A couple of members have asked me about the remote compressor control I've got in my shop.
Here are the details of the setup. It revolves around a DP (Definite Purpose) contactor I got from Grainger.
http://www.grainger.com/Grainger/items/2UTN5
It's rated for up to 5hp at 230v.
Think of it as a big magnetic switch. Apply voltage to the coil and the magnet energizes and closes the contacts in the switch, passing voltage thru from the line to the load.
The coil on this contactor is rated for 120v, so all you need to do is get 120v to the coil when you want the compressor to run.
Rather than wiring a direct circuit, I used a remote-control Insteon appliance module I got from Smarthome.com:
http://www.smarthome.com/2456S3/App...Plug-in-Appliance-Control-Module-3-pin/p.aspx
This device is nothing more than a small DP contactor that can be triggered by other Insteon devices. I also bought a Insteon relay switch (don't want a dimmer in this situation):
http://www.smarthome.com/2476S/Swit...ontrol-On-Off-Switch-Non-Dimming-White/p.aspx
I put the DP contactor in an enclosure like this one:
http://www.homedepot.com/h_d1/N-5yc...splay?langId=-1&storeId=10051&catalogId=10053
Ran 220v into the box to one side of the contactor (there are 4 spade lugs on each side, 2 for each pole of the switch). From the other end of the contactor, two wires out to the pressure switch on the compressor.
Added a cord to the box with a 3-pole plug on the end. Hot to one side of the coil, and neutral to the other side of the coil. (I put the hot on the coil connector in the back of the box - there are 2 spade lugs for each coil connection, and the bare lug is hot when 120v is present).
Plug the cord into the appliance module. Plug the appliance module into a wall socket.
Install the switch in a box that has hot and neutral wires (must have neutral). Cap the line lead from the switch.
Press and hold the "on" side of the toggle until the switch beeps. Within 4 minutes, press the "learn" button on the appliance module to link the two devices.
Insteon uses RF and neutral line X-10-ish protocols so it's very reliable.
Of course, you don't have to use the Insteon controls, that adds $80 to the cost, you just have to have a switched 120v line going to the contactor coil.
If the compressor is like mine (Quincy QV41C60VC), it has an unloader valve that only engages when the pressure switch reaches full value. That can be a problem if you turn the compressor off before it reaches full pressure and try to turn it on before the head pressure has a chance to bleed off.
I solved this by t'ing in a electric valve at the check valve on the top of the tank. The valve is normally open (requires voltage to close the valve).
This is completely optional. If you don't cycle the compressor on and off in mid-cycle, or if you wait a few minutes from off to on below full pressure you should be fine.
I started out with this valve:
http://www.grainger.com/Grainger/items/2G499
I already had this valve from another project.
It's perfect because it's a 1/8" valve, and the check valve has a 1/8" port.
However, the coil is making a hell of a racket when engaged, and the max operating pressure is 150psi, while my compressor cut-out is 175psi. I don't know if this is because the valve is old or damaged or if it's PO'd about the extra 25psi.
I've just ordered this - part # 4738K712 - rated for 175psi operating pressure:
http://www.mcmaster.com/ctlg/DisplC...track=true&ScreenWidth=1280&McMMainWidth=1066
The valve is wired to the free pair of lugs for the 120v coil on the DP contactor. When the contactor is triggered, the valve closes. When the contactor is released, the valve opens and vents the compressor head pressure.
I also have another one of these valves on the drain for the compressor, but the coil is a 220v model - I wired it up to the terminals on the pressure switch. When I cut the power to the compressor, the tank dumps completely. I'm frequently away from the shop for days and sometimes weeks at a time - I prefer to completely drain the tank every time I leave.
Total cost:
Contactor: 24.33
Enclosure: 14.77
Insteon Switch: 45.99
Insteon Appliance Module: 34.99
175psi Unloader valve 91.89
You could get all this for as little as $39.10, or blow the whole wad for $211.97 (plus freight and applicable sales tax).
