I got it all completed today. 222v to the machine. Special thanks to mm08822 for walking me through it all.


:thumbup: My pleasure!

As been said before, "220/221 whatever it takes."

Post some pics of your first project.
 

6PTsocket

Well-known member
Joined
Mar 12, 2014
Messages
4,593
Calling for 220?

Well as has been seen here, getting the voltage correct IS important.

So what if the OP just assumed the 220v on machine label meant 240v? **** the smoke gets let out!
Gee, I guess that if 222 didn't let out the smoke, 220 probably would not have either. Considering normal small line fluctuations, 222 IS 220. There is no such thing as different 220, 230 and 240 service. I usually measure about the same as the OP, just over 220. Tell me how low voltage is going to damage a dynamic brake? It might not work as well but damage?

Sent from my SM-G900V using Tapatalk
 
OP
W

Whiskeymike

Well-known member
Joined
Oct 31, 2013
Messages
775
Location
Austin, TX
the manufacturer says that it needs to be 220v +/- 5% which means roughly 209v to 231v. I don’t know how it would break, as I don’t understand the intricacies of electromagnetic circuits.

All in all, it was an extra $100 to get it working. I knew before I bought it, I might have to do this. As long as the brake works to my expectations, I’ll be happy with it.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,180
Location
SE MI
I don’t know how it would break, as I don’t understand the intricacies of electromagnetic circuits.

Electromagnets are pure resistance when used in a DC circuit. In an AC circuit they also have inductance, but that is not really important in this application.

If the voltage is above spec, then the magnet will draw more current (Ohm's Law V=IR and R is constant in this case). More current will mean more heat .

Now because this magnet is only turned on for a short period of time and that is followed by a long off period (very low duty cycle) this probably does not matter. If used in some kind of "production" environment with pre-cut blanks and pre-set edges stops that duty cycle could easily get above 50% and then the extra heat could be an issue.
 
To avoid these ads, REGISTER NOW!

nsula_country

Well-known member
Joined
May 23, 2013
Messages
1,534
Location
Northwestern Louisiana
OP did right by following the recommendations of the MFG. Line voltage at our house and shop (2 services) run about 242v-248v. Well above their spec for the machine. If this had been my brake, I'd probably use a buck too. Had this been a motor, I would haven't thought twice about hooking up and using the machine.

At work our 480 is tapped about 500v-510v when the plant is idle. Once everything is running and loaded it drops to about 482v-490v. A plant down the road was having some issues and asked the City to bump the primary up a little. Then we had some devices starting to trip on overvoltage alarms around 500v (Fronius 500 amp Inverter Welding Power Supplies). We ended up dropping down an output tap on our transformers.

There are limitations of how high or low of voltage devices will tolerate.

CT
 

foolishpride

Well-known member
Joined
Mar 21, 2009
Messages
343
Location
Southwestern Ohio
I would have asked the POCO to raise the tap on the tapchanger on the transformer supplying you. Probably would eliminate the need for the zig-zag transformer.
 

bloomingtonmike

Well-known member
Joined
Dec 1, 2011
Messages
314
Location
Bloomington, IL
Old thread. But I picked up a Baileigh Magnetic Brake last week and got a SquareD Buck Transformer installed last night. Made a video about that if anyone needs the info. Used same calculator listed here in this thread as it turns out.

 