Valley NY
That would be NOS and not useable since as Norcal pointed out, is not properly rated.

Someone probably dug it out of a garage somewhere and dusted it off

Do you have any pics?
No, and I cant remember where I saw it for sale. If I remember correctly it was some no name chinese ****, not NOS.
 

FMB4

Well-known member
Joined
Jan 19, 2017
Messages
2,926
Aluminum wiring: be it branch or feeder is an absolute no go for me. The last thing you want to 'cheap out' on is electrical.
 

csp

Well-known member
Joined
Mar 23, 2010
Messages
5,720
Location
Franktown, CO
Very common in the late 1960's & early 1970's, in mobile homes, & multi family dwellings, tract homes, it became aluminum alloy conductors in the early 70's which improved the product.

BTW, there seem to be a big push for copper clad aluminum conductors in the NEC.
The person you quoted was referring to the availability of AL today, based on the person who stated that he's seen contractors using it now in response to the price of copper.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,903
Location
Richmond, VA
Aluminum wiring: be it branch or feeder is an absolute no go for me. The last thing you want to 'cheap out' on is electrical.
Aluminum is totally safe for feeder and it is used in nearly every house, including by the utility. It isn't cheaping out.

But it's your money to spend
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,049
Location
Coronado, CA
This problem surfaced years ago, as I recall the wire makers managed to put legal pressure on the Consumer Products Safety Commission and the only way I know to get the information, was to make a Freedom Of Information Act request. I had a copy years ago, but lost it.

The Building should, IMHO, be re-wired by the HOA.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,073
Location
Modesto, CA
Aluminum wiring: be it branch or feeder is an absolute no go for me. The last thing you want to 'cheap out' on is electrical.
nothing wrong with aluminum feeders or branch circuit wiring (#8 SER and larger). its used everyday... but today's aluminum wiring is not the same as the wiring from decades ago. they changed the alloys to fix the issue.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
This problem surfaced years ago, as I recall the wire makers managed to put legal pressure on the Consumer Products Safety Commission and the only way I know to get the information, was to make a Freedom Of Information Act request. I had a copy years ago, but lost it.

The Building should, IMHO, be re-wired by the HOA.
The CPSC never acted on AL wiring as it not really a consumer product.
 

Knight511

Well-known member
Joined
Dec 28, 2020
Messages
91
Location
TX
nothing wrong with aluminum feeders or branch circuit wiring (#8 SER and larger). its used everyday... but today's aluminum wiring is not the same as the wiring from decades ago. they changed the alloys to fix the issue.
Got a quote to finish my project 2 weeks ago and the electrician refused to use AL wire (#2 and #4) to make the run to the subpanel citing the problems from decades past. Not all electricians are as up to date on materials as you are, unfortunately.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,903
Location
Richmond, VA
Got a quote to finish my project 2 weeks ago and the electrician refused to use AL wire (#2 and #4) to make the run to the subpanel citing the problems from decades past. Not all electricians are as up to date on materials as you are, unfortunately.
I wouldnt hire someone that is so out of touch with current practices. Sound alike the guy that does it his way and would blow off a modern code change because it is "new fangled ********"
 

Knight511

Well-known member
Joined
Dec 28, 2020
Messages
91
Location
TX
I wouldnt hire someone that is so out of touch with current practices. Sound alike the guy that does it his way and would blow off a modern code change because it is "new fangled ********"
When he cited "the code" preventing running a subpanel from a subpanel (first sub is less than 24 inches from the main panel (which is out of space) and then stacked the Al comment on, I opted to quit being "scared" of my freaking attic and finish the job I planned.

Clarification: My house main panel is 200amp and will be out of space, so I want a subpanel next to it in the garage to provide the space for the pool, eave outlets, and the new subpanel in my workshop. He wanted to double up circuits on the main panel until there was enough space for 2 100amp sub panels and the pool breaker. I felt like that was just cramming too much **** into an already stuffed full break panel.
 

Innovate1

Well-known member
Joined
Jul 28, 2014
Messages
4,297
Location
Illinois near St. Louis, Missouri
I had a house built around 1970 that had aluminum wire for the receptacles. Had it about 5 years. Fortunately didn't have to do much to the place over that time although I recall replacing one receptacle and getting one rated for aluminum wire. As I understand it, and I could be wrong, is that the wire of that era was soft and more recent wire is harder alloy. It would creep over time allowing the connections to become loose. There are, or were, devices that would put a full load on the circuit for a very brief time (to reduce heating of the load) and measure the voltage drop. If it was high you have a problem. The same thing could be done with a heater or blow drier and a multimeter. I did it a few places as a test and never found any issues. I suppose such tests would need to be repeated at some interval to catch problems that develop over time.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,073
Location
Modesto, CA
When he cited "the code" preventing running a subpanel from a subpanel (first sub is less than 24 inches from the main panel (which is out of space) and then stacked the Al comment on, I opted to quit being "scared" of my freaking attic and finish the job I planned.

Clarification: My house main panel is 200amp and will be out of space, so I want a subpanel next to it in the garage to provide the space for the pool, eave outlets, and the new subpanel in my workshop. He wanted to double up circuits on the main panel until there was enough space for 2 100amp sub panels and the pool breaker. I felt like that was just cramming too much **** into an already stuffed full break panel.
and what was the code he cited? the actual code number?

I'd fire this guy quicker than i could say abracadabra
 