I have a zone valve that needs replacing. It runs two rooms in basement. How do I go about making the pipes safe to work on? There's a water shut off before the valve but I know there will still be water after it... and hot at that probably! It's been stuck open for a while and keeps recirculating. Also, can I use regular silver solder?
 
To avoid these ads, REGISTER NOW!

MEngineer

Well-known member
Joined
Apr 13, 2015
Messages
345
Location
Everett, Wa
Not knowing where you live I would assume that you are not cold enough to need heat yet.

I would recommend shutting down your heating system so that you can drain the lines associated with your valve, and then adequately bleed the lines after replacement.

Silver solder is just fine, though since it should not be tied to your potable water, leaded solder would also be acceptable.

Something to consider: most zone valves have replaceable motor heads. typically (in my experience) the motor unit will fail, but the valve will still be ok.

you may consider buying a replacement motor head, actuator, whatever they call it and checking to see if that resolves the issue. I would also check Supplyhouse.com for any of your plumbing needs as they have REALLY competitive pricing and are super helpful via customer service.
 

sms1974

Well-known member
Joined
Jul 9, 2014
Messages
210
Location
Grafton Ohio
What brand of valve is it? some valves have a motor that can be replaced without getting into cutting out piping
 
OP
S

SuzukiGS750EZ

Well-known member
Joined
Apr 26, 2012
Messages
3,273
Not knowing where you live I would assume that you are not cold enough to need heat yet.

I would recommend shutting down your heating system so that you can drain the lines associated with your valve, and then adequately bleed the lines after replacement.

Silver solder is just fine, though since it should not be tied to your potable water, leaded solder would also be acceptable.

Something to consider: most zone valves have replaceable motor heads. typically (in my experience) the motor unit will fail, but the valve will still be ok.

you may consider buying a replacement motor head, actuator, whatever they call it and checking to see if that resolves the issue. I would also check Supplyhouse.com for any of your plumbing needs as they have REALLY competitive pricing and are super helpful via customer service.
I replaced the top portion, the head and it made no difference. Heat guy's told me I need a new bottom portion. Can you explain how to drain & bleed system or link? Thanks guys!
 

Kaizen

Well-known member
Joined
Jan 9, 2015
Messages
6,938
Location
New England
Pics of the setup will be helpful to tell you what to do.
With the tacos if you can manually operate it with the lever then it’s probably the head. You sure you didn’t leave the lever in the on position?


Sent from my iPhone using Tapatalk
 

Jim greengo

Well-known member
Joined
Sep 3, 2018
Messages
7,415
Location
Behind my house
Pics of the setup will be helpful to tell you what to do.
With the tacos if you can manually operate it with the lever then it’s probably the head. You sure you didn’t leave the lever in the on position?


Sent from my iPhone using Tapatalk

What he said.
 
OP
S

SuzukiGS750EZ

Well-known member
Joined
Apr 26, 2012
Messages
3,273
Here's the setup. If you need anything more specific please ask. c7cf5fe92fbfa3fc87adf31a52db5701.jpgdff5d417dd0e8357fce340e9afb77539.jpgb282f726267123f65f4ba305430211a8.jpg
 

Attachments

  • b282f726267123f65f4ba305430211a8.jpg
    b282f726267123f65f4ba305430211a8.jpg
    63.5 KB · Views: 0
  • dff5d417dd0e8357fce340e9afb77539.jpg
    dff5d417dd0e8357fce340e9afb77539.jpg
    62.7 KB · Views: 0
  • c7cf5fe92fbfa3fc87adf31a52db5701.jpg
    c7cf5fe92fbfa3fc87adf31a52db5701.jpg
    90.1 KB · Views: 0
OP
S

SuzukiGS750EZ

Well-known member
Joined
Apr 26, 2012
Messages
3,273
Pics of the setup will be helpful to tell you what to do.
With the tacos if you can manually operate it with the lever then it’s probably the head. You sure you didn’t leave the lever in the on position?


Sent from my iPhone using Tapatalk
I can pull the lever with pliers. The guy who was here to service the system said he sprayed wd40 in there and used a c clamp to free it but said it would probably freeze again. The other one has been fine and is easy to operate.
 
To avoid these ads, REGISTER NOW!

Kaizen

Well-known member
Joined
Jan 9, 2015
Messages
6,938
Location
New England
Hope all of that mess isn’t your handiwork? Pipe insulation doesn’t work well like that. Water heater electric and rest of those wires should be better secured.
Do you know how to solder?
Hard to tell if that zone has shut offs on both sides. If it had two then you could shut them off and cut. The remaining water would slowly gurgle out as the vacuum is released. A short space very quickly. If there is one shutoff then the whole zone then the whole zone back to boiler will drain. Not horrible you just have to wait for it and tilt the pipe till it’s dry. You can’t solder in a pipe with water leaking into it. Good news is it’s hot so you have awhile to figure this all out.
I’d cut back before the elbow on one side and then in the side of the zone. Easier to cut out and replace. Make sure you read taco instructions on removing head before heat. You can build it all on a bench then just have to solder two joints in the air.
Shut off water supply to boiler and all other shut offs on it. If you cannot isolate that loop with two shutoffs (beginning at boiler and ending as close as you can to boiler) it would be a good time to add one. It will help with both zones when you have to bleed it after.


