Romex IN conduit for protection

Ramper

Well-known member
Joined
Nov 30, 2010
Messages
1,484
Location
Southern MN
I am working to complete my shop (30x40 pole building). I have successfully run some out outlets in the ceiling (not up yet so in the rafters).

I want to add some outlets to some shelving that was installed when we bought the property. The shelving was 4 feet deep across the back wall and half of one side. There were two shelves (one about 4 feet up and one about 8 feet). I took some of the bottom selves out to make some more floor space (I gain about 24 feet by four feet). I want to add some outlets to the posts of the shelves I took out. I plan to run romex in the wall to to the posts, but would like to protect the outlets and wire by using metal conduit and boxes.

Can I use the conduit to protect the romex? Would PVC be OK or should I use metal. I plan to run four outlets (two plugs each) on their own GFCI protected circuit (I will use a GFCI for the 1st outlet)
 
To avoid these ads, REGISTER NOW!

over40pirate

Well-known member
Joined
Aug 31, 2012
Messages
160
Some where I read that Romex in conduit, is regarded as a damp environment and requires the direct burial type of Romex.
 
OP
R

Ramper

Well-known member
Joined
Nov 30, 2010
Messages
1,484
Location
Southern MN
I just have the yellow (12 gauge) romex. Did I use the wrong stuff of the ceiling outlets?
 
To avoid these ads, REGISTER NOW!

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
It sounds as if you are wanting to just run it up the posts to protect the wire, and not run a complete conduit system. Romex is very difficult to pull in conduit, so if you want to fully run conduit, get THHN wire, if you just want to run up the posts to the rafters and stop, yes, its legit and a good thing to do. Plastic or metal depends on the boxes you use. Inside I would be using metal (EMT) and steel boxes. They make a conduit end to clamp the wire where it exits the EMT, which makes for a neater installation.

29250d1266352582-emt-conduit-998019841_09-13-07_i-rv.jpg


Charles
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
If using EMT you can also use a press on EMT plastic bushing on the end where the Romex enters. You need to staple the Romex within 12" of the conduit end.
 