Reset breakers, house power still out.

To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,754
Hopefully when the breaker died it didn't single phase( allowed only one of the 110 lines to pass thru) and burn your compressor/fan.

TheGrooveking

That is a single phase service, single phasing is when 1 leg of a 3 Ø circuit is lost. BTW, single pole contactors are common on HVAC equipment which means they only switch 1 leg of the 240V supply.
 

rickairmedic

Well-known member
Joined
May 31, 2005
Messages
4,165
Location
louisville ,Ky
Pull the disconect out by the AC unit and pull the panel off of it . The capacitor is going to be a round cylinder with 3-4 wires going to the top of it if the top is rounded up and not flat and rexessed into the top then you have a blown capacitor . The only way you are going to get one on the 4th of July will be to call an AC guy as all the supply houses will be closed " trust me I are an AC guy and although I am working tomorrow all the supply houses here are closed " .


Oh yeah dont touch any of the contacts on the capacitor without first shorting them out with a screwdriver as they can hold up to 440 volts in a residential unit and you will barely remember what happened when " if " you wake up :D.


Rick
 

danski0224

Well-known member
Joined
Jan 29, 2005
Messages
13,405
Location
Near Naperville, IL
Oh yeah dont touch any of the contacts on the capacitor without first shorting them out with a screwdriver as they can hold up to 440 volts in a residential unit and you will barely remember what happened when " if " you wake up :D.

I wouldn't be telling people that without telling them to pull the disconnect first.

Sometimes, troubleshooting stuff is best left to the pros. The OP in this case has difficulties with simply resetting a circuit breaker.

Not sure if basic internet electrical HVAC troubleshooting is something I would provide.

And a good AC guy will have a few spare parts for emergencies.
 
To avoid these ads, REGISTER NOW!

Corins

Well-known member
Joined
Feb 11, 2011
Messages
162
Location
Canada
Sometimes, troubleshooting stuff is best left to the pros. The OP in this case has difficulties with simply resetting a circuit breaker.

I agree that leaving stuff to the pros is the best idea if your not sure of something. However it wasn't so much resetting a breaker obviously he did that correctly, it just doesn't do any good if the main is shot.
 

TheGrooveking

Well-known member
Joined
Dec 30, 2007
Messages
3,233
Location
An alternate reality in a parallel universe.
That is a single phase service, single phasing is when 1 leg of a 3 Ø circuit is lost. BTW, single pole contactors are common on HVAC equipment which means they only switch 1 leg of the 240V supply.


Yes you are correct in regards to it being called single phase service, but if you look at the two legs on a scope you will see they are not in phase with each other, hence two 110 lines equalling 220 volt because they are opposing each other in the sine wave. You are correct in regards to some equipment switching only one leg of a 220 circuit(I find that to personally be a cheap stupid unsafe way to build a piece of equipment).

As it was late and I was very tired when I posted, I mixed up loosing one leg and loosing the neutral, which I've seen burn a lot of stuff up and even cause fires. THanks for the correction, I'd rather be wrong than to have other learn/use incorrect information.

TheGrooveking
 

bgott

Well-known member
Joined
Oct 31, 2005
Messages
3,512
Location
Houston, TX.
You are correct in regards to some equipment switching only one leg of a 220 circuit(I find that to personally be a cheap stupid unsafe way to build a piece of equipment).

They do it that way because there is a heater in the compressor that they want to run all the time. It keeps the refrigerant vaporized so that it doesn't turn to liquid and slug the compressor on start-up.
 

rickairmedic

Well-known member
Joined
May 31, 2005
Messages
4,165
Location
louisville ,Ky
Pull the disconect out by the AC unit and pull the panel off of it . The capacitor is going to be a round cylinder with 3-4 wires going to the top of it if the top is rounded up and not flat and rexessed into the top then you have a blown capacitor . The only way you are going to get one on the 4th of July will be to call an AC guy as all the supply houses will be closed " trust me I are an AC guy and although I am working tomorrow all the supply houses here are closed " .


Oh yeah dont touch any of the contacts on the capacitor without first shorting them out with a screwdriver as they can hold up to 440 volts in a residential unit and you will barely remember what happened when " if " you wake up :D.


Rick

I wouldn't be telling people that without telling them to pull the disconnect first.

Sometimes, troubleshooting stuff is best left to the pros. The OP in this case has difficulties with simply resetting a circuit breaker.

Not sure if basic internet electrical HVAC troubleshooting is something I would provide.

And a good AC guy will have a few spare parts for emergencies.


Ya gotta read a little more in depth Danski :D and yes theres at least 40 capacitors on my service truck right now . My point was the only way the OP was going to get one on a holiday weekend was to call a service tech out .


Rick
 