I welcome questions and suggestions.
Regards
Here are the details of the setup. It revolves around a DP (Definite Purpose) contactor I got from Grainger.
http://www.grainger.com/Grainger/items/2UTN5
It's rated for up to 5hp at 230v.
Think of it as a big magnetic switch. Apply voltage to the coil and the magnet energizes and closes the contacts in the switch, passing voltage thru from the line to the load.
The coil on this contactor is rated for 120v, so all you need to do is get 120v to the coil when you want the compressor to run.
Rather than wiring a direct circuit, I used a remote-control Insteon appliance module I got from Smarthome.com:
http://www.smarthome.com/2456S3/App...Plug-in-Appliance-Control-Module-3-pin/p.aspx
This device is nothing more than a small DP contactor that can be triggered by other Insteon devices. I also bought a Insteon relay switch (don't want a dimmer in this situation):
http://www.smarthome.com/2476S/Swit...ontrol-On-Off-Switch-Non-Dimming-White/p.aspx
I put the DP contactor in an enclosure like this one:
http://www.homedepot.com/h_d1/N-5yc...splay?langId=-1&storeId=10051&catalogId=10053
Ran 220v into the box to one side of the contactor (there are 4 spade lugs on each side, 2 for each pole of the switch). From the other end of the contactor, two wires out to the pressure switch on the compressor.
Added a cord to the box with a 3-pole plug on the end. Hot to one side of the coil, and neutral to the other side of the coil. (I put the hot on the coil connector in the back of the box - there are 2 spade lugs for each coil connection, and the bare lug is hot when 120v is present).
Plug the cord into the appliance module. Plug the appliance module into a wall socket.
Install the switch in a box that has hot and neutral wires (must have neutral). Cap the line lead from the switch.
Press and hold the "on" side of the toggle until the switch beeps. Within 4 minutes, press the "learn" button on the appliance module to link the two devices.
Insteon uses RF and neutral line X-10-ish protocols so it's very reliable.
Of course, you don't have to use the Insteon controls, that adds $80 to the cost, you just have to have a switched 120v line going to the contactor coil.
If the compressor is like mine (Quincy QV41C60VC), it has an unloader valve that only engages when the pressure switch reaches full value. That can be a problem if you turn the compressor off before it reaches full pressure and try to turn it on before the head pressure has a chance to bleed off.
I solved this by t'ing in a electric valve at the check valve on the top of the tank. The valve is normally open (requires voltage to close the valve).
This is completely optional. If you don't cycle the compressor on and off in mid-cycle, or if you wait a few minutes from off to on below full pressure you should be fine.
I started out with this valve:
http://www.grainger.com/Grainger/items/2G499
I already had this valve from another project.
It's perfect because it's a 1/8" valve, and the check valve has a 1/8" port.
However, the coil is making a hell of a racket when engaged, and the max operating pressure is 150psi, while my compressor cut-out is 175psi. I don't know if this is because the valve is old or damaged or if it's PO'd about the extra 25psi.
I've just ordered this - part # 4738K712 - rated for 175psi operating pressure:
http://www.mcmaster.com/ctlg/DisplC...track=true&ScreenWidth=1280&McMMainWidth=1066
The valve is wired to the free pair of lugs for the 120v coil on the DP contactor. When the contactor is triggered, the valve closes. When the contactor is released, the valve opens and vents the compressor head pressure.
I also have another one of these valves on the drain for the compressor, but the coil is a 220v model - I wired it up to the terminals on the pressure switch. When I cut the power to the compressor, the tank dumps completely. I'm frequently away from the shop for days and sometimes weeks at a time - I prefer to completely drain the tank every time I leave.
Total cost:
Contactor: 24.33
Enclosure: 14.77
Insteon Switch: 45.99
Insteon Appliance Module: 34.99
175psi Unloader valve 91.89
You could get all this for as little as $39.10, or blow the whole wad for $211.97 (plus freight and applicable sales tax).
I welcome questions and suggestions.