Most of the outlets in my house (built in 1966) are not grounded. I have one in particular that my entertainment center is plugged into. I have a Tripp Lite Isobar plugged into that outlet that my subwoofers are plugged into. The Isobar buzzes when there is power applied. If I disconnect the coax to my cable box, the red light comes on the Isobar telling me that there is a ground fault.
Anyway, I called an electrician and he said he can run a ground wire to the water pipe to ground the outlet. Is that code? It sounded sketchy to me. Also, only half of the house has been re-piped, so the other half will be done at some point in the future, which would affect the grounding.
What's the right way to do this? I'm an noob when it comes to electrical.
Thanks!
Why does that sound sketchy to you?
Code still allows a ground wire to be ran separate from the branch circuit wiring to retrofit older houses.
U need to make sure that the water line is bonded to the neutral bar in the main service panel.
The ground fault light on the surge suppressor comes on when the cable is disconnected because the surge suppressor lost the ground connection to the neutral bar in the main service panel via the cable line whoch should be bonded to the main service panel neutral/ground bar. The way surge suppressors work with ground fault lights is they send a small amount of current on the ground wire to check if there is a path to ground.
The part of the house that isnt repiped isnt a problem. U can just run the green ground wire to the nearest GROUND/BONDED metal water line
As you probably know the plumbing needs to be metal and grounded it self.
my electrical box is also grounded to my plumbing or maybe it is my plumbing is grounded to my breaker box, Being that my box has two out side ground rods.
The plumbing is BONDED to the main service panel as it should be.
And youre confused about the 2 types of electrical grounding.
EGC/equipment grounding is different than grounding electrodes.
EGCs provide low resistant paths for fault current so breakers can trip and clear the fault.
Grounding electrodes such as grounding rods have several purposes the main being to ground lightning strikes.
EGCs and grounding electrodes are 2 different animals- dont confuse the 2!
Heres a good article that helps to clear up the confusion:
http://www.electriciantalk.com/articles/the-confusion-of-the-term-grounding/
BTW 20' of buried metal water line can be used as a grounding electrode. But again thats different than an EGC.
A ground wire theoretically shouldn't have any current on it under normal circumstances - it's there for protection. If you have stray current on the coax you should figure out where it's coming from.
The stray current is from the IsoBar thats sending a minute amount of current over the shielding of the coax to detect whether the equipment grounding is kosher...
The BEST solution is replace that one outlet with a GFCI. You can plug a 3 prong cord in directly, even though there is no ground. GFCI's even com with a sticker that say "Not Grounded".
It is totally safe and code legal, because GFCIs protect against any small amount of leakage current.
The OP needs a grounded outlet not a GFCI.
Using a GFCI will NOT provide the surge suppressor with the proper fault current path to shunt surge current. A surge suppressor needs a grounded 3-wire outlet to function properly..
There is a drawback if your house has a neutral fault, and is connected by metal plumbing to the neighbors, You can create a deadly hazard at their box.
The plumbing should be bonded to the neutral bar in the main service panel to prevent the plumbing from becoming energized from a wiring fault. This is standard practice. If it doesnt get bonded fault current could energize the plumbing and the breakers wont be able to clear the fault.
And if the service neutral is lost, the neutral return current can and will flow over the grounding electrodes as well as the metal water line. But as is usually the case, one hot leg will see higher voltage than the other which can create a dangerous situation that can burn the house down.