Diesel Dan
Well-known member
What options are there for feeding a building 240V/200A at a distance of 800' from meter?
Obviously voltage drop will be an issue.
Possible to use step up/down transformers?
Looking for ideas other than having POCO drop another pole/meter.
Voltage drop calculator shows raising voltage to 480/600V drops conductor cost a lot.
Found a 50KVA 240v-600v single phase step up transformer for $1500.
Seen some threads recommending doing 240-2400v but cost of conductors jumps and could only find smallest of 6 awg when calcs show only 12 awg needed.
Obviously voltage drop will be an issue.
Possible to use step up/down transformers?
Looking for ideas other than having POCO drop another pole/meter.
Voltage drop calculator shows raising voltage to 480/600V drops conductor cost a lot.
Found a 50KVA 240v-600v single phase step up transformer for $1500.
Seen some threads recommending doing 240-2400v but cost of conductors jumps and could only find smallest of 6 awg when calcs show only 12 awg needed.