Still on the fence about where to put my building. First of all how many 125amp sub panels can you connect to a 200 amp main panel? Then the second question is would it be cheaper to have the power company drop another line in? Or is 250-300ft too far? I thought they did this for free.
 
To avoid these ads, REGISTER NOW!
OP
H

Hobby_Man22

Well-known member
Joined
Nov 16, 2020
Messages
3,581
Location
tx
I know 2 gauge thwn wire is rated at 130 amps. I don't know what gauge it would have to be for a 300ft run underground though.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,847
Location
Richmond, VA
You want to use a voltage drop calculator to determine gauge required.

If you are considering running copper, I would strongly recommend rethinking that. Aluminum will be a fraction of the cost
 

mrobins297aaa

Well-known member
Joined
Sep 20, 2010
Messages
3,283
Location
south east michigan
I'm about 170' to my barn from the main panel and I ran four 2/0 al for 100 amp panel in the barn.
In hind sight I think I could have went a little smaller on the wire gauge.
 
OP
H

Hobby_Man22

Well-known member
Joined
Nov 16, 2020
Messages
3,581
Location
tx
I'm about 170' to my barn from the main panel and I ran four 2/0 al for 100 amp panel in the barn.
In hind sight I think I could have went a little smaller on the wire gauge.
Better to go overkill and do it once. For some reason electricians aren't always happy to come back out 6 months later to do the job again.
 
OP
H

Hobby_Man22

Well-known member
Joined
Nov 16, 2020
Messages
3,581
Location
tx
I'm about 170' to my barn from the main panel and I ran four 2/0 al for 100 amp panel in the barn.
In hind sight I think I could have went a little smaller on the wire gauge.

Is it a big deal to run this length underground? I would think they would just use gas powered trencher and make quick work of it.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,847
Location
Richmond, VA
Is it a big deal to run this length underground? I would think they would just use gas powered trencher and make quick work of it.
Never lived somewhere with rocks in the soil, huh?

Nothing is easy about trenching 300' in places like New England.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,771
Location
NW Iowa
I can trench 300' in an hour, it's not a big deal. You can run secondary 2-300 ft without an issue. Might need to bump the wire up a size.
 

tez929rr

Well-known member
Joined
Dec 26, 2005
Messages
3,766
Location
Welfare, TX
Still on the fence about where to put my building. First of all how many 125amp sub panels can you connect to a 200 amp main panel? Then the second question is would it be cheaper to have the power company drop another line in? Or is 250-300ft too far? I thought they did this for free.
Another line means another meter and monthly meter charge.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,243
Location
SE MI
First, why do you think you need 125A ? Most DIY garages/shed can do fine on a 60A feed. The size of the main breaker does not matter. Worst case if you exceed the 60A feed in the main panel you will have to walk 300' to reset it.

Many POCOs will not install a second drop and meter unless it is for commercial or farm/ranch use.
 
Last edited:

Rusty Wrench

Well-known member
Joined
Aug 19, 2021
Messages
190
I'm about 170' to my barn from the main panel and I ran four 2/0 al for 100 amp panel in the barn.
In hind sight I think I could have went a little smaller on the wire gauge.
Similar. 200' 3/0 direct burial aluminum to a 100A panel.
Can run 6.5kW heater, 25A compressor, 25A BendPak + shop lighting simultaneous. No trips.

Edit: for 300' I might bump to next wire size. This' where you might want a sparky.
 
To avoid these ads, REGISTER NOW!

Skooterj

Well-known member
Joined
Mar 11, 2021
Messages
752
Location
Indiana
I looked into having my POCO drop a separate service at my garage. The will install it for free, but it has a minimum service fee of $35 a month. So if I never turned a light on, it would still cost me $420 a year. I had a electrician quote me out $1200 to run 100 Amp service out of my main panel in my basement to the garage, install a new box and wire it all. Return on investment less than 3 years. If I do it myself, I figure I can do it for less than $600...
 

Rusty Wrench

Well-known member
Joined
Aug 19, 2021
Messages
190
That's a badass attachment. :D

My electrician used a ditchwitch for direct bury cable. I've learned since the irrigation installers around here use a vibrating/slicing attachment to pull pipe through soil without opening a trench. By request they will pull electric conduit. It wouldn't have worked for me because our local code requires 30" deep with the locating tape 12" above that. But maybe an option for you.
 

AP514

Well-known member
Joined
Jan 23, 2014
Messages
768
Location
Pearland, Tx
Hell if your going 300 ft go at least 90 AMPs..
IMO 60 amp is wasting your money. It leaves you Zero upgrade room...
Also I went Copper for the WIN :)...(Oh here comes the comments on that..:0 )
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,847
Location
Richmond, VA
Hell if your going 300 ft go at least 90 AMPs..
IMO 60 amp is wasting your money. It leaves you Zero upgrade room...
Also I went Copper for the WIN :)...(Oh here comes the comments on that..:0 )
There is no win in running copper over aluminum, but it is your money to do with as you please
 
OP
H

Hobby_Man22

Well-known member
Joined
Nov 16, 2020
Messages
3,581
Location
tx
How can he suggest anything? I didn't even say how big the building was or what i'm putting in it.
 