Sent from my iPhone using Tapatalk
 
OP
S

SuzukiGS750EZ

Well-known member
Joined
Apr 26, 2012
Messages
3,273
Hope all of that mess isn’t your handiwork? Pipe insulation doesn’t work well like that. Water heater electric and rest of those wires should be better secured.
Do you know how to solder?
Hard to tell if that zone has shut offs on both sides. If it had two then you could shut them off and cut. The remaining water would slowly gurgle out as the vacuum is released. A short space very quickly. If there is one shutoff then the whole zone then the whole zone back to boiler will drain. Not horrible you just have to wait for it and tilt the pipe till it’s dry. You can’t solder in a pipe with water leaking into it. Good news is it’s hot so you have awhile to figure this all out.
I’d cut back before the elbow on one side and then in the side of the zone. Easier to cut out and replace. Make sure you read taco instructions on removing head before heat. You can build it all on a bench then just have to solder two joints in the air.
Shut off water supply to boiler and all other shut offs on it. If you cannot isolate that loop with two shutoffs (beginning at boiler and ending as close as you can to boiler) it would be a good time to add one. It will help with both zones when you have to bleed it after.


Sent from my iPhone using Tapatalk
Thank you for your explanation. No, NONE of that is my handy work besides the overhead light/ switch I installed and that was done properly lol. I've been going through the house getting it up to snuff, this room is a sump pump/utility/storage room. Last on the list. Yes, I know how to solder, I have sweat many pipes. That zone has a shut off before the valve and that's it, unless I'm missing something?
 
Last edited:
OP
S

SuzukiGS750EZ

Well-known member
Joined
Apr 26, 2012
Messages
3,273
Yes, the mold on the ceiling/subfloor is being taken care of. It's a chimney leak.57c2548d72bbb9224699b34c33b500d9.jpg01de8ef1187d055479d88368a9d2109c.jpg088271ca4291e7b08c96db89a5b9fd43.jpg
 

Attachments

  • 57c2548d72bbb9224699b34c33b500d9.jpg
    57c2548d72bbb9224699b34c33b500d9.jpg
    80.3 KB · Views: 0
  • 01de8ef1187d055479d88368a9d2109c.jpg
    01de8ef1187d055479d88368a9d2109c.jpg
    100.8 KB · Views: 0
  • 088271ca4291e7b08c96db89a5b9fd43.jpg
    088271ca4291e7b08c96db89a5b9fd43.jpg
    108.3 KB · Views: 0

Kaizen

Well-known member
Joined
Jan 9, 2015
Messages
6,938
Location
New England
Thank you for your explanation. No, NONE of that is my handy work besides the overhead light/ switch I installed and that was done properly lol. I've been going through the house getting it up to snuff, this room is a sump pump/utility/storage room. Last on the list. Yes, I know how to solder, I have sweat many pipes. That zone has a shut off before the valve and that's it, unless I'm missing something?



Back on the boiler there are two yellow shut offs. Those might be the end of the loops. Above the circulator. Shut them all off and the water supply to it.
Below these yellow ones there is another pipe coming in as well. Put one there as well. I’m a little shut off crazy but makes life easy. If you can isolate that circulator then when it fails on a freezing day you can change it out in 20 min after grabbing one at hd.
When done you will put a hose on the drain. I put one on my main pipe to circulator. Then with the unit still off you just open the fill valve manually, open one zone valve manually, and the shutoff so city water pressure runs through and purges the air out of the zone. Then shut all of that off and repeat with other zones. Not much air will be in system after that.


Sent from my iPhone using The Garage Journal mobile app
 
OP
S

SuzukiGS750EZ

Well-known member
Joined
Apr 26, 2012
Messages
3,273
Back on the boiler there are two yellow shut offs. Those might be the end of the loops. Above the circulator. Shut them all off and the water supply to it.
Below these yellow ones there is another pipe coming in as well. Put one there as well. I’m a little shut off crazy but makes life easy. If you can isolate that circulator then when it fails on a freezing day you can change it out in 20 min after grabbing one at hd.
When done you will put a hose on the drain. I put one on my main pipe to circulator. Then with the unit still off you just open the fill valve manually, open one zone valve manually, and the shutoff so city water pressure runs through and purges the air out of the zone. Then shut all of that off and repeat with other zones. Not much air will be in system after that.


Sent from my iPhone using The Garage Journal mobile app
Does it make a difference if I'm on well water (for bleeding)? And if I don't get all the air out, it'll clunk, right? Should I shut off the water at the well tank?
 
Last edited:

Kaizen

Well-known member
Joined
Jan 9, 2015
Messages
6,938
Location
New England
here a pic of stuff you should know. shut off water as indicated. only difference for well is pressure. higher pressure gets air out better. esp on 2nd floor loops. should work fine to get most of the air out. system should get the rest out as it runs. right that tinging or banging is air.

heater.jpg
 
OP
S

SuzukiGS750EZ

Well-known member
Joined
Apr 26, 2012
Messages
3,273
here a pic of stuff you should know. shut off water as indicated. only difference for well is pressure. higher pressure gets air out better. esp on 2nd floor loops. should work fine to get most of the air out. system should get the rest out as it runs. right that tinging or banging is air.



heater.jpg
Awesome. Thanks for doing that. Knew none of those!
 

66cj225

Well-known member
Joined
Nov 4, 2011
Messages
332
Location
NH
All those topics you've discussed and your heat looks like that? If you're going to drain it, now's the time to clean it up.
 