OP
H

Hobby_Man22

Well-known member
Joined
Nov 16, 2020
Messages
3,581
Location
tx
Yes. 125amp will be sufficient for now and whatever dumb idea I come up with in the future.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,771
Location
NW Iowa
A 2/0 aluminum would be a nice size. At 100a load the voltage drop is pretty reasonable. It's pretty rare to load a feeder to 100% and if you do it's probably only for a few minutes.

Nice thing about 2/0 is it will fit the breakers without having to reduce it and it will fit in the panels better too.

If you plan to load it heavy you could use 4/0 but there will be more hassle.
 
OP
H

Hobby_Man22

Well-known member
Joined
Nov 16, 2020
Messages
3,581
Location
tx
Im liking this idea. Just put the second building 300ft away put a vehicle lift inside it and just buy another air compressor for that building too. That was the reason for connecting the two buildings was to make it so all my tools stay in one building, but I guess it's not that big a deal to just have a second smaller toolbox another compressor etc.
 

csp

Well-known member
Joined
Mar 23, 2010
Messages
5,720
Location
Franktown, CO
How can he suggest anything? I didn't even say how big the building was or what i'm putting in it.
What does the building size have to do with electrical amperage needs?

I'm not going to lie, given what I've seen in your other threads I'm not convinced you know what your electrical needs are even if you do know what you're putting in it.
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,883
Location
Austin, TX
How can he suggest anything? I didn't even say how big the building was or what i'm putting in it.
FYI: We're kinda asking you: "Whatcha gonna do with it, IE - what's in it"?
Everyone here is trying to give you good advice. If you don't want to disclose, and just say, "I need 125A" - I get it, but you *might* be missing advice where you can step up to 150A or step down to 90A for some very marginal money.

FYI, I have a 2400 sqft shop in Texas, same state as you. I "get by" with 90A pretty darn well. And that shop has 2 ACs, a refrigerator, and a hot tub. I have a 240V MIG welder, run a 1.5 HP pump for our home, and have multiple RV connections.

Clarification appreciated, if you're willing to provide it. :)
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,847
Location
Richmond, VA
Sometimes people don't want to share details. If the guy is sure 125a is the right number, so be it. We aren't saving the world here
 
  • Like
Reactions: csp
OP
H

Hobby_Man22

Well-known member
Joined
Nov 16, 2020
Messages
3,581
Location
tx
Sometimes people don't want to share details. If the guy is sure 125a is the right number, so be it. We aren't saving the world here
I like to think I'm pretty straight forward with my questions. Yes I don't like to spill out all the details all the time. Might as well post my address and send some of you guys out there to look for yourself
 
OP
H

Hobby_Man22

Well-known member
Joined
Nov 16, 2020
Messages
3,581
Location
tx
Some people don't want to just get by. Some people want to not have to worry about it. I think it's dumb to have to remember to turn the air compressor off because if it kicks on when I'm using the welder it's gonna be dark in the shop. Then you have a friend show up one day and you have to explain this to him and he reminds you you're a cheap sob. Personally something like an electrical panel that's gonna be usable for the next 50 years isn't something to be cheap on. Now if you want to buy heb branded dr pepper vs the real brand now we're talking. To each their own......😆
 

frankd

Well-known member
Joined
Aug 5, 2014
Messages
677
Location
Long Island, NY
Some people don't want to just get by. Some people want to not have to worry about it. I think it's dumb to have to remember to turn the air compressor off because if it kicks on when I'm using the welder it's gonna be dark in the shop. Then you have a friend show up one day and you have to explain this to him and he reminds you you're a cheap sob. Personally something like an electrical panel that's gonna be usable for the next 50 years isn't something to be cheap on. Now if you want to buy heb branded dr pepper vs the real brand now we're talking. To each their own......😆

It's not the cost of the panel. It's the 300ft of wire that's gonna get you. I recently added a sub-panel to a separate storage building. Mine was only about 100ft from the house. I rented what I thought was a large enough trench digger from home depot but the soil is very hard and rocky so we had quite a bit of trouble digging the trench. It doesn't sound like you'll have that issue.
If the local electric company will run a separate meter to your garage, then I'd have them do that. If not, I'd go with aluminum wire over copper. I used 6 gauge aluminum xhhw-2. I felt like I only needed 50 amps but if you're looking for 125, you'll probably need to go with 2/0.
I paid just over $100 for the wire. If I had gone with copper, it would have been well over 3 times the price.